Generator start-up torque

  • Thread starter Thread starter royalbas001
  • Start date Start date
AI Thread Summary
The discussion focuses on calculating the torque for a starter generator (СГ-18-1С) rated at 18 kW and operating between 3600 to 6200 RPM. Initial calculations suggest a torque of approximately 48 Nm at 4000 RPM, but further analysis indicates a maximum applied shaft torque of 125 Nm is possible. The calculations confirm that the output power translates to around 24.13 HP, leading to a torque of about 43 Nm at 4000 RPM when considering efficiency losses. The generator is designed for starting diesel engines and supplying electric energy, with a maximum current of 800 amps. Accurate torque calculations are crucial for selecting an appropriate motor for the application.
royalbas001
Messages
1
Reaction score
0
TL;DR Summary
Torque calculation of СГ-18-1С
Hi
I want to design a test rig for starter generator ( СГ-18-1С ). The output of the starter generator is 28V, 18KW @ rpm 3600 - 6200. The output will be regulated through excitation winding current.

I want to choose a motor to run the stater generator. Please tell me, How to calculate the torque of the starter generator.

I calculated as Torque = Power x 60 / 2 x Pi x rpm, results a ~48Nm torque at 4000 rpm. Is it correct or need to consider the excitation winding current? Please suggest. I want to choose the motor using V- belt pully drive with step up.

Thank you
 
Engineering news on Phys.org
1 HP = 746 Watts
18KW / 746

18 000/746 = 24.13 HP

HP x 5252 /rpm = Torque (Ft.Lbs.)
24.13 x 5252 / 4000 = 31.68 FtLbs

1FtLb = 1.356 Nm
31.68 x 1.356≅ 43Nm

That assumes 100% efficiency in the starter and the belts, which of course will not happen.

Cheers,
Tom
 
  • Like
Likes Ivan Nikiforov
Welcome to PF.

The SG-18-1S starter/generator is a Russian built direct current machine of mixed excitation, with air cooling by a built-in fan, designed for starting of diesel engines, supplying electric energy, and recharging batteries.

Specified as 18 kW.
Generator maximum current: 800 amp continuous. ( Vmax of 22.5 volt ).
Maximum applied shaft torque = 125 N∙m.
Maximum speed 7000 RPM.

To generate the maximum output will require an engine rating of 18 kW.
18 kW is equivalent to 24 HP.

4000 RPM * 0.10472 = 418.9 radian/sec.
18 kW / 418.9 = 43.0 N∙m.
My numbers agree with Tom.G

For 18 kW output, shaft torque will be;
@ 3600 RPM, 48. N∙m
@ 4000 RPM, 43. N∙m
@ 4400 RPM, 39. N∙m
@ 5200 RPM, 33. N∙m
@ 6000 RPM, 29. N∙m
 
  • Like
Likes Ivan Nikiforov
Here's a video by “driving 4 answers” who seems to me to be well versed on the details of Internal Combustion engines. The video does cover something that's a bit shrouded in 'conspiracy theory', and he touches on that, but of course for phys.org, I'm only interested in the actual science involved. He analyzes the claim of achieving 100 mpg with a 427 cubic inch V8 1970 Ford Galaxy in 1977. Only the fuel supply system was modified. I was surprised that he feels the claim could have been...
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...