How to calculate Battery run-time?

AI Thread Summary
To calculate battery run-time for a UPS supplying a PC, it's essential to consider both the amp-hours and the voltage of the battery. For a 24V, 1500Ah UPS, the raw capacity is 36kWh, allowing for approximately 240 hours of theoretical run-time at 150W consumption, though practical usage should account for at least a 10% efficiency loss. It's crucial to differentiate between watts and volt-amperes, as consumer battery backups are typically rated in VA, not watts, affecting the actual run-time. For example, a 1500VA UPS may only support 900W to 600W due to varying power factors, which can significantly reduce expected run-time. Therefore, accurate calculations must include these factors to avoid overestimating performance.
Artahir
Messages
2
Reaction score
0
I can't get my head around question about energy consumption, energy supply and run-time. I think I forgot (Im sure I forgot) something in my equation. I am trying to find a way to calculate for how long could UPS supply my PC I don't know why I can't find Amp-hours of UPC on it but let's assume it's 1500Ah and my PC consumption is 150W. I tried to do some digging first I found some explanations but none of them made sense to me I feel like it can't be so complicated. Or when I found easier equations it didn't make sense (the result). could anyone give me answer?
 
Engineering news on Phys.org
What voltage is the battery in the UPS? If it is 24V, 1500Ah you have a raw capacity of 24⋅1500Wh=36kWh. Divide by 150W and you get 240h.

This is just a coarse calculation, assume at least 10% less going from theory to practice.
 
Svein said:
What voltage is the battery in the UPS? If it is 24V, 1500Ah you have a raw capacity of 24⋅1500Wh=36kWh. Divide by 150W and you get 240h.

This is just a coarse calculation, assume at least 10% less going from theory to practice.
Exactly this is my calculation which I tried based on my logical assumption. but I used Voltage 230 AC for my desk PC and it doesn't make sense because if you add Voltage it means more hours and with 230 Iam around 2k hours which is stupid right?
 
You need volt-amp-hours, not amp-hours. An APC 1500 (retail $400, so you know where that fits in their product line) stores 220 V-A-hours. (792 kJ in SI) That has the energy needed to run a 150 W device for 88 minutes: 720,000 kJ / 150 W = 5280s = 88 minutes. This is an absolute upper limit: you don't have perfect efficiency, and you can't get the last bit of charge out of the battery. APC claims 50 minutes for that load.
 
  • Like
Likes davenn
Watch out for Watts versus Volt-Amps. Consumer Battery Backup devices are advertised in VAs not Watts. Usually the Power Factor is 0.6 but some of the off-brand ones use a Power factor as low as 0.4. So a 1500VA rating could be anywhere between 900W and 600W; that is the level that the overload shutdown is set for. Also, many modern computer power supplies have Power Factor Correction built-in to keep their power factor high, 0.8 to 0.95. That being the case, the actual runtime could be only 1/2 of the 'computed' runtime. And no-load losses of Battery Backup also seem to be significant but I haven't measured them.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...