How do I properly charge a VRLA battery?

AI Thread Summary
Charging a Valve Regulated Lead Acid (VRLA) battery typically requires maintaining a float voltage of around 2.25 Vpc, and boosting to 2.4 Vpc is generally not necessary. If the battery discharges to 20%, it can be recharged using only the float voltage without adverse effects. The consensus is that VRLA batteries do not need equalization like flooded lead acid batteries. Manufacturer documentation can be confusing, but it is important to refer to it for specific guidelines. Overall, maintaining the recommended float voltage is sufficient for optimal battery health.
pocho
Messages
9
Reaction score
3
hello, pozdrav


my question is about Valve Regulated Lead Acid battery. may i charge it only with "float" voltage (cca 2,25 Vpc) or do i have to "boost" it (2,4 Vpc) sometimes? if my battery gets discharged to 20% can i recharge it only with "float" voltage?

i have capacity cca 150Ah, 220V; temperature is ideal 20°

thank you

hvala
 
Engineering news on Phys.org
This a pretty good white-paper on batteries. It says VRLA batteries generally do better at the recommended float voltage, and don't require "equalization" like a flooded lead acid. But I would look at the manufacturer's documentation to be sure.

http://www.apcmedia.com/salestools/SADE-5TNRJR_R2_EN.pdf
 
Last edited by a moderator:
thank you gtacs. this is a good resource. manufacturers documents are a bit confusing, i checked Sonnenschein and EnerSys websites.

it seems that "boost" treatment is not needed for VRLA. that is fine with me, because i had some trouble with overvoltages: boost_voltage x number_of_cells > voltage_tolerance.

thank you, have a nice day
 
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...