Induction Motor Query: Current, Power, Torque & Speed

AI Thread Summary
In a simulation of a three-phase induction motor, it was observed that as the supply frequency decreased from 50 Hz to 30 Hz, both current and power drawn from the supply decreased. However, below 30 Hz, the current increased while power continued to drop, raising questions about the motor's performance. This behavior is attributed to poor power factor at low frequencies, leading to increased magnetizing current as the motor approaches stall conditions. The discussion emphasizes the importance of real-world experimentation, suggesting that practical tests with a transformer and adjustable voltage source can provide insights into motor behavior that simulations cannot replicate. Understanding the concept of "Volts per Hertz" is recommended for further clarity on this phenomenon.
Physicist3
Messages
103
Reaction score
0
Hi, I am currently simulating a 3 phase induction motor system. One of the tests that I have run is to keep the motor parameters (reactance, resistance etc.) constant, and then change the frequency of the supply (50, 40, 30 Hz etc.) before measuring input parameters (current and power drawn from supply), along with output parameters such as torque and rotational speed. Throughout, I have kept the value of the voltage supply constant. Having completed the tests, I have found that when the frequency is dropped from 50 to 40, and from 40 to 30 Hz, both the current and power drawn from the supply decrease. However, when dropping the frequency below 30Hz, I have found that the current drawn from the supply increases again, yet the power (watts) continues to decrease with a constant voltage. I don't quite understand how this is possible, would it be the result of a really poor power factor at low frequency as the motor begins to stall and inductive parameters become more influential on the system?
 
Engineering news on Phys.org
It's properties of inductors allright.

You need to try this for real with a small transformer and Variac adjustable transformer.

Remember that flux is integral of voltage
so,
as you lower frequency with voltage held constant,
the period of each half cycle grows longer,
which means the integration has a longer interval,
which gives it a larger result, it is after all a definite integral;

which means flux will reach a level that's unsustainable in iron;
which means magnetizing current will go up to force the extra flux that the iron can't accept out through the air ;
which makes the motor hum and vibrate and get hot;

and your simulation will not emit the sounds and smoke that a real motor would.

That's why you need to take a small transformer, ammeter, and adjustable voltage source
and drive the little transformer into saturation while you watch current increase sharply at saturation point,
hear it hum and feel it vibrate and get hot, maybe even smell the hot insulation.

Look up term "Volts per Hertz" for a better explanation.

I encourage that experiment with real parts. It'll make your mind intuitively aware of what the math is telling you.

I appreciate the power of simulation, but it's a poor substitute for the visceral reality of a proper electric machinery lab.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...