leonardo-energy.org said:
Another advantage of DC distribution is the lack of reactive power in the system. Reactive power results in increased losses in AC systems due to larger current magnitude for an equal amount of transferred power. Non-linear loads, such as AC-DC converters (without power factor correction (PFC)), require reactive power in an AC system. In view of the large number of converters in data centers, much is to be gained by migrating to a DC system.
The problem with DC distribution systems is the insulation and inductance of the cables.
The insulation of AC is less demanding than the insulation of DC. Insulation of AC does not usually become polarised or grow conductive trees and whiskers, as often happens with DC.
Disconnecting DC can be difficult. Unplugging or switching off can strike an arc that is difficult to extinguish. AC reverses phase twice each cycle and so can be switched safely at lower cost. Look at the DC and AC ratings of switches and relay contacts to see a real advantage of AC over DC. As an example, 10A contacts are rated at either 30VDC or 250VAC.
I would distribute power within the server farm as DC, but I would do it with an advantageous twist to cut the weight and cost of cables, switch gear and connectors. To distribute power to racks I would use three phases of square wave AC. At any point in time two phases would supply the current while the third would have 2 msec to change polarity without load. The converter would operate at 50Hz or 60Hz. The 3PH SQ AC would be distributed over normal industrial cables and switch gear, with normal 3PH connectors. It is after all, 3PH 400VAC.
There would be two or more AC feeders entering the server farm from from separate sub-stations. Within the server farm there would be AC motors driving DC generators that charge three UPS battery banks to 400 VDC. Diesel engines could be clutched to two of the generators. All that is current marine propulsion technology. There would be crossbar connections to allow redundancy during fault conditions and while servicing.
Two independent supplies of 3PH SQ 400VAC would be generated from separate UPS battery banks by 3PH H-bridges. Those would operate between 50Hz and 60Hz. That redundant power would be distributed throughout the building to all racks.
Each power module in the rack would receive two 3PH SQ 400VAC inputs. A three phase, six diode bridge on each power input would regenerate 400VDC in the rack without ripple. (That would also minimise big electrolytic capacitor requirement and temperature problems in the rack supplies).
The rectified 400VDC would then be reduced efficiently using multiple distributed synchronous buck converters to LV DC for logic circuits.