Harmonics on 3 phase 3 wire system

AI Thread Summary
In a 3-phase, 3-wire system fed by a generator with non-linear loads, the presence of harmonic currents on the neutral conductor depends on the connection type of the loads. If the loads are wye-connected with their neutral tied to the generator's neutral, third harmonic currents will return through the neutral. However, if the loads are delta-connected or if the wye's neutral is left floating, these currents will be constrained to the phase windings, potentially leading to neutral instability. The discussion highlights the complexities of harmonic issues, especially with variable speed drives, and emphasizes the importance of proper grounding and bonding practices. Understanding these factors is crucial for effective harmonic management in electrical systems.
Depak
Messages
3
Reaction score
0
Lets say I have a switchboard that requires ONLY 3 Phase loads, transformer, UPS, Motors, ETC. ( no neutral is required at all)
Now let's say I am feeding this from a generator where I have 4 wires from the alternator ABCN connected to the aforementioned switchboard.
the N of the generator alternator is Bonded to ground inside of the aforementioned switchboard but NOT at the generator location.

The 3 phase loads that are feeding from the switchboard are non-linear and have a fairly "dirty" harmonic profile.

The question is will i see any harmonic loads on the neutral conductor between the main service and the generator?

can someone point me to a white paper or other documentation that clarifies this point either way?

thank you

-Deepro
 
Engineering news on Phys.org
Depak said:
The question is will i see any harmonic loads on the neutral conductor between the main service and the generator?

Bonding is irrelevant

If your loads are wye connected with their neutral tied to neutral of generator, then all their third harmonic current will return through that neutral. You'll see in your neutral the sum of their 3rd harmonic currents. That's why for computer systems the neutral conductor is sized same as lines.
If your loads are delta connected then 3rd harmonic current is constrained to the phase windings.
Place a clamp-on current probe around neutral and observe current. If it's 180 (150?) hz, is its amplitude objectionable?

We once corrected objectionable 3rd harmonic current by opening the neutral connection . The downside was the system would not continue to operate when a single line fuse opened.

I wish i knew of a white paper - would've saved us a lot of midnight oil.
In recent years the rise of variable speed drives has prompted a lot of articles on harmonics. Try a search on "third harmonic neutral "

below is hardly a white paper but it describes our experience in mid 1970's .

http://www.designnews.com/author.asp?section_id=1368&doc_id=273075
 
Last edited by a moderator:
Thank you very much but you missed the point of the question. Perhaps this is my fault that I did not explain it well. My English is not perfect.

Generator is Wye,

5 wires extend from the generator to the main switchboard. A, B , C , N , G

(here is the important part ) At the main switchboard there is NO loads connected to the neutral.

Copied from the original question “I have a switchboard that requires ONLY 3 Phase loads, transformer, UPS, Motors, ETC. ( no neutral is required at all)"
 
Depak said:
(here is the important part ) At the main switchboard there is NO loads connected to the neutral.

indeed i didn't get from your post that the neutral in the switchboard (if indeed there is one) is not connected.
So your loads might be all delta,
or wye with neutral left floating.
If the latter there will be interesting voltage between switchboard neutral and the generator's neutral, known as "neutral instability", I hope you are able to connect some meters and oscilloscopes .
Harmonic problems can be hideous to figure out. We had shaft currents eating bearings in rotating machines, and industry knowledge of the phenomenon was sparse until VFD's pushed the problem down into home appliance sized motors.

Don't apologize for your English, it's quite good. I suppose a picture is worth a thousand words in any language.

old jim
 
Thanks Jim, there is not floating neutral. The N and G and bonded at the main service. The N feeds back to the N in the alternator and the G feed to the casing of the generator the N and G are not bonded at the generator. I cannot scope this as it is not installed this is a theatrical question.
 
Depak said:
N and G are not bonded at the generator.

that's interesting. Our code has requirements for "separately derived service" which a generator would be.

If a separately derived system is required to be grounded, the conductor to be grounded is allowed to be connected to the grounding electrode system at any location between the source terminals (transformer, generator, etc.) and the first disconnecting means or overcurrent device. The location of the grounding electrode conductor connection to the grounded conductor must be at the same point as where the bonding jumper is connected to the grounded conductor. By establishing a common point of connection, normal neutral current will be carried only on the system grounded conductor. Metal raceways, piping systems, and structural steel must not provide a parallel circuit for neutral current.
Exhibits 250.13 and 250.14 illustrate examples of grounding electrodeconnections for separately derived systems.
http://www.mjobee.com/projects&news/delta xfmr1.pdf page 25 of 146

so it looks at first glance like you're okay bonding at the panel's service entrance. I'm accustomed to bonding right at the source.
 
Back
Top