How Thick Should the Concrete Foundation Be to Counteract Buoyancy Underwater?

AI Thread Summary
To determine the thickness of a concrete foundation for a submerged pump station, one must calculate the buoyancy forces acting on the structure. The density difference between concrete (2300 kg/m^3) and water (1000 kg/m^3) yields a buoyant force of 1300 kg/m^3, which is crucial for counteracting buoyancy. However, additional factors such as the pump station's dimensions, weight, and environmental conditions (like water currents) must also be considered. Accurate calculations require knowing the volume of the pump station and any external forces acting on it. Ultimately, a comprehensive understanding of these variables is essential to determine the necessary concrete foundation thickness.
ahmed2810
Messages
2
Reaction score
0
Member advised to use the homework template for posts in the homework sections of PF.
Hello, I have a question about buoyancy of concrete in water. If a submersible pump station is placed under water, and it has under it a concrete foundation to hold it in equilibrium.
How can someone calculate the minimum weight of the concrete foundation?

The pump station has a diameter: 1.6 meter
density of the water is: 1000 kg/m^3
Density of the concrete is: 2300 kg/m^3
the height of the submersed item is 2 meter under water

How thick must the concrete foundation be to counterbalance the buoyancy forces?
PS: please show me equations, and not just an explanation
 
Physics news on Phys.org
Hi,
I guess the pump has a negative buoyancy in water, so it will stay at the bottom even if there is no concrete.
The buoyancy of concrete in water is simply 2300(conctete)-1000(water)=1300 kg m^-3

You may also need to take pressure forces due to currents (if any) acting on the pump.
 
Thank you for the answer, it is not the pump itself that is going to be in water, but the pumpstation (the sump), and inside it there will be the pump. On the bottom of the pumpstation there will be a concrete foundation. This has to hold the structure down because the buoyancy will act upwards. So my question actually was, how thick and heavy must the foundation be to counterbalance the forces.

Therefore 1300 kg/m^3 is not the answer, as this is just the difference of the density of both of the concrete and the water
 
Hello Ahmed, :welcome:

You may need to collect some more information: you provide a diameter of 1.6 m for the pump station, but: is it cylindrical ? If so what height (so you can calculate the volume). What is the weight ?
And about the prospective location: still water or lots of current ? etc.

AS SG says, the concrete provides 1300 kg/m3 pull-down force, but that is a static situation.
 
You need to estimate what is the positive buoyancy of your pump station.
Without this number, how do you want to calculate the amount of concrete needed ?
1300 km/m^3 is the exact answer for concrete apparent density in seawater. This is Archimede :)

Once again, you also need to know if there are other forces applied to your system (I mean other
than the only gravity force) like a transverse pressure force due to currents that could move your
pump station. All these numbers are required to scale the amount of concrete needed to counteract
all the forces.
 
I multiplied the values first without the error limit. Got 19.38. rounded it off to 2 significant figures since the given data has 2 significant figures. So = 19. For error I used the above formula. It comes out about 1.48. Now my question is. Should I write the answer as 19±1.5 (rounding 1.48 to 2 significant figures) OR should I write it as 19±1. So in short, should the error have same number of significant figures as the mean value or should it have the same number of decimal places as...
Thread 'Collision of a bullet on a rod-string system: query'
In this question, I have a question. I am NOT trying to solve it, but it is just a conceptual question. Consider the point on the rod, which connects the string and the rod. My question: just before and after the collision, is ANGULAR momentum CONSERVED about this point? Lets call the point which connects the string and rod as P. Why am I asking this? : it is clear from the scenario that the point of concern, which connects the string and the rod, moves in a circular path due to the string...
Thread 'A cylinder connected to a hanging mass'
Let's declare that for the cylinder, mass = M = 10 kg Radius = R = 4 m For the wall and the floor, Friction coeff = ##\mu## = 0.5 For the hanging mass, mass = m = 11 kg First, we divide the force according to their respective plane (x and y thing, correct me if I'm wrong) and according to which, cylinder or the hanging mass, they're working on. Force on the hanging mass $$mg - T = ma$$ Force(Cylinder) on y $$N_f + f_w - Mg = 0$$ Force(Cylinder) on x $$T + f_f - N_w = Ma$$ There's also...
Back
Top