Heat Flow Rate through Thin Metallic Plates: Air vs. Vacuum

AI Thread Summary
Heat flow rate through two parallel metallic plates is influenced by the medium in the gap—air or vacuum. When filled with air, convection can significantly alter heat transfer if the gap is large, while a vacuum relies solely on blackbody radiation, described by the equation E = σ(ΔT)^4. The temperature difference between the plates (ΔT) plays a crucial role, as energy transfer is proportional to the fourth power of this difference. If the gap is filled with wood, heat transfer occurs via conduction, following the equation E = kAΔT/L, where k is the thermal conductivity of the wood. Understanding these principles is essential for optimizing thermal insulation in various applications.
salsero
Messages
39
Reaction score
0
Two parallel thin metallic plates with a gap between them are used as a heat insulator. How does the heat flow rate through this device depend on the temperatures on its two sides in the following two cases?

Case 1: The gap is filled with air.
Case 2: There is a vacuum in the gap.
 
Science news on Phys.org
Energy transfer will be by blackbody radiation.

E= σ(ΔT)4

σ=5.67e-8 (Wm-2C-4)
(ΔT)= Temperature difference between the plates.

Air or vacuum will have little effect as long as the gap is small. If the gap is large enough to allow air convection then all bets are off. It is a very different and difficult problem.
 
1. Should it be (dT)^4 or d(T^4)?
2. What would be the answer if the gap were filled with wood?
 
That is
(ΔT)= Temperature difference between the plates.

The energy transfer is proportional to the fourth power of the temperature difference


If the gap were wood heat transfer would be by conduction.

E= kAΔT/L

k = Thermal conductivity of Wood (will depend upon the type of wood)
A = Area
L= Length
 
That should be

E = σΔ(T4)

Sorry I missed that the first time!
 
I need to calculate the amount of water condensed from a DX cooling coil per hour given the size of the expansion coil (the total condensing surface area), the incoming air temperature, the amount of air flow from the fan, the BTU capacity of the compressor and the incoming air humidity. There are lots of condenser calculators around but they all need the air flow and incoming and outgoing humidity and then give a total volume of condensed water but I need more than that. The size of the...
Thread 'Why work is PdV and not (P+dP)dV in an isothermal process?'
Let's say we have a cylinder of volume V1 with a frictionless movable piston and some gas trapped inside with pressure P1 and temperature T1. On top of the piston lay some small pebbles that add weight and essentially create the pressure P1. Also the system is inside a reservoir of water that keeps its temperature constant at T1. The system is in equilibrium at V1, P1, T1. Now let's say i put another very small pebble on top of the piston (0,00001kg) and after some seconds the system...
Back