How to test a 1.5 pound magnesium anode

AI Thread Summary
Testing a 1.5-pound magnesium anode for grounding tracer wire involves understanding its conductivity and signal strength compared to a smaller anode. There are no established standards specifically for tracer wire grounding, which complicates testing methods. Conductivity is influenced more by the shape and surface area of the anode rather than just its weight, with deeper placement in moist soil enhancing performance. Ground resistance testers are recommended for evaluating grounding effectiveness, and larger anodes may provide better corrosion protection and longevity. Overall, the relationship between anode size and conductivity requires further investigation to determine optimal performance.
Mike Moore
Messages
2
Reaction score
0
Hello my name is Mike Moore and I work for Copperhead Industries, LLC We are a tracer wire manufacture for the underground non-metallic pipe utility sector, natural gas, water, sewer and telecom. We use magnesium anodes for grounding out the far end of the tracer wire system which completes the electrical circuit needed to carry the tracer wire signal.

My question, I need to know where or how you can test a 1.5 pound magnesium anode that's used for grounding of tracer wire and not cathodic protection. What I'm trying to find is would a 1.5 # verses a 1/2 # perform better in conductivity or signal strength. I know bigger anodes are better in corrosion protection, but does it matter in conductivity? Does distance of a tracer wire locate signal get stronger with larger anode or does size not matter when it comes to grounding and conductivity? My thought would be the longer the anode the more surface we contact the better the ground. Would a larger anode last longer?

Thanks for any guidance or answers!

Thanks,
Mike
North American Sales Manager
 
Engineering news on Phys.org
Mike Moore said:
Hello my name is Mike Moore and I work for Copperhead Industries, LLC We are a tracer wire manufacture for the underground non-metallic pipe utility sector, natural gas, water, sewer and telecom. We use magnesium anodes for grounding out the far end of the tracer wire system which completes the electrical circuit needed to carry the tracer wire signal.

My question, I need to know where or how you can test a 1.5 pound magnesium anode that's used for grounding of tracer wire and not cathodic protection. What I'm trying to find is would a 1.5 # verses a 1/2 # perform better in conductivity or signal strength. I know bigger anodes are better in corrosion protection, but does it matter in conductivity? Does distance of a tracer wire locate signal get stronger with larger anode or does size not matter when it comes to grounding and conductivity? My thought would be the longer the anode the more surface we contact the better the ground. Would a larger anode last longer?

Thanks for any guidance or answers!

Thanks,
Mike
North American Sales Manager

Hi Mike, and Welcome to the PF.

What professional/regulatory standards apply? It sounds like there should be some standards that would need to be tested to, no?
 
No there is no standard for grounding of tracer wire, but it is starting to get traction across North America. The problem for us is finding a way to test the conductivity. To understand tracer wire a little more go to www.mrwa.com and scroll down middle of page and click on tracer wire spec/ installation guide. What is the difference in cudutivity from heavy long skinny anode to fat short anode? Does greater/ more Earth surface contact make greater conductivity? Would a 1.5# anode 16" lomg be better then 1/2# 6" long? Thanks for input! - Mike
 
Wouldn't the conductivity depend much more on the shape and surface area than the weight?
 
  • Like
Likes berkeman
I work as an electrician and we use a "ground resistance tester" when we have questions of a ground being adequate.
Our unit is a fluke, but almost any quality tester manufacturer makes them. A little pricey ($1400 and up ), but indispensable
when evaluating an installation. You can set up a test with differing length rod next to each other and see where the point is where more
rod doesn't give you any less resistance.
In electrical a minimum 6' in contact with soil(90 degree angle to the ground) is required, but ground rods (copper or galvanized steel) come in 8' minimum( so you can drive them at up to 45 degrees to the ground).
Just google ground resistance tester.
 
anorlunda said:
Wouldn't the conductivity depend much more on the shape and surface area than the weight?

You are absolutely correct. The deeper it reaches down into the moist soil, and the more "salts" in the soil, the better the ground.
If we test a ground installation and it is not low enough resistance there is a method of lowering it using salts. Don't have to do that very often though.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...