A kitchen incident involved an air conditioner and refrigerator losing power simultaneously, leading to a dangerous situation when sparks and flames erupted from an outlet. Upon inspection, a severely burned outlet box and damaged wires were discovered, prompting a call to an electrician for assistance. The homeowner emphasized the importance of being attentive to electrical issues, as the situation could have resulted in a fire. Discussions highlighted the need for regular maintenance of electrical connections, including tightening screws in circuit breaker boxes and outlets to prevent arcing and potential hazards. The conversation also touched on the risks associated with older wiring systems, particularly in log cabins, and the necessity of checking smoke alarms and ensuring that circuits can handle the load of multiple appliances. Overall, the incident served as a cautionary tale about electrical safety and the importance of vigilance in home maintenance.
turbo
Insights Author
Gold Member
Messages
3,157
Reaction score
57
Glad I was home!

This afternoon, I was in the kitchen cleaning blueberries when the air conditioner and refrigerator both quit at once. I checked the breakers, and couldn't find a tripped one, nor would those appliances power up. I got out my DMM and checked outlets - there was power to every outlet in the kitchen except the outlet feeding those two appliances. Then I started to check the outlet over the kitchen stove and sparks and flames shot out of the outlet. I only had gotten one probe into the neutral slot - I hadn't probed the hot slot yet. I ran out to the panel, shut off the breakers to the kitchen outlets, grabbed a screwdriver and took off the trim plate only to see a very badly burned outlet-box with scorched, damaged wires. This was a problem more complex than a simple outlet replacement, so I called my electrician brother-in-law and he came right over and helped me sort out the problem. If I hadn't been home AND paying attention to details, the place could have burned down. As it is, we have a little burned wallpaper and an increased wariness about poor connections in our outlets. I'm going to have to check the connections at our outlets for integrity.
 
Physics news on Phys.org


turbo-1 said:
This afternoon, I was in the kitchen cleaning blueberries when the air conditioner and refrigerator both quit at once. I checked the breakers, and couldn't find a tripped one, nor would those appliances power up. I got out my DMM and checked outlets - there was power to every outlet in the kitchen except the outlet feeding those two appliances. Then I started to check the outlet over the kitchen stove and sparks and flames shot out of the outlet. I only had gotten one probe into the neutral slot - I hadn't probed the hot slot yet. I ran out to the panel, shut off the breakers to the kitchen outlets, grabbed a screwdriver and took off the trim plate only to see a very badly burned outlet-box with scorched, damaged wires. This was a problem more complex than a simple outlet replacement, so I called my electrician brother-in-law and he came right over and helped me sort out the problem. If I hadn't been home AND paying attention to details, the place could have burned down. As it is, we have a little burned wallpaper and an increased wariness about poor connections in our outlets. I'm going to have to check the connections at our outlets for integrity.

Whew, that could have been really bad - good thing you caught it. Check your smoke alarms!
 


Do I remember correctly that you live in a log cabin? Like all smart Mainers? :wink:

Glad nothing bad happened.
 


That must have been lucky for people for miles around, a fire in the Turbo kitchen could have caused a county wide shut down and the use of several hazmat teams.
 


turbo-1 said:
This afternoon, I was in the kitchen cleaning blueberries when the air conditioner and refrigerator both quit at once. I checked the breakers, and couldn't find a tripped one, nor would those appliances power up. I got out my DMM and checked outlets - there was power to every outlet in the kitchen except the outlet feeding those two appliances. Then I started to check the outlet over the kitchen stove and sparks and flames shot out of the outlet. I only had gotten one probe into the neutral slot - I hadn't probed the hot slot yet. I ran out to the panel, shut off the breakers to the kitchen outlets, grabbed a screwdriver and took off the trim plate only to see a very badly burned outlet-box with scorched, damaged wires. This was a problem more complex than a simple outlet replacement, so I called my electrician brother-in-law and he came right over and helped me sort out the problem. If I hadn't been home AND paying attention to details, the place could have burned down. As it is, we have a little burned wallpaper and an increased wariness about poor connections in our outlets. I'm going to have to check the connections at our outlets for integrity.

Whew! What could cause the outlet to go bad? Was it a wiring problem?
 


I had that happen once before... Thankfully I was home, too!

Glad you got it taken care of, that beautiful garden isn't worth as much without a house full of people to eat the bounty...
 


wolram said:
That must have been lucky for people for miles around, a fire in the Turbo kitchen could have caused a county wide shut down and the use of several hazmat teams.

:smile: Like a capsaicin factory burning down!
 


larkspur said:
Whew! What could cause the outlet to go bad? Was it a wiring problem?
A connection that got either loose or perhaps corroded and allowed arcing.
 


Borek said:
Do I remember correctly that you live in a log cabin? Like all smart Mainers? :wink:

Glad nothing bad happened.
Yep! Log cabin. It is probably time to survey and possibly upgrade the wiring - the place was built some time ago and some outlets are polarized but not grounded. Unfortunately, the outlet with the problems was a relatively modern receptacle that is grounded, and my false sense of security regarding upgraded receptacles is now dashed.
 
  • #10


I had a wire in the meter base burn up and lost current to half the house one time. The electrician that fixed it, said that the wires in the meter base and all the wire connections in the circuit breaker box should be tightened down every 10 years, due to the alternating currents vibrating the wires and the connections. Once they get a little loose, arcing can happen. He also said that about every 15 to 20 years every screw should be tightened up--that includes all the outlet boxes.

you did get lucky being there, turbo
 
  • #11


wolram said:
That must have been lucky for people for miles around, a fire in the Turbo kitchen could have caused a county wide shut down and the use of several hazmat teams.

lisab said:
:smile: Like a capsaicin factory burning down!
OK, you two. :devil:

The fire-fighters have air-packs and would not have been in too much pain and neighbors can always be evacuated to a safe distance. I would not have wanted to be around when my cupboards and pantry full of hot stuff started burning with exploding jars of habanero relish joining the mix. Just simmering the stuff prior to canning requires opened windows and fans unless you're really used to the effects. If the cops want to pepper-spray me some day (I'm never that bad!) they'll probably have to squirt me in the eyes - I think I've managed to get about every other type of capsaicin accidentally over the years, and I'm getting used to it. :rolleyes:
 
  • #12


Did you have both an A/C and fridge on the same circuit? Maybe it was overloaded when both came on together? Better check that the circuit can handle the load of both starting up together.

And yes, VERY lucky you were right there when it happened and noticed something wrong before it got bad. We had an outlet in my parent's kitchen do something similar once, except nothing was even plugged in at the time. Some sort of short. I just looked over and noticed it smoking ever so slightly and hollered for my parents.
 
  • #13


rewebster said:
I had a wire in the meter base burn up and lost current to half the house one time. The electrician that fixed it, said that the wires in the meter base and all the wire connections in the circuit breaker box should be tightened down every 10 years, due to the alternating currents vibrating the wires and the connections. Once they get a little loose, arcing can happen. He also said that about every 15 to 20 years every screw should be tightened up--that includes all the outlet boxes.

you did get lucky being there, turbo
Thanks rewebster. You're right about re-tightening. A number of years ago in our old house, we started getting some odd brightenings and dimmings of lights. I thought the power company had a problem with the entrance transformer because a load on one leg of the panel would cause higher voltage on the other leg. Nope! I talked to my brother in law, and he told me to open the main panel and tighten the ground and neutral clamps. That fixed it. Clamp(s) were loose, allowing neutral to lose its reference to ground. That house was built during a period when electricians were transitioning from copper to aluminum cables, and clamp technology was not keeping up.
 
  • #14


Moonbear said:
Did you have both an A/C and fridge on the same circuit? Maybe it was overloaded when both came on together? Better check that the circuit can handle the load of both starting up together.

And yes, VERY lucky you were right there when it happened and noticed something wrong before it got bad. We had an outlet in my parent's kitchen do something similar once, except nothing was even plugged in at the time. Some sort of short. I just looked over and noticed it smoking ever so slightly and hollered for my parents.
Yes they are on the same circuit, and have never tripped a breaker, even when the compressors start at the same time. The odd thing is that an outlet on the same circuit with a loose/corroded neutral connection caused the problem. I WILL be surveying and checking and tightening connections.
 
  • #15


Wow, turbo, it's really good you were there. Electricity is a scary thing to be sure. No taking it for granted.
 
  • #16


This is exactly why I am amish.
 
  • #17


Glad to hear you're ok, that could have been really bad!
 
  • #18


Borek said:
Do I remember correctly that you live in a log cabin? Like all smart Mainers? :wink:

Glad nothing bad happened.

I believe that those who live in Maine are Maniacs... Seems to apply to all I have known. :devil:
 
  • #19


Integral said:
I believe that those who live in Maine are Maniacs... Seems to apply to all I have known. :devil:
Fair cop! The Maine Air National Guard has that painted on their tails, and it ain't far wrong.
 
  • #20


Evo said:
Glad to hear you're ok, that could have been really bad!
Thanks. I don't care about personal hazard (could jump out a window pretty easily), but it would be a bummer to lose photographs and other belongings that cannot be replaced, along with my guitars, amps, guns, and the contents of my computer HDs. The last is perhaps the thing I should worry least about - my collaborators and I share data, graphs, draft texts, etc so that it would be tough to lose significant pieces of the work that I've been doing on astronomy for the last few years.
 
  • #21


I live in an apartment condo that was built in the 70s. One night my arm brushed against the metal plate on the wall in the bathroom that housed the “razors only” plug-in. It was hot. Really hot. A hot wall plate covering electrical wires could not be a good thing. I have no idea how long it was like that.

I immediately went to the box and flipped the breaker off and then spent the whole night sleepless. I got up every half hour or so to make sure the plate had cooled. It had, but I continued getting up all night to check it. It frightened the beejeebeez out of me.

I called my landlord in the morning, and he came out the same day and replaced the whole kit and caboodle. And it made me make serious plans for a quick exit, if it came to that. Reading this thread, now, makes me think I’ll call my landlord in the morning and have him come and check all of my electrical outlets, just to be sure. Potential for fire concerns me an awful, awful lot.
 
  • #22


rewebster said:
I had a wire in the meter base burn up and lost current to half the house one time. The electrician that fixed it, said that the wires in the meter base and all the wire connections in the circuit breaker box should be tightened down every 10 years, due to the alternating currents vibrating the wires and the connections. Once they get a little loose, arcing can happen. He also said that about every 15 to 20 years every screw should be tightened up--that includes all the outlet boxes.

you did get lucky being there, turbo

I don't doubt the electrician's statement about the wires having to be tightened every so often, since experience is a pretty reliable source.

I do doubt his explanation. It's only the electrons that move in a wire. Electrons only have a mass of 9.1 x 10^-31 kg and their motion due to the electrical current is very slow:


I/(Q e r^2 pi) since the latex image didn't work.

Where Q is the number of movable electrons per cubic centimeter and e is the electrical charge per electron (1.6 x 10^-19).

I don't think the motion due to electricity is going cause much vibration of the wire itself.

I'd almost be tempted to toss in the fact that the electrons are already orbiting the nucleus and that the thermal motion of an electron far outweighs the motion due to the electric current, but both of those types of motion are essentially random and wouldn't contribute to any harmonic vibration of the wire itself. Still, the motion of an electron due to electricity could almost be considered a slight bias for the electron to travel one direction over the other.

I'd buy thermal expansion and contraction of the wire over time before I'd buy the electrical current causing the wires to vibrate.
 
  • #23


Electrons no, but electromagnetic field surrounding the wire? Transformers buzz, perhaps wires buzz too, just very quiet.
 
  • #24


Was it aluminun wire? It is the slight heat/cool cycles in the aluminum wire that has had it banned here for years, simple expansion and contraction,over time loosens the retaining screw.
 
  • #25


The wire in my application was copper. Pretty solid stuff, normally, but I guess a little looseness allowed some arcing and eventually, the arcing eroded the wire-clamp interface to the point where some substantial heat was generated.
 
  • #26


glondor said:
Was it aluminun wire? It is the slight heat/cool cycles in the aluminum wire that has had it banned here for years, simple expansion and contraction,over time loosens the retaining screw.

If it's aluminum wire, isn't it recommended the connections be soldered because this is such a common problem, especially where aluminum wires connect to copper contacts?
 
  • #27


lisab said:
Whew, that could have been really bad - good thing you caught it. Check your smoke alarms!

Why quote when you're the first one to answer?
 
  • #28


Werg22 said:
Why quote when you're the first one to answer?

Habit.
 
  • #29


lisab said:
Habit.

Noon's habit? I see you have started your training already :smile:
 
  • #30


Borek said:
Noon's habit? I see you have started your training already :smile:

:smile:
 
Back
Top