Help with voltage losses in cable question

  • Thread starter Thread starter dc2209
  • Start date Start date
  • Tags Tags
    Cable Voltage
AI Thread Summary
The discussion focuses on calculating voltage losses in high-voltage cable circuits, specifically transitioning from a 400kV circuit to a 132kV circuit over a 50km Ostrich cable. A user initially calculated a voltage drop of 441.4 volts for a different scenario involving a 200km Squab cable circuit. They sought assistance for the second question, which mirrored the first but with different parameters. Key calculations included cable resistance, current per cable, and voltage drop, leading to a significant loss of 43kV. The conversation highlights the importance of proper formatting and unit clarity in calculations for accurate results.
dc2209
Messages
14
Reaction score
0
the 400kV circuit is then stepped down onto a 132kV circuit (Ratio 3:1) and is used to feed a 50km, 2 wire (Ostrich) cable circuit, calculate voltage loss in the cable run.

and this a table that went with the question http://gyazo.com/a47c72d45a149cffa9d781ace8a2008d

and the first question was as follows : If the output from the generator is 500 MVA and it is feeding onto a 200km long, 4 wire (Squab) cable circuit via a step up transformer (Ratio 1:16) calculate the voltage loss in the cable run. I have calculated this question and got a voltage drop value of 441.4 volts.


Just wondering if anyone could give me a hand on where to start with the second question?

Thanks.
 
Physics news on Phys.org
Edit: Ah, I think now I understand it.
Would have been easier with the original questions, in the right order.

Question 2 is the same as question 1, just with different numbers. Where do you run into problems?
 
mfb said:
Edit: Ah, I think now I understand it.
Would have been easier with the original questions, in the right order.

Question 2 is the same as question 1, just with different numbers. Where do you run into problems?


This is my answer, would you say that seems right to you?

Cable length = 50 km

Cable resistance = 0.227 ohms/km (single ostrich)

Ostrich resistance = 50 x 0.227 = 11.35ohms

2 cable parallel resistance = 11.35 || 11.35 = 5.68ohms

Max current per ostrich = 492A


I = 500x106/400x103 = 1250 Amps

Step up transformer ratio = 3:1
Line voltage = 400x103 / 3 = 132kV (O/P on transformer)
Line current = 1250 × 3 = 3750A
Voltage drop per run = I×R = 3750 ×11.35 = 43kV


thanks
 
Formatting looks broken in the calculation of I. And you can use the final voltage there directly. Units are missing. Apart from that, it looks right, and the loss is significant...
 
mfb said:
Formatting looks broken in the calculation of I. And you can use the final voltage there directly. Units are missing. Apart from that, it looks right, and the loss is significant...


Ah yeah the third numbers are powers. Ok thanks
 
The simplified lumped circuit of a transmission line will be:
In a symmetrical and steady state load, neglecting Xc [nevertheless Xc could be elevated] the voltage drop [approximate] will be DV=sqrt(3)*I*[R*cos(fi)+X*sin(fi)].
X = k log (GMD / GMR)
GMD=(DAB*DBC*DCA)^(1/3) where: DAB[for instance]=distance between phase A and B [typical].
GMR [according to manufacturer catalogue]
 