How Can I Minimize Voltage Drop Across a 50 ft Wire with 80A Load?

AI Thread Summary
To minimize voltage drop across a 50 ft wire carrying an 80A load, using an appropriate wire gauge is crucial; 8AWG may result in an unacceptable 5.1V drop. Calculating the resistance of different wire gauges can help determine the necessary size to achieve an acceptable voltage drop. Alternatively, implementing remote sensing by running smaller sense wires alongside the power cables can allow the battery charger to adjust its output voltage based on the actual voltage at the robot's battery. This approach can effectively maintain performance without the need for an onboard charger. Proper planning and calculations are essential for optimal power delivery in this setup.
monkeyman
Messages
1
Reaction score
0
Hi all,

I'd like to ask for your help in solving a problem. I'm currently working on building a small ground robot for a certain research problem. The robot is powered by batteries, and consumes a continuous 80A @ 12V when all of its systems are active. The batteries provide capacity for about 2 hrs of runtime, but since extended testing sessions are common, we would like to use a high amperage battery charger that can remain connected to the batteries indefinitely, which will continuously top off and keep the batteries charged so the robot can also run indefinitely.

Now the question is, we can approach this one of two ways: 1. Have the battery charger on-board the robot, and run a 120VAC extension cord from the power source to the charger. This obviously presents no problems, is certainly feasible, except that now we have an extra charger on the robot which is only dead weight. So, is it possible to 2. Have the battery charger external, and run a 12V line out to the batteries on board the robot?

The problem is, say we are talking about a 50 ft. length piece of wire, maybe 8AWG. With 80A running through this, will there be an appreciable voltage drop at the other end? I found this calculator, http://www.powerstream.com/Wire_Size.htm which says there will be a 5.1V drop, which is obviously unacceptable. However, I have no clue what calculations were performed to arrive at this answer. Can anyone help out? Thanks.

I know my question is kind of long and convoluted. If you need any clarifications on the problem, please ask. Thanks again.
 
Engineering news on Phys.org
Look up a table of resistance for different gauges, like this one:

http://en.wikipedia.org/wiki/American_wire_gauge

Use whatever gauge is necessary to achieve the resistance you need to obtain an acceptable voltage drop.

Alternatively, use remote sensing (run two small sense wires alongside the power cables, connected to the power cables at the robot's battery, and have the battery charger regulate its output voltage according to the sense wires).

- Warren
 
Very basic question. Consider a 3-terminal device with terminals say A,B,C. Kirchhoff Current Law (KCL) and Kirchhoff Voltage Law (KVL) establish two relationships between the 3 currents entering the terminals and the 3 terminal's voltage pairs respectively. So we have 2 equations in 6 unknowns. To proceed further we need two more (independent) equations in order to solve the circuit the 3-terminal device is connected to (basically one treats such a device as an unbalanced two-port...
Thread 'Weird near-field phenomenon I get in my EM simulation'
I recently made a basic simulation of wire antennas and I am not sure if the near field in my simulation is modeled correctly. One of the things that worry me is the fact that sometimes I see in my simulation "movements" in the near field that seems to be faster than the speed of wave propagation I defined (the speed of light in the simulation). Specifically I see "nodes" of low amplitude in the E field that are quickly "emitted" from the antenna and then slow down as they approach the far...