Heating Air with Steam: Efficiency and Options

AI Thread Summary
To efficiently heat pressurized air from 60F to 200F using available resources, an air-steam heat exchanger is preferred due to its lower cost of ownership compared to electric coil heaters. The steam supply is adequate, with a flow rate that exceeds the requirements, and it operates without the complications of high voltage or extensive controls. Insulating steam pipes is necessary to maintain efficiency. The discussion also highlights the importance of controlling the heater outlet temperature for optimal performance. Overall, using steam for heating offers significant advantages in this scenario.
dyollnave
Messages
2
Reaction score
0
Hey everyone, I have a questions. I am trying to determine the most efficient way to heat pressurized air (35-40 psig, and a flow of 20-30 scfm) at an inlet temperature of 60F, to an exit temperature of 200F with minimal pressure lose. On site I have the availability of saturated steam at (50-80 psig, with a flow rate of 50lb/hr avg, 287 lb/hr max.), as well as electricity(up to 3-phase, 480v). What are the best options given the above information.

What are the advantages/disadvantages of a air-steam heat exchanger vs. an electric coil type heater.

Condensate trapping and drain are not an issue, as waste water disposal is already in place.

Thanks a bunch, I look forward to joining everyone on PF!
 
Engineering news on Phys.org
The air will be used to dry items further down the process line, not vented into a room.
 
Maybe you checked this, but looking at your numbers, I back of envelope calculated that you have plenty of steam flow available. A small thermodynamic steam trap would also be fine.

Main advantage of steam heater is:

* cost of ownership (less than 10 lb/hr steam vs about a 1.5 kW heater),
* no need for high voltage (240/480 volt, 3 phase, 60 Hz),
* less controls (power must be cut if heater element surface temperature reaches HIGH alarm setpoint).

Of course, you will need to insulate your steam pipes leading to the air heater.

Are you going to control heater outlet temperature?
 
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
I'm trying to decide what size and type of galvanized steel I need for 2 cantilever extensions. The cantilever is 5 ft. The space between the two cantilever arms is a 17 ft Gap the center 7 ft of the 17 ft Gap we'll need to Bear approximately 17,000 lb spread evenly from the front of the cantilever to the back of the cantilever over 5 ft. I will put support beams across these cantilever arms to support the load evenly