How to figure the voltage drop at different points along a circuit?
  • Thread starter Thread starter alan2023
    Voltage drop
The discussion revolves around calculating voltage drop at various points along a circuit with multiple loads positioned at different distances from the power source. Participants explore mathematical approaches to determine voltage drop, considering factors such as wire resistance and load characteristics. The conversation includes both theoretical and practical aspects of electrical circuit analysis.
  • One participant proposes a formula for calculating voltage drop for a single load and questions how to adapt it for multiple loads at varying distances.
  • Another participant suggests that the complexity of the calculation increases with constant-power loads, which can affect voltage drop significantly.
  • Some participants mention the need to consider upstream loads when calculating voltage drop at a specific load point.
  • There are suggestions to use simultaneous equations or circuit simulation software (like SPICE) to solve for voltage drop in more complex scenarios.
  • One participant provides a detailed table of circuit parameters and voltage drops for various distances, indicating a method of calculating voltage drop for each load separately.
  • Another participant questions the method of summing voltage drops from the table, suggesting a different approach based on wire resistivity.
  • Participants discuss different methods of calculating voltage drop, including the 2KIL/CM method and its relation to resistivity.
  • There is mention of the importance of drawing the circuit and including wire resistance to accurately analyze voltage drop across multiple loads.
Participants express differing views on the methods for calculating voltage drop, with no consensus on a single approach. Some agree on the need for circuit analysis while others propose different mathematical techniques. The discussion remains unresolved regarding the best method to apply in complex scenarios.
Participants highlight limitations in their approaches, such as the need for specific assumptions about load characteristics and wire resistivity. The discussion reflects varying levels of complexity in circuit analysis based on the arrangement of loads and distances from the source.
This discussion may be useful for electrical engineers, electricians, and students interested in understanding voltage drop calculations in circuits with multiple loads.
alan2023
TL;DR
How to figure the voltage drop at different points along a single circuit run connecting multiple loads along the way?
I'm trying to determine how to measure mathematically the voltage drop at various points along a circuit with loads at different points along the way. Let's assume all loads on 100% when the circuit is on. For a basic formula I use (for single phase): 2 * K-Value (12.9 Cu) * Amps * Length(ft)/Circular Mils of conductor. This works great for one load at one distance. How do you figure the wire size and voltage drop when it's one circuit with multiple loads along the circuit at various distances from the source? What I tried was just calculating each load's voltage drop at its distance. Then I added all the drops together to determine total drop and adjust wire size accordingly. My gut says I need to consider the other loads "upstream" from the load I'm calculating, as these are affecting the total amps at that point on the circuit. Am I overthinking this?
Welcome to PF.
Are you asking about how to factor in wire losses when connecting to multiple loads that are spaced at different distances from the source?
If so, that depends on the input characteristics of the loads. If they are purely resistive, then it's a pretty straightforward calculation with the wire segments replaced by their resistance.
If the loads are more like constant-power loads (like switching power supplies), things get way more complicated. A constant power load has two stable operating points in such situations: A high input voltage and low input current operating point, and a low input voltage and high input current operating point. If you have too much wire resistance so that the voltage from your source is drooping down near half of its original value for loads near the end of the wire, then those loads at the end will snap from the first operating point into the second operating point, which drags down the voltage on the wire even more. This can cause the whole power distribution network to essentially crowbar into current limit.
Let's say for this example all loads the same resistive load just different distances. All on at the same time.
The resistive loads will draw current, I = V/R, but the voltage will fall along the line.
Unless equal resistive loads are equally spaced along a ladder network, you will need to solve a set of simultaneous equations using matrices.
Alternatively, get a copy of SPICE to solve the network for you.
Then just substitute resistors for the wire lengths and the loads and solve the KCL or KVL simultaneous equations.
(Oops, Baluncore beat me to it...) :smile:
Cir. #Phase (1 or 3) (2 for 1 phase; 1.732 for 3 phase)COPPER/ALUM. (12.9/COPPER,21.2/ALUM.)AmpsDistance (feet)Applied VoltageSize Wire
1212.90.358512012
1212.90.3513012012
1212.90.3517012012
1212.90.3520512012
1212.90.3524512012
1212.90.3529012012
1212.90.3532512012
1212.90.3536512012
1212.90.3540012012
1212.90.3544012012
1212.90.3549512012
1212.90.3554512012
1212.90.3558012012
That table is from my example. All the same loads. Varying distances.
Was there supposed to be another column for the voltage seen at the load?
That's exactly what I want to figure out mathematically without measuring each one.
Well, you have two lengths of wire carrying the specified current, so just use the resistivity of the wire and the two lengths to figure out the voltage drop in the round trip of wire. Subtract that number from the applied 120Vrms source voltage to see what the voltage is reduced to at the load...
Cir. #Phase (1 or 3) (2 for 1 phase; 1.732 for 3 phase)COPPER/ALUM. (12.9/COPPER,21.2/ALUM.)AmpsDistance (feet)Applied VoltageSize WireCMV. Drop
1212.90.35851201265300.12
1212.90.351301201265300.18
1212.90.351701201265300.24
1212.90.352051201265300.28
1212.90.352451201265300.34
1212.90.352901201265300.40
1212.90.353251201265300.45
1212.90.353651201265300.50
1212.90.354001201265300.55
1212.90.354401201265300.61
1212.90.354951201265300.68
1212.90.355451201265300.75
1212.90.355801201265300.80
This is the entire table. I just did the math for each load separately. Looks like total voltage drop would be 5.91 if this is the correct method.
How are you going from your table's 0.80V to the 5.91V you mention in your reply?
Just adding all the voltage drops together in the column "V. Drop"
Sorry, that makes no sense to me. 12AWG copper wire has a resistivity of about 1.6 Ohms/1000 feet, so for your 495 foot distance for the two sections of wire you will get about 1.6 Ohms * 0.35A = 0.56V of drop. So the 120Vrms source voltage is dropped to 119.44Vrms.
I think we're getting off track. I know there are different methods of figuring voltage drop. You are using the resistivity of the copper wire. I'm using the 2KIL/CM method. That's a topic for another conversation. I guess I really just wanted to understand the science of how the voltage drop could change in different points on the circuit based on its distance from source and the loads after and before.
What's that?
As Baluncore and I said, draw your circuit with the resistances and solve the KCL simultaneous equations. If all you have is a source connected by a wire pair to a single load, it is a trivial calculation like the one I did above.
Sounds good, thank you for your time.
Mike Holt Voltage Drop This is a copy/paste from one source on that method. The chaper and tables are referencing the National Electric Code book.
Voltage Drop Using the Formula Method
When the circuit conductors have already been installed, the voltage drop of the conductors can be determined by using one of the following formulas:
VD = 2 x K x Q x I x D/CM - Single Phase
VD = 1.732 x K x Q x I x D/CM - Three Phase
“VD” = Volts Dropped: The voltage drop of the circuit conductors as expressed in volts.
“K” = Direct Current Constant: This is a constant that represents the direct current resistance for a one thousand circular mils conductor that is one thousand feet long, at an operating temperature of 75º C. The direct current constant value to be used for copper is 12.9 ohms and 21.2 ohms is used for aluminum conductors. The “K” constant is suitable for alternating current circuits, where the conductors do not exceed No. 1/0.
“Q” = Alternating Current Adjustment Factor: Alternating current circuits No. 2/0 and larger must be adjusted for the effects of self-induction (skin effect). The "Q" adjustment factor is determined by dividing alternating current resistance as listed in NEC Chapter 9, Table 9, by the direct current resistance as listed in Chapter 9, Table 8.
“I” = Amperes: The load in amperes at 100 percent, not 125 percent for motors or continuous loads.
“D” = Distance: The distance the load is located from the power supply, not the total length of the circuit conductors.
“CM” = Circular-Mils: The circular mils of the circuit conductor as listed in Chapter 9, Table 8.
I'd say this is what separates the electrical engineers from the electricians. If you have a long pair of wires with taps along the length of it, each tap drawing currents, you have to solve this by drawing out a circuit including the resistance of the wire. You will end up with a network of resistors that is solvable using basic circuit analysis.
DV1=Z1*SUM(I1,I2...In)
I1=S1/V2 and so on.
DV2=Z2*(I2,I3...In)
Usually we know Vn and then we may build the voltage line as Vn-1=Vn+DVn
DVn=Zn*In
In=Sn/Vn
If we only know V1, we must first consider all V2 to Vn equal to V1 and iterate the voltage drops as many times as we need to achieve the proposed error limit.
The result may be like this:
All currents are assumed to be equal to 0.35 A and the voltage variation at each point does not produce current change.
If the circuit consists of two conductors of the same type - forward and reverse - we will have to multiply by 2 -in the table I did not!.
Let's consider the power injected in each point is constant P(i)=I(i)*V(i)=K P=120*0.35=42 W
In this case first we take V1=V2=...Vn=120 V
I(i)=42/V(i) and finally -after 2 iterations-V13=115.0779V [the error is 0.000313%]
If the circuit consists of two conductors of the same type - forward and reverse - we will have to multiply by 2 ...
If the supply voltage was 120 VDC; and assuming 12 AWG copper, for both the supply line, and the return line; and the loads sink a constant current of 350 mA DC;
Then 115.212 volts DC would appear across the terminals of the final current sink.
Do the loads sink 350 mA RMS, or a constant current of 350 mA, alternating with supply polarity ?
Or maybe have a resistance of; 120 V / 0.342 A = 342.857 ohm.
There can be many answers to a poorly defined problem.
This is actually a real world install. The .35A loads are LED bollard lights installed along a walkway. The #12 is THHN insulated wire installed 24" underground in PVC conduit. (I believe we actually installed #10 THHN) The 120v is AC nominal voltage,(could be anywhere from 115-125v, let's figure 120v). It's one circuit connecting all the loads. Being 120v, it would be two conductors. One grounded and one ungrounded conductor. (Hot and Neutral) In my table the "distance" is the approximate distance each light is from the source (the breaker panel).
So if given this information, what would be a formula(s) for calculating what we should expect to see for voltage at any point along the circuit knowing the distances and loads before and after?
(I'm tempted to just go there and turn them on and test at different points, but I want to understand the science of this:biggrin: out of pure interest in understanding.)
Is that 0.35 amp RMS sinewave, or a fixed continuous current?
Do they each have PF control?
Can each lamp be modelled as a 120 / 0.35 = 342.86 ohm load?
Input 120 VDC. End of the line; 115.367 VDC
Yes, I believe 0.35 amp RMS sinewave. Just typical 120v AC 60 hz power you would find in the USA.
No PF control.
For simplicity, yes, just figure 120/.35=342.86 ohms.
Using Baluncore's 1m6 ohms per foot for 12 ga, and a constant current draw for each load, the resulting voltage at each load point can be calculated, with an end-of-the line value of 115.212 volts. This is hardly different from the result with a constant resistance for each load.
I suspect the result with a constant power (for constant brightness) load would also be hardly different.
For a constant, polarity dependent, current draw from a supply of, 120 VDC or 120 VACrms, without reservoir capacitor:
As above but with resistive loads:
I blame berkeman for the 1m6 ohms per foot for 12 ga.
12AWG copper wire has a resistivity of about 1.6 Ohms/1000 feet,...
Someone, sometime, had better check that number, and that it is resistance and not resistivity per foot. If we all use that number, we will all agree to six digits, accepting that reality may be different, due to alloy composition, work hardening, and absolute temperature.
I agree.
A clever PF corrected, LED controller, would supply a constant current to the LED from a reservoir capacitor, that was charged through a rectifier from the supply, with a charge current proportional to instantaneous supply voltage. That is the 120 VDC, or 120 VACrms, resistive (342.86 ohm) load model, giving an end of the line; 115.367.
  • · Replies 22 ·
  • · Replies 28 ·
15K