How Do You Calculate Transformer Losses and Resistances from Test Data?

  • Thread starter Thread starter alnywk
  • Start date Start date
  • Tags Tags
    Phase Transformer
AI Thread Summary
To calculate transformer losses and resistances from test data, the open circuit (OC) and short circuit (SC) tests provide essential parameters. The OC test reveals core losses, while the SC test helps determine copper losses and equivalent resistance. The equivalent resistance can be calculated by analyzing the voltage, current, and power from the SC test data. It is justified to consider the power input during the OC test as core loss since it remains constant regardless of load. Understanding these principles is crucial for accurately assessing transformer performance.
alnywk
Messages
13
Reaction score
0
urgent : single phase transformer

Homework Statement



A 2200/220 V, 500kVA, 50Hz distribytion transformer has been tested by means of the open circuit. the test data obtained is as follow:
open circuit test: V(l)= 220V, I(l)= 85A, P(oc)= 1800W
short circuit test V(h)=95V, I(h)=227.3A P(sc)= 8.2kW



2. Relevant question

1.equivalent resistance referred to the low voltage side (state all assumption)

2. resistance of the low side winding only

3.transformer copper loss of the secondary winding during the open circuit test

4. transformer core loss when rated voltage is applied

5. explain if it justified to use the power input during the open circuit test as core loss?






The Attempt at a Solution

 
Physics news on Phys.org
It is so clear that you want us to do your homework. Here is a hint. OC tests are used to find parameters on the primary side, and SC tests are for the secondary side. Once you find out your core loss, you can assume it to be a constant and not varying with load. Only the Cu losses will change with load.
 