Inability of Earth fault protection system

AI Thread Summary
The discussion highlights challenges in Earth fault protection systems, particularly when using three line current transformers (CTs) that can lead to spurious trips due to false zero sequence currents. A ring current transformer at the neutral point of a power transformer is suggested as a solution to enhance sensitivity and response time for Earth fault protection. However, in a specific case involving an island electrical system with an auto transformer, the protection system failed to respond adequately to ground faults. This failure is attributed to the electrical and magnetic coupling between primary and secondary windings, which causes mixing of Earth fault currents and complicates accurate detection. The inability to differentiate between primary and secondary fault currents ultimately undermines the effectiveness of the protection system.
m.s.j
Messages
212
Reaction score
1
As you know, for Earth fault protection of electrical system, the residual current measurement is often performed using the three line CTs. But in this case the protective relay must be slightly time-delayed to avoid spurious trips caused by circulation of a false zero sequence current following a brief period of saturation in the current transformers (magnetizing current, switching surge or down stream faulty). This limitation leads to too high a setting compared to the maximum available Earth fault current, and consequently to a loss of sensitivity.
This difficulty can be largely overcome by using a ring current transformer in neutral point of power transformer in order to achieve zero-sequence current measurement. In this case the Earth fault relay can simultaneously provide both rapid and sensitive Earth fault protection.
This technical recommendation is applied to a new island electrical system with power auto transformer by a design group. They used the Earth fault relay and related NCT in neutral point of auto transformer. But they had not suitable response from Earth fault protection against the occurrence of ground faults.

How can you explain the reason of protection system inability in this case?

BEST REGARDS
MSJ


------------------------------------------------
Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
 
Engineering news on Phys.org
Your quiz questions are usually out of my area of expertise, MSJ, but I'll venture a guess on this one. Since you specifically mentioned "island", I'll guess that the higher soil conductivity associated with islands in salt water oceans was causing the ground fault currents to still trip the GFCI circuit too quickly. Am I close?
 
berkeman said:
Am I close?

No my friend, the island electrical system concept is not important here.

How can we address experts and how can we adverties for our web site?


BEST REGARDS
MSJ
 
Last edited:
Because of electrical and magnetically coupling between primary and secondary windings of auto transformers, the primary and secondary Earth fault currents are mixed in neutral point of transformer. The difference phase angle between secondary current and induced primary current is approximately 180 degree, therefore the amount of through Earth fault current is the difference of Ip and Is , where the Ip and Is are the primary and secondary Earth fault current respectively. So the Earth fault protection system in neutral point can not detect actual primary or secondary Earth fault currents.
 

Attachments

  • 44.GIF
    44.GIF
    2.8 KB · Views: 506
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top