Do Hot Swap PSUs Risk Phase-to-Phase Voltage Exposure?

AI Thread Summary
Hot swap PSUs in data center servers are designed to allow individual modules to be replaced without shutting down the system. Concerns arise regarding the potential for phase-to-phase voltage exposure, particularly in setups where PSUs are powered by different phases in a 240-volt system. It is crucial that these systems prevent any AC mains voltage from connecting to the low current lines, as this could create dangerous voltage differentials. The design should ensure that any connections between swappable PSU modules and the common power circuitry are safe and compliant with voltage standards. Overall, proper design practices should mitigate the risk of cross-phase voltage exposure in redundant hot swap PSU configurations.
Skaperen
Messages
86
Reaction score
0
I'm looking for information on how hot swap PSUs as used in computers (used typically for data center servers) are designed. In particular, I want to focus on the common aspects between the 2 or more PSU subunits that can be swapped. What kinds of connections are made between the individual swappable PSU module, and the common power circuitry? Is there any chance the any mains AC voltage would go across this connection, or by any other means, even if it is intended as a low current or current limited connection? What I am wondering about is whether this could be exposed to a phase-to-phase higher voltage (e.g. 416 volts) if/when the individual PSU modules are powered by separate phases (in a 240 volt phase to neutral system).

Hopefully, no hot swap PSU systems even exist where they allow AC mains voltages from separate PSU modules to be applied together anywhere, or if they do, are specifically designed to handle the worst case (e.g. at least 480 volts differential for PSUs that can operate at 100-240 volts). Common non-swappable PSUs for PCs only have DC and control lines that I have ever seen. But I can't get enough info on the hot swap type to rule out any phase-to-phase risks.

I am wanting to wire up servers which have 1+1 PSU redundancy (e.g. can run on 1 PSU being powered) to separate UPSes (small scale units, 1 or 2 per rack, not a giant room scale UPS). These UPSes would be wired to different phases in sequence. If I lose power to one phase only, and time passes by that exhausts the UPS battery, the phase diversity should still keep everything running (as long as the two remaining phases have that much capacity). Phase diversity UPSes would be nice, too, but I just don't see that on the market in rack size scales (3 to 6 kVA).

But in any case, what I am exploring at the moment is any possible cross phase risks, where phase to phase exceeds 240 volts, in the 1+1 redundant hot swap PSU system designs.
 
Engineering news on Phys.org
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...