Japan Earthquake: Nuclear Plants at Fukushima Daiichi

AI Thread Summary
The Fukushima Daiichi nuclear plant is facing significant challenges following the earthquake, with reports indicating that reactor pressure has reached dangerous levels, potentially 2.1 times capacity. TEPCO has lost control of pressure at a second unit, raising concerns about safety and management accountability. The reactor is currently off but continues to produce decay heat, necessitating cooling to prevent a meltdown. There are conflicting reports about an explosion, with indications that it may have originated from a buildup of hydrogen around the containment vessel. The situation remains serious, and TEPCO plans to flood the containment vessel with seawater as a cooling measure.
  • #8,501
There is a bit more detail on the two workers who exceeded 250mSv here:
http://jen.jiji.com/jc/eng?g=eco&k=2011053000517"

External exposure stood at 73.71 millisieverts for the worker in his 30s and at 88.7 millisieverts for the one in his 40s.

Does this mean that the internal exposure has been normalised to an annual or lifetime dose?
 
Last edited by a moderator:
Engineering news on Phys.org
  • #8,502
tonio said:
OK. Some remarks. If I am correct, the size of R4 building is 35 x 45 m. Assuming that the height of the refuelling floor is close to 15 m, it;'s volume is about 20.000 m^3, about a tenth of what you specify. This space, which I assume is well isolated (apart from the open blowout panels) and is not mechanically ventilated anymore, is heated by a large SPF, which generates about 3 MW of heat. I am not a physicist, but I assume that such a powerfull heat source, dumping an amount of steam in this space which is enough to fill it completely in just 1,5 minutes, will heat it to a temperature close to 100 degrees and will effectively refresh it's (steamy) atmosphere every few minutes.

Not a huge difference from your estimate, but the height of the refuelling floor is 15.8 m according to the drawings we've seen (for Unit 3), so volume is closer to 25,000 m3.

I would not assume the space is well isolated, however. Various diagrams and descriptions give me the impression that there are a multitude of open hatchways that connect the airspace of every floor to every other floor. If that is true then the atmosphere inside the building as a whole is communicable subject to drafts, convection, and buoyancy factors. There are probably rooms and spaces sealed off due to containment considerations.

But even then the entire volume of the building would be somewhat less than 71,000 m3 (35 x 45 x 45) because the primary containment vessel - which shuold be completely isolated - occupies some fraction of the total volume.
 
Last edited:
  • #8,503
http://ajw.asahi.com/article/0311disaster/fukushima/AJ201105300291"
http://ajw.asahi.com/article//0311disaster/fukushima/AJ201105300298" interesting !
 
Last edited by a moderator:
  • #8,504
elektrownik said:
http://ajw.asahi.com/article/0311disaster/fukushima/AJ201105300291"
http://ajw.asahi.com/article//0311disaster/fukushima/AJ201105300298" interesting !

Ah yes, Megafloat to the rescue. Again. It holds 10,000 tons of water and it has been obvious for quite a while that it's not going to be very useful. A drop in the proverbial bucket.

And hoses. TEPCO has secured hoses for Plan B. Or is it Plan C, D, E or F?
 
Last edited by a moderator:
  • #8,505
I don't know where the news reporter got this info but he seems to confirm that groundwater level is quite high:

It has not been confirmed that contaminated water has leaked into the groundwater from the basements in large quantities, but the levels of contaminated water in the basements are currently only a few meters lower than that of the groundwater.
http://ajw.asahi.com/article/0311disaster/fukushima/AJ201105300291

By the way, did you notice that he copied what jlduh said a couple of days ago (May 27th):

So what I foresee is the possibility that when the basements where almost empty (with regular pumps ejecting out the inflows from the watertable, which was probably routine operation to keep these basements dry), then of course the direction of flow was from outside to inside (because of hydrostatic differential). When the basements are filling in with water, the differential is reducing and eventually, this differential can be inverted if water level inside basement becomes higher than water table level outside. Then the flow will invert also, and so leakage from basement towards watertable can happen (with contamination).
https://www.physicsforums.com/showpost.php?p=3325027&postcount=8356

Asahi Shimbun May 30th:

As long as water is flowing from the surrounding groundwater into the contaminated water, because the level of the groundwater is higher than that in the basements, the threat of substantial leaks is not considered acute. But if the level of the contaminated water rises above that of the groundwater, water would begin flowing in the other direction and is likely to spread contamination.

:cool:
 
Last edited by a moderator:
  • #8,506
NUCENG said:
I calculated a boiloff rate based on adiabatic heating and came up with 20 m^3/sec.
How did you get these figures? I get 2 m^3 / sec.

I calculate 1.35 kg/sec boiloff rate: 3.05e6 W/(2.256e6 J/kg) These are ~75 mol, which give 22.4 * 373/273 * 75 l = 2.3e3 l = 2.3 m^3 steam - make it 2 m^3 because it is saturated and not an ideal gas.
 
  • #8,507
I don't see any solution for Fukushima (in case of water leaks), they need to inject water to RPV to cool down melted cores, they can't stop, but it look like all RPVs are leaking and drywells also so water is going to reactor and turbine buildings, and to other locations. To install cooling system they need closed loop, but to do this they would need fix at last drywell leak, but we still don't know how big is damage. In theory they could fix leak, but to do this they would need to stop water injection, but they cant, and if they could then there is also extrem radiation problem, I think that it will be not possible to work in leak location for many years, radiation would be too hight. Closed loop with reactors as water tanks is not a solution also because we know that they are not sealed and water is leaking outside...
 
  • #8,508
Borek said:
I am not so sure about stratification. Bubbles of pure hydrogen will go up, no doubt about it. But if the gases are well mixed, from what I remember stratification due to masses of molecules is negligible, as mixing due to thermal motion is way too strong. For reasonably good results you need very high towers and very low temperatures (cryogenic distillation) - neither were present.

Agreed. I was definitely thinking more of discrete pockets of gas coming out of the water that were large enough to have enough buoyancy to get significantly toward the top of the building before spreading out and mixing into the surroundings, not a nice mixture leaving the SFP. My mechanism requires that the gases aren't very well mixed when they leave the pool.
 
  • #8,509
elektrownik said:
I don't see any solution for Fukushima (in case of water leaks), they need to inject water to RPV to cool down melted cores, they can't stop, but it look like all RPVs are leaking and drywells also so water is going to reactor and turbine buildings, and to other locations. To install cooling system they need closed loop, but to do this they would need fix at last drywell leak, but we still don't know how big is damage. In theory they could fix leak, but to do this they would need to stop water injection, but they cant, and if they could then there is also extrem radiation problem, I think that it will be not possible to work in leak location for many years, radiation would be too hight. Closed loop with reactors as water tanks is not a solution also because we know that they are not sealed and water is leaking outside...

Is not the plan to have the water recycled after going through AREVAs decontamination?
If the planned 1200 ton/day processing is achieved, they can reuse the cleaned water and still gradually drain the site, because the cooling only uses about half that.
AREVA expects to process 250,000 tons of water, so they plan to be at this well into next year.
Where they put the processed water other than into the Pacific is still an open question. Presumably one could put it into an old supertanker and moor it somewhere out of typhoon prone areas, but for the cesium 137 it would only be a halflife or so before the ship rusted out completely.
 
  • #8,511
elektrownik said:
... [ignition of hydrogen in unit #4] ...

Hydrogen/oxygen mixtures can be ignited by contact with a suitable catalyst, such as certain bare metals. The catalyzer will initially combine H2+O2 flameless, but will get hot as a result. (The explosion that convinced Fleischmann and Pons that they had achieved cold fusion was later conjectured to be a chemical D2 + O2 explosion catalyzed by palladium.)
 
  • #8,512
thehammer2 said:
As the gas mixture leaves the pool, the hydrogen is MUCH less dense than the gases around it, so due to buoyancy alone, it will rise to the top and accumulate. The result is stratification, like oil floating on top of water.

This does not happen. No matter what the difference in density, gases that are mixed will stay mixed, and gases that are initially stratified will gradually diffuse into each other, even if they are kept perfectly still (without macroscopic motion). Indeed there must have been significant convection currents in the service floor of #4, because of the powerful heat+steam source in one corner.

That said, IMHO radiolysis seems a better explanation than H2 leakage from #3. I cannot see how a warm steam+H2 mixture, much lighter than air, would have chosen to travel backwards into the venting pipe of #4, and force its way through a tortuous path with several valves and tubing into a closed building with the AC turned off --- instead of flowing up the venting tower. I suppose that if some of the H2+steam from #3 managed to get into the chimney, it would have created negative pressure at its base, thus sucking back any gas that happened to flow towards #4
 
  • #8,513
~kujala~ said:
I don't know where the news reporter got this info but he seems to confirm that groundwater level is quite high:


http://ajw.asahi.com/article/0311disaster/fukushima/AJ201105300291

By the way, did you notice that he copied what jlduh said a couple of days ago (May 27th):

https://www.physicsforums.com/showpost.php?p=3325027&postcount=8356

Asahi Shimbun May 30th:



:cool:

Maybe some journalists are reading this forum :-p
Next time I will write some big BS (humm I'm sure i did already!) and we will see if they copy it :biggrin:
 
Last edited by a moderator:
  • #8,514
elektrownik said:
I don't see any solution for Fukushima (in case of water leaks), they need to inject water to RPV to cool down melted cores, they can't stop, but it look like all RPVs are leaking and drywells also so water is going to reactor and turbine buildings, and to other locations. To install cooling system they need closed loop, but to do this they would need fix at last drywell leak, but we still don't know how big is damage. In theory they could fix leak, but to do this they would need to stop water injection, but they cant, and if they could then there is also extrem radiation problem, I think that it will be not possible to work in leak location for many years, radiation would be too hight. Closed loop with reactors as water tanks is not a solution also because we know that they are not sealed and water is leaking outside...

This is called a technical NIGHTMARE. Maybe less spectacular than Tchernobyl, but much more perverse on the long run, IMHO.
 
  • #8,515
How did the area handle the storm that just went through? Or is it still going through?
 
  • #8,516
jlduh said:
Maybe some journalists are reading this forum :-p
Next time I will write some big BS (humm I'm sure i did already!) and we will see if they copy it :biggrin:

Someone stole (borrowed) my analogy to the "Titanic" and called the disaster a "Nuclear Titanic", early on. Not even so much as a thank you e mail. Sigh.
 
  • #8,517
frangin said:
@swl ,
From the same samples, Cs134 from 1600 up to 4100 and Cs137 from 1700 to 4300 becquerel/liter

i found it in this realease :

http://www.tepco.co.jp/en/press/corp-com/release/betu11_e/images/110529e3.pdf

On page two of the above quoted document, TEPCO's data indicates that the Iodine-131 level measured in water from "Screen of 1Fs unit 2 (inside the silt fence)" is much higher than the levels indicated in Units 1, 3 and (of course) 4.

Given similar starting levels it would take well over a month of decay to account for this difference. I understand that the starting points would likely have been different, so I considered the ratio between the Iodine-131 and the Cesium levels (both 134 and 137). Unit two appears to have far more Iodine relative to Cesium than any of the other units.

Unit 1: I131 650Bq/L; Cs134 1,500Bq/L; Cs137 1,600Bq/L
Unit 2: I131 24,000Bq/L; Cs134 4,100Bq/L; Cs137 4,300Bq/L
Unit 3: I131 720Bq/L; Cs134 5,100Bq/L; Cs137 5,400Bq/L
Unit 4: I131 160Bq/L; Cs134 4,500Bq/L; Cs137 4,800Bq/L (shut down mode before accident and much lower Iodine levels than the other units)

So, I am now wondering if this could be an indication that unit 2 had a criticality accident over a month after the tsunami, or is there some other likely explanation?
 
Last edited by a moderator:
  • #8,518
Here some quotes about the hydrogen collecting up in the buildings:

Borek said:
I am not so sure about stratification. Bubbles of pure hydrogen will go up, no doubt about it. But if the gases are well mixed, from what I remember stratification due to masses of molecules is negligible, as mixing due to thermal motion is way too strong. For reasonably good results you need very high towers and very low temperatures (cryogenic distillation) - neither were present.

Jorge Stolfi said:
Hydrogen/oxygen mixtures can be ignited by contact with a suitable catalyst, such as certain bare metals. The catalyzer will initially combine H2+O2 flameless, but will get hot as a result. (The explosion that convinced Fleischmann and Pons that they had achieved cold fusion was later conjectured to be a chemical D2 + O2 explosion catalyzed by palladium.)

Jorge Stolfi said:
No matter what the difference in density, gases that are mixed will stay mixed, and gases that are initially stratified will gradually diffuse into each other, even if they are kept perfectly still (without macroscopic motion). Indeed there must have been significant convection currents in the service floor of #4, because of the powerful heat+steam source in one corner.

That said, IMHO radiolysis seems a better explanation than H2 leakage from #3. I cannot see how a warm steam+H2 mixture, much lighter than air, would have chosen to travel backwards into the venting pipe of #4, and force its way through a tortuous path with several valves and tubing into a closed building with the AC turned off --- instead of flowing up the venting tower. I suppose that if some of the H2+steam from #3 managed to get into the chimney, it would have created negative pressure at its base, thus sucking back any gas that happened to flow towards #4

Just my unqualified 2 cents:
First of all, thanks to Nuceng and all the others for their valuable insights!

Please do also consider the fact that much, if not most of the steam will condensate at the walls etc due to the very low dew point.
The increased pressure even speeds up condensation.
This means that the mixture steam-hydrogen inevitably gets richer in hydrogen with time, because hydrogen cannot condensate under earthly temperatures/pressures.
Until explodable conditions have been achieved, Then just a little spark or hot surface could initiate the "kaboom procedure"...

The observation that only RB#2, the only that allowed hydrogen to escape, remained in shape, appears to confirm my hypothesis as far I see.

Compare this to a fridge where you put a pot of boiling water in. The steam will condense at the walls, some leaking out at the door, but not popping it open.
(Finally, due to lack of (pressed out) air the fridge will develop underpressure, making it difficult to open the door. Unlike a reactor...)

attachment.php?attachmentid=36063&d=1306808731.jpg
Consider this photo just before explosion.
Do you also see steam leaving through building weak points at wall/ceiling corner of reactor building #1 (left)?
Doesn't this indicate high pressure in the reactor building?
(Or maybe I misinterpret this image ? It could be Daini or some other plant?!? But what is that optical distortion looking like steam? German "Spiegel" posted this photo short before Daiichi explosion #1, with picture description suggesting it was Daiichi 1+2...)

So, could the inevitable outcome have been that eventually an explosive hydrogen-oxygen ratio developed, ready to be ignited by a slight spark or some hot surface?
 

Attachments

  • daiichireactor1beforrexplo.jpg
    daiichireactor1beforrexplo.jpg
    49.7 KB · Views: 561
Last edited:
  • #8,519
Last edited by a moderator:
  • #8,520
Atomfritz said:
...
Consider this photo just before explosion.
Do you also see steam leaving through building weak points at wall/ceiling corner of reactor building #1 (left)?
Doesn't this indicate high pressure in the reactor building?
(Or maybe I misinterpret this image ? It could be Daini or some other plant?!? But what is that optical distortion looking like steam? German "Spiegel" posted this photo short before Daiichi explosion #1, with picture description suggesting it was Daiichi 1+2...)

So, could the inevitable outcome have been that eventually an explosive hydrogen-oxygen ratio developed, ready to be ignited by a slight spark or some hot surface?
My first thought was prop wash from the helicopter causing that image distortion...? Do you have another image without the chopper?

Thanks to a number of people for all the detailed analysis in the attempt to come up with plausible scenarios for the #4 explosion/fire.
 
  • #8,521
Atomfritz said:
Here some quotes about the hydrogen collecting up in the buildings:
.
.
Just my unqualified 2 cents:
First of all, thanks to Nuceng and all the others for their valuable insights!

Please do also consider the fact that much, if not most of the steam will condensate at the walls etc due to the very low dew point.
The increased pressure even speeds up condensation.
This means that the mixture steam-hydrogen inevitably gets richer in hydrogen with time, because hydrogen cannot condensate under earthly temperatures/pressures.
Until explodable conditions have been achieved, Then just a little spark or hot surface could initiate the "kaboom procedure"...

The observation that only RB#2, the only that allowed hydrogen to escape, remained in shape, appears to confirm my hypothesis as far I see.

Compare this to a fridge where you put a pot of boiling water in. The steam will condense at the walls, some leaking out at the door, but not popping it open.
(Finally, due to lack of (pressed out) air the fridge will develop underpressure, making it difficult to open the door. Unlike a reactor...)

Consider this photo just before explosion.
Do you also see steam leaving through building weak points at wall/ceiling corner of reactor building #1 (left)?
Doesn't this indicate high pressure in the reactor building?
(Or maybe I misinterpret this image ? It could be Daini or some other plant?!? But what is that optical distortion looking like steam? German "Spiegel" posted this photo short before Daiichi explosion #1, with picture description suggesting it was Daiichi 1+2...)

So, could the inevitable outcome have been that eventually an explosive hydrogen-oxygen ratio developed, ready to be ignited by a slight spark or some hot surface?

I'm not sure where that is, but I'm confident it's not Fukushima 1. As to the distortion, I'd say it's due to hot exhaust from the heli.
 
  • #8,522
Atomfritz said:
Consider this photo just before explosion. German "Spiegel" posted this photo short before Daiichi explosion #1, with picture description suggesting it was Daiichi 1+2...)

It is not Daiichi. Check the checkers pattern :smile: and other details. The tower is very similar though, so it may be Daini.
 
  • #8,523
Jorge Stolfi said:
This does not happen. No matter what the difference in density, gases that are mixed will stay mixed, and gases that are initially stratified will gradually diffuse into each other, even if they are kept perfectly still (without macroscopic motion). Indeed there must have been significant convection currents in the service floor of #4, because of the powerful heat+steam source in one corner.

That said, IMHO radiolysis seems a better explanation than H2 leakage from #3. I cannot see how a warm steam+H2 mixture, much lighter than air, would have chosen to travel backwards into the venting pipe of #4, and force its way through a tortuous path with several valves and tubing into a closed building with the AC turned off --- instead of flowing up the venting tower. I suppose that if some of the H2+steam from #3 managed to get into the chimney, it would have created negative pressure at its base, thus sucking back any gas that happened to flow towards #4

Yeah, I retract my earlier stupid. I had a brainfart and completely forgot about the convection and the fact that the hydrogen was likely coming up premixed with the steam.

I was definitely thinking about more discrete releases that I've encountered where the gas is pure enough and in quantities where buoyancy is a factor and it can collect at low or high points.
 
  • #8,524
jlduh said:
The new live webcam is ON, you can check it by yourself...http://www.tepco.co.jp/nu/f1-np/camera/index-j.html

Following this link, I get a completely different picture than on the TBS/JNN live feed. Nice weather with almost blue skies on the first, gray and rainy on the latter ().
 
Last edited by a moderator:
  • #8,525
Atomfritz said:
snip


attachment.php?attachmentid=36063&d=1306808731.jpg



Consider this photo just before explosion.
Do you also see steam leaving through building weak points at wall/ceiling corner of reactor building #1 (left)?
Doesn't this indicate high pressure in the reactor building?
(Or maybe I misinterpret this image ? It could be Daini or some other plant?!? But what is that optical distortion looking like steam? German "Spiegel" posted this photo short before Daiichi explosion #1, with picture description suggesting it was Daiichi 1+2...)

So, could the inevitable outcome have been that eventually an explosive hydrogen-oxygen ratio developed, ready to be ignited by a slight spark or some hot surface?

Lol, I'm no power plant spotter but they looks suspiciously coal fired. There's even a coal loader in the image. Thats the quality of MSM I guess.
 
  • #8,526
Atomfritz said:
Please do also consider the fact that much, if not most of the steam will condensate at the walls etc due to the very low dew point.
I think NUCENG made a simple conversion error - it get 2 m^3/sec (see my previous post). So it is not that much. Compare it to a steam train which has about the same power (3MW for a big one is realistic).

Consider this photo just before explosion.
Do you also see steam leaving through building weak points at wall/ceiling corner of reactor building #1 (left)?
Besides it is a different NPP I think the effect is simply related to the bright sun light that is reflected towards the camera by the left building.
 
  • #8,527
Needing a mechanism to pull slight vacuum on unit 4?
when did they begin adding water to U-4's SFP?
could the building have got fairly well filled with steam from pool then cooled off?

remember the grade school science project , bring a can with some water to a boil then remove heat and cap it, watch it collapse as steam condenses.

i see from here they report injecting water to pool on 15th. surely there's a record of when they began that operation.

http://www.jaif.or.jp/english/news_images/pdf/ENGNEWS01_1300189582P.pdf
 
Last edited by a moderator:
  • #8,528
jim hardy said:
Needing a mechanism to pull slight vacuum on unit 4?
when did they begin adding water to U-4's SFP?

Good question. I believe that between the venting of #3 and the explosion of #4 the latter was completely without power, so it is not clear how they would have managed to pump water into the pool. AFAIK they would have had to rig the pipes inside the building to make it possible to pump water from outside. But the floors are all connected through the elevator shaft and the stairwells, so if they entered the building then any negative pressure inside would have immediately equalized through the entrance door. Or not?

Did they even worry about the #4 SFP before the building exploded?
 
  • #8,529
Jorge Stolfi said:
Did they even worry about the #4 SFP before the building exploded?

No, there was no something like SFP problemm, they were fighting to cool down cores... It was funy, there was nothing about SFPs but after unit 4 explosion they were confused that there is such problem...
 
  • #8,530
Just wanted you to know... This http://ex-skf.blogspot.com/" sometimes has interesting news but it also is perhaps too sensational. For instance it had a couple of days ago a piece of news about TEPCO roadmap:

http://ex-skf.blogspot.com/2011/05/kyodo-news-tepco-believes-stabilizing.html

Somebody posted in the comments a link to a presentation already posted here:

http://dels.nas.edu/resources/static-assets/nrsb/miscellaneous/SekimuraPresentation.pdf

The writer of the blog (arevamirpal::laprimavera) later makes a comment concerning the above presentation:

arevamirpal::laprimavera said...
Sekimura's slide No.18 is a blatant lie. EDG didn't work even before the tsunami, and off-site power went down because of earthquake only.

This of course is not true. AFAIK there is not a single source saying diesel generators didn't work before tsunami, I don't know where the idea has come from?

http://www.world-nuclear-news.org/RS_Massive_earthquake_hits_Japan_1103111.html
A more serious situation emerged at Tepco's nearby Fukushima Daiichi power plant, after the sudden stoppage of emergency diesel generators. These had started as expected upon automatic reactor shutdown, but stopped after one hour leaving units 1, 2 and 3 with no power for important cooling functions.
 
Last edited by a moderator:
  • #8,531
Atomfritz said:
(Or maybe I misinterpret this image ? It could be Daini or some other plant?!? But what is that optical distortion looking like steam? German "Spiegel" posted this photo short before Daiichi explosion #1, with picture description suggesting it was Daiichi 1+2...)

So, could the inevitable outcome have been that eventually an explosive hydrogen-oxygen ratio developed, ready to be ignited by a slight spark or some hot surface?

This Reuters Photo is showing the Haramati Thermal Power Plant (Coal) by Tepco. It was originally distributed by Reuters as "Fukushima Daiichi shortly before the explosion" or similar. I had written Reuters an email about it, but they apparently care little for journalistic accuracy.

You can find the plant by searching for its Japanese name "原町火力発電所" on google maps/earth.
 
  • #8,532
Explosion near reactor #4 during debris removal. TEPCO "assume" it was a buried gas tank. A what, now?

http://online.wsj.com/article/BT-CO-20110531-701810.html
 
Last edited by a moderator:
  • #8,533
Last edited by a moderator:
  • #8,534
Oil tanks at #5 and #6 may be leaking. Not good when you rely on diesels for emergency power.

http://news.xinhuanet.com/english2010/world/2011-05/31/c_13903549.htm
 
  • #8,535
From the TV Asahi website

On the afternoon of May 31st at Fukushima Daiichi there was a large explosion heard near reactor #4. The explosion is believed to have been caused by a pressurized tank rupturing.

According to Tepco, at 2:30pm today near the south side of the #4 reactor building, remote-controlled heavy equipment was being used to clear away rubble when a large explosion was heard. It is believed the machinery ruptured a tank that was buried in the rubble. Exactly what type of tank it was is now under investigation, but there was no fire and there were no injuries. There was no change in the surrounding radiation levels.

http://news.tv-asahi.co.jp/ann/news/web/html/210531044.html
 
Last edited by a moderator:
  • #8,536
zapperzero said:
Oil tanks at #5 and #6 may be leaking. Not good when you rely on diesels for emergency power.

Are the diesels already repaired? If not, oil leaks don't matter much. That is - they add to the mess, but they don't make the system more vulnerable.
 
  • #8,537
Gary7 said:
From the TV Asahi website

On the afternoon of March 31st at Fukushima Daiichi there was a large explosion heard near reactor #4. The explosion is believed to have been caused by a pressurized tank rupturing.

According to Tepco, at 2:30pm today near the south side of the #4 reactor building, remote-controlled heavy equipment was being used to clear away rubble when a large explosion was heard. It is believed the machinery ruptured a tank that was buried in the rubble. Exactly what type of tank it was is now under investigation, but there was no fire and there were no injuries. There was no change in the surrounding radiation levels.

http://news.tv-asahi.co.jp/ann/news/web/html/210531044.html

Reported by NHK as an oxygen cylinder:

http://www3.nhk.or.jp/daily/english/31_36.html

An oxygen cylinder has burst at the Fukushima Daiichi nuclear plant. But the plant operator says the blast caused no damage to the plant's facilities, and no injuries.
 
Last edited by a moderator:
  • #8,539
Borek said:
Are the diesels already repaired?

One EDG (emergency diesel generator, is this the approved initialism? alphabet soup in nuke industry is almost as bad as the army) was spared by the tsunami and this is one of the big reasons why 5 and 6 are not in the situation the rest are in. Afaicr they used that EDG exclusively to power cooling, alternatively, to the reactors and their pools until offsite power became available.
 
  • #8,540
~kujala~ said:
Just wanted you to know... This http://ex-skf.blogspot.com/" sometimes has interesting news but it also is perhaps too sensational.

The amount of bad news and utter BS s/he's wading through could make anyone a bit frantic. The source material, though? Pure gold, everything or almost everything confirmed, all open source info...
 
Last edited by a moderator:
  • #8,541
htf said:
I think NUCENG made a simple conversion error - it get 2 m^3/sec (see my previous post). So it is not that much. Compare it to a steam train which has about the same power (3MW for a big one is realistic).


Besides it is a different NPP I think the effect is simply related to the bright sun light that is reflected towards the camera by the left building.

Nope, no conversion error. When writing my post I copied the number wrong. Thanks.
 
  • #8,542
I know that some generators were in inspection/modyfication, so they were offline and doesn't turn on
 
  • #8,543
Borek said:
Are the diesels already repaired? If not, oil leaks don't matter much. That is - they add to the mess, but they don't make the system more vulnerable.

one generator (and only one) was working after earthquake (this for unit 5,6), there is power lines and generators drawing in this big report which was posted here some pages back
 
  • #8,544
tonio said:
OK. Some remarks. If I am correct, the size of R4 building is 35 x 45 m. Assuming that the height of the refuelling floor is close to 15 m, it;'s volume is about 20.000 m^3, about a tenth of what you specify. This space, which I assume is well isolated (apart from the open blowout panels) and is not mechanically ventilated anymore, is heated by a large SPF, which generates about 3 MW of heat. I am not a physicist, but I assume that such a powerfull heat source, dumping an amount of steam in this space which is enough to fill it completely in just 1,5 minutes, will heat it to a temperature close to 100 degrees and will effectively refresh it's (steamy) atmosphere every few minutes.

I used 19260 m^3 in my calculation for refuel floor volume. Did I copy another number wrong? As pointed out by others I miscopied the 2.0 m^3/sec steam rate as 20 m^3/sec.
 
Last edited:
  • #8,545
Gary7 said:
From the TV Asahi website

On the afternoon of March 31st at Fukushima Daiichi there was a large explosion heard near reactor #4. The explosion is believed to have been caused by a pressurized tank rupturing.
...
http://news.tv-asahi.co.jp/ann/news/web/html/210531044.html

Shouldn't that be May 31st? A simple typo today but in the future someone might search the thread looking for info about this latest explosion and get the wrong idea.
 
Last edited by a moderator:
  • #8,546
NUCENG, I think this is what he was referring to...
NUCENG said:
... That 20 m^3/sec will not result in a flow out the openings of 20 m^3/sec. The approximate volume of the refuel floor is about 2E5 m^3. It will be hot and humid and there will be some steam dilution and mixing of hydrogen. However over time the hydrogen concentration has 24 hours from the minimum time I calculated to accumulate to the Lower Explosive Limit in the top of the bulding.

Maybe you meant to write 2E4 cubic meters :smile:
 
  • #8,547
MiceAndMen said:
Shouldn't that be May 31st? A simple typo today but in the future someone might search the thread looking for info about this latest explosion and get the wrong idea.

Yes - thanks for that. Now fixed.
 
  • #8,548
MiceAndMen said:
NUCENG, I think this is what he was referring to...


Maybe you meant to write 2E4 cubic meters :smile:

yep. Looks like I need a new set of hands so I can count zeros.
 
  • #8,549
First step set in getting SFP under control

Cooling system being tested at No. 2 reactor

[PLAIN said:
http://www3.nhk.or.jp/daily/english/31_26.html][/PLAIN] The operator of the troubled Fukushima Daiichi nuclear power plant has installed a circulatory cooling system at one of the plant's crippled reactors.

The Tokyo Electric Power Company started trial operation of the system at the No. 2 reactor building on Tuesday.

The utility has been pumping about 50 tons of water into a used fuel pool in the building every few days.

The pool's temperature is around 70 degrees Celsius, apparently producing steam that is filling the building and resulting in a humidity level of 99.9 percent. The humidity and high radiation levels have been hampering repair work at the site.

The new system is to pump water out of the pool to a heat exchanger and return the water to the pool as coolant.

The firm says it plans to bring the pool's temperature to around 40 degrees Celsius in a month through the system.

TEPCO hopes to reduce the humidity level before installing equipment to remove radioactive substances in the building.

The cooling system is the first to be completed at the plant. The firm hopes to start operating similar systems at the plant's No. 1 and 3 reactors in June, and at the No. 4 reactor in July.
Tuesday, May 31, 2011 19:04 +0900 (JST)

SFP-2 is producing about 400kW compared to the 2 to 3 MW of SFP-4

Furthermore we soon will get to know where the steam is coming from - the fuel pool or the reactor.
Where is the steam produced in the reactor disappearing to?
 
Last edited by a moderator:
  • #8,550
But how they can do this without entering building ? And why they can't do this for other units ? Steam is not only from sfp, unit 2 is at atmospheric pressure and also we know that there is water leak from core to turbine building, so drywell/torus must be leaking also.
 