The discussion revolves around the technical aspects and current status of the nuclear plants at Fukushima Daiichi following the earthquake and tsunami in Japan. Participants are seeking reliable information regarding the operational conditions, safety measures, and potential risks associated with the nuclear reactors in the aftermath of the disaster.
  • Some participants express skepticism about the reliability of media reports and emphasize the need for technical information from official sources like TEPCO and METI.
  • There are concerns regarding the reactor pressure levels, with reports suggesting that pressure may have exceeded safe limits, which some participants describe as a significant issue.
  • Questions are raised about the likelihood of a meltdown, with differing opinions on whether this is a realistic concern or media exaggeration.
  • One participant explains the role of coolant in a nuclear power plant, noting that it is essential for cooling the reactor and managing decay heat after shutdown.
  • There is discussion about the reactor's ability to be scrammed (shut down) and the implications of losing coolant, with some participants clarifying that decay heat continues to be produced even after shutdown.
  • Concerns are raised about the explosion of the containment building and its implications for safety, with speculation about the potential release of radioactive materials.
  • Participants discuss the wind direction at the time of the explosion and its potential impact on the dispersion of any radioactive materials released.
Participants do not reach a consensus on the likelihood of a meltdown or the implications of the current situation at Fukushima Daiichi. There are multiple competing views regarding the severity of the situation and the reliability of information being reported.
Participants note the limitations of available information, including the reliance on second-hand reports and the challenges in verifying the status of the reactors and containment structures. There are also unresolved questions regarding the operational status of safety systems and the exact nature of the explosion.
  • #11,521
nikkkom said:
I don't understand this underground wall building thing. Isn't it FAR easier to achieve the same by drilling wells and periodically (say, daily) pumping water out?
Maybe just a decision to go for a more robust solution?
Pumps have been known to fail.
Of course, building a watertight underground barrier in an area prone to sizable earthquakes is not exactly something anyone does routinely either. Temblors make concrete break, as we've seen.
A freeze barrier, which freezes a large stretch by piping in a chiller material such as liquid air might be more reliable, as the breaches in the wall would self heal, but would also still depend on sustained maintenance.
  • #11,522
  • #11,523
Pumps can be repaired. It's still cheaper than huge underground wall.
  • #11,524
  • #11,525
I'm not sure the aim is to lower the water table under the plant, it may actually be the opposite. Perhaps they are thinking that keeping the natural water table high may reduce leakage of contamined water from the various basements of the plant.
  • #11,526
Well it makes sense that if it's going to leak anyway, you want fresh water leaking into the contaminated water, not the other way around.
  • #11,527
clancy688 said:
Does anyone remember the first INES-7 classification which stated something around 10%? Next came a revised number which was closer to 20% than to 10%. And now there's 40%? Just great...
It was often claimed that the estimate had gone from 10% of Chernobyl in April to 20% in June, but that is not correct. There were two estimates in April at 7% and 12% by NISA and NSC respectively (an average of 10% I guess), the lower of which was updated to 14% in June. The initially higher one (by NSC) was not revised and there was never a 20% estimate by either NISA or NSC.
I agree with your comments about TBq vs PBq. They must have missed three zeros or switched the unit.
UPDATE: They have already published http://bit.ly/uuIEY4" for the summary in the comments section, explaining that they accidentally wrote TBq where they meant PBq.
  • #11,528
LOL! That's my name there. I wrote G. Wotawa an email concerning those two values and he contacted the head scientist. I'm still a student so I never expected my name to appear in such an official paper. At least not yet. Feels nice... even if it's just a little comment. :)
  • #11,529
Hooray for peer review! And this was kind of a biggie.
  • #11,530
http://www.aec.go.jp/jicst/NC/tyoki/sakutei/siryo/sochi5/index.htm List of the documents that were distributed during the 5th meeting of the middle and long term committee that was held on 28 October. The update of the middle and long term schedule is available on http://www.aec.go.jp/jicst/NC/tyoki/sakutei/siryo/sochi5/siryo3.pdf .
http://www.asahi.com/national/update/1028/TKY201110280512.html The middle and long term committee has disclosed a draft report :
2011: start of decommissioning
about 2014: start of pool fuel removal
about 2021: start of melted fuel removal
about 2026: end of melted fuel removal
2041 or later: end of decommissioning
http://news.tbs.co.jp/newseye/tbs_newseye4863985.html Two workers were injured at Fukushima Daiichi during the disassembly of the big crane that was used to build unit 1's cover. They were hit by a bundle of diameter 36 mm steel wire that fell down.
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111028_01-e.pdf Cracks were found on a part of the ceiling crane at the the common fuel pool.
http://www3.nhk.or.jp/news/html/20111028/t10013582051000.html Three similar cracks had been found on crane axles at Kashiwazaki-Kariwa after the 2007 earthquake. As the common fuel pool must be used within 3 years during the removal of fuel from reactor building pools, Tepco will change the broken parts.
http://www.mbs.jp/news/jnn_4863874_zen.shtml A French research institute says that the release of Cs-137 into the sea is 2.16 E16 Bq, or about 30 times larger than Tepco said at the end of April (940 E12 Bq). [ http://www.irsn.fr/FR/Actualites_pr...ident_Fukushima_sur_milieu_marin_26102011.pdf in French ]
http://sankei.jp.msn.com/affairs/news/111021/dst11102117120014-n1.htm (21 October) According to Tepco, the 250 mSv/h at the 5th floor of unit 2 is probably caused by deposits on floor and walls of radioactive gasses leaked from the PCV when the reactor was hot. The peeling off of the paint on the fuel handling crane was probably caused by steam.
http://www3.nhk.or.jp/news/genpatsu-fukushima/20111029/0820_cover.html Unit 1's cover structure is now completed with its radioactive substance removing system that uses filters and could remove 90% of radiations during tests.
  • #11,531
tsutsuji said:
http://www.aec.go.jp/jicst/NC/tyoki/sakutei/siryo/sochi5/index.htm List of the documents that were distributed during the 5th meeting of the middle and long term committee that was held on 28 October. http://sankei.jp.msn.com/affairs/news/111021/dst11102117120014-n1.htm (21 October) According to Tepco, the 250 mSv/h at the 5th floor of unit 2 is probably caused by deposits on floor and walls of radioactive gasses leaked from the PCV when the reactor was hot. The peeling off of the paint on the fuel handling crane was probably caused by steam.
Tsutsuji-san, your work is the only comprehensive and careful monitoring site for the developments in this accident that I know of. No sensationalism, no preaching, just the facts. We are in your debt.
As a follow up to your last two items, it is reported that TEPCO is doubling the water injection into reactor 1 to about 8 tons/hr in conjunction with the completion of the cover structure. Presumably this increased flow plus the internal filtering are to prevent radioactive steam from contaminating the now closed off structure.
The problem is that afaik, reactor 1 is still generating well in excess of a megawatt of decay heat. That is enough in an hour to heat all 8 tons of water by 100 degrees centigrade and to boil off some of it in addition. So there will be substantial volume of radioactive steam generated inside the enclosure. TEPCO must control the flow of that steam very completely, else the enclosure becomes an instrument of contamination of all of reactor 1, mirroring the experience of the 5th floor of reactor 2.
Presumably TEPCO could curtail the steam generation with much more extensive water injection, but as the latest JAIF status report shows the water treatment facility running at about 40% capacity, TEPCO may not be able to inject more water because there is no place to store or process any more.
The impression is that while TEPCO has a grip on the situation, the margins remain pretty tenuous.
  • #11,532
Dear members of this forum!
I have just registered here and didnt follow all 700+ pages of this discussion. Howerver, i participate actively on russian analog of this topic on site atominfo.ru which now is about to turn 600+ pages. I would like to ask someone here to give me brief summary on what you think on few questions that caused controversy among us in Russia:
1. hydrogen flow path from PCV into confinements: leakage? Vented into reactor hall on purpose? Backflow? Commonalities in units 1-2-3?
2. hydrogen flow unit 4: TEPCO explanations credible?
3. what is your intuition on conditions of RPVs? Total lower plenum breach or "leakage" only?
4. Where did Unit 2 blow up? S/C?
5. Unit 1 IC failure mode?
6. Units 2,3 RCIC failure mode: S/C saturation?
7. SFP fuel damage? Any at all?
8. Very specific question on hardened vent in Unit 1.
Here is diagram:
Is it possible to tell if MO210 valve is normally open or closed? Other valves? Purpose of rupture disc if we decide valve is in closed position?
More questions coming. Thank you all.
  • #11,533
My ideas: partly guesses, partly on more solid ground:
1. Leakage past containment lid seals is probably one route, since it has been reported on several occasions that they tend to leak even during regular containment pressure testing (around 5 bar), and during the accident, the PCV pressures exceeded 8 bar.
2. I would not say it's impossible, and the higher contamination on the outside of the SGTS filters as compared to the inside filters seems to support this idea.
3. Main circulation pump seals are probably leaking at all units. In addition to that, Unit 1 appears having depressurised during the late evening of March 11, which possibly indicates a leak from the bottom of the RPV. Boiling water reactor bottom plenum is not expected to completely breach even in severe accidents - it is more probable that some instrumentation tubes and/or control rod penetrations fail first and let the corium flow out. Other units than 1 - hard to say, since in my opinion we don't even have a good idea of the extent of the core damages.
5. According to the TEPCO report to the IAEA, it appears that the unit 1 IC did not fail at all: it just was not used. At 15:03 on March 11, they closed the IC valve and at 15:07 activated the HPCI; after the tsunami the HPCI failed, but the IC was not reactivated. Around 18:18-18:25 they briefly opened the IC valve, but closed it again for another 3 hours. Around 18:30 there would probably have been so much hydrogen in the reactor, that the steam was not able to enter the IC any more. In the recent video it was shown how the water gauges at the IC:s show the tanks still to be 70 % full.
6. A plausible explanation, although I have not been able to get verification.
7. The results given in April on the unit 4 pool water samples indicate very limited (if any) damage to unit 4:s spent fuel. At Unit 3, there probably are failures in the pool due either the hydrogen explosion or the subsequent uncovery.
8. According to the TEPCO reports to the IAEA, the MO210 valve seems to be normally closed and has to be opened as part of preparations for venting. All in all, it seems a very complicated procedure, with DC current needed for the said valve, compressed air for the other valve, and the containment pressure must be high enough to break the rupture disc. My uneducated guess is, that since there's no scrubbing or filtration in the pressure relief line, they have tried to make spurious initiation of the venting improbable by providing the multiple obstacles. Which turned out catastrophical, since the failure to vent the containments in the severe accident conditions delayed the capability to pump in firefighting water and most probably made the core damages much worse than they would have been if the pressure reduction would have taken place sooner. (Another contributing factor seems to have been the design of the reactor pressure relief lines, which also require both DC current and compressed air to function, and the delay to relieve reactor pressure after the failure of the RCIC/HPCI systems seems in my opinion to have been the most significant single factor contributing to the core damages at units 2 and 3.)
I am no expert in GE BWRs (consider myself somewhat of an expert on the ASEA line of BWRs, however), and have followed the events from the other side of the globe mainly through NHK, TEPCO's reports and the wonderful contributions of Tsutsuji-san, so the answers above are not to be taken as anything more than just my personal impressions based on the data I've been able to get.
  • #11,534
Hello neighbor! While there is no consensus yet, I will attempt to summarize and others will undoubtedly correct me.
Here goes:
1. leakage, in all cases (units 1, 2 3).
2. disputed. the other theory is hydrogen produced via radiolysis of the (hot) water of the #4 SFP.
3. disputed. possibility of no RPV bottom head breaches is still being taken into consideration, at least by some.
4. S/C breach is supposed to have occurred
5. operator error or equipment failure. IC was not used to capacity.
6. apparently they did not fail, per se
https://www.physicsforums.com/showpost.php?p=3419527&postcount=10696
7. unknown, presumed to be limited
8. Vent path is supposed to be closed in normal operation. The idea is to open the valve, then wait for the pressure disk to blow when pressure reaches its preset limit.
  • #11,535
tsutsuji said:
http://www.tepco.co.jp/en/nu/fukushima-np/images/handouts_111015_04-e.pdf Infrared pictures of top parts of unit 1 and unit 3
The markings in these new IR-pictures - and also the shape of the largest hotspot (or rather "hotline") in the unit 1 -picture - seem to resolve the question about the shapes of the reactor well shield plugs used in Fukushima Daichi units. Apparently the japanese didn't like the idea of full semicircles - but instead wanted to divide the circular lids into three sections.
Another note - or rather question: What might be those hot rodlike objects just outside the Unit 3:s SPF:s NW corner? As a layman (who has only just recently found this forum) i dare not say, what I personally suspect...
  • #11,536
ppaavola said:
<..>What might be those hot rodlike objects just outside the Unit 3:s SPF:s NW corner? As a layman (who has only just recently found this forum) i dare not say, what I personally suspect...
Well, they caught my eye too :-) After considering the weather at the time and date of the recording, as displayed by the webcam, and conferring with VIS photos, I think they most likely are some parts of corrugated iron from the roof covering that have come to lie there on top of everything else, and oriented such that they are being heated by the morning sun.
  • #11,537
"and oriented such that they are being heated by the morning sun."
looks like they're 80-90F in a 65-ish ambient? sounds reasonable for warming in the sun.
IR cameras are sensitive to emissivity of a surface , so might be strips of galvanized sheet lying on rubble.
but there's been lots of peculiar shapes in the photos over these months and many of us are watching and wondering, like you.
  • #11,538
I too would guess they are just some steel girders from all the mess that
- were modestly heated up by the underlying SFP steam
- were modestly heated up by the morning sun (assuming time on photo is in Japan timezone)
The difference is 10 deg Celsius, IR camera is calibrated on quite a sensitive scale. For comparison, if we were to take those er.. rods and put them in the blueish area (removing SFP heat which has a T of about 24 Celsius relative to the 18 Celsius of other structure) they would probably glow dark yellow or light orange (28 C) in that pic.
I think if those were fuel rods the gamma emissions would be noticeable, including to the ground by gamma backscatter and we would have seen a huge robot-based effort to remove them, which didn't happen AFAIK.
  • #11,539
Also, if hot fuel assemblies were lying there now, scattered off the NW corner of the SFP. they should've lit up on the roof ever since the explosive events on March 14th, but there is no heat signature apparent in that spot in any of the early thermographs from March and April.
  • #11,540
People. Please, please for the love of Shub-Niggurath stop with the fuel rods thing.
Here's all the testing you need, to find out if used fuel rods are out in the open:
Are low-flying birds dropping dead out of the sky? (Y/N).
  • #11,541
http://www.nikkansports.com/general/news/f-gn-tp0-20111031-857148.html It was found that two rest stations, because they are located outside of the plant premises close to the western entrance gate, are not included in the radiation management area, while the radiation there is about 2 ~ 16 μSv/h. It is required by law to include into the management area all the areas where an accumulated dose of 1.3 mSv is exceeded in 3 months.
http://www3.nhk.or.jp/news/genpatsu-fukushima/20111030/0435_2gouki.html The PCV gas extraction system was started on 28 October at unit 2.
  • #11,542
tsutsuji said:
http://www.nikkansports.com/general/news/f-gn-tp0-20111031-857148.html It was found that two rest stations, because they are located outside of the plant premises close to the western entrance gate, are not included in the radiation monitoring area, while the radiation there is about 2 ~ 16 μSv/h. It is required by law to include into the monitoring area all the areas where an accumulated dose of 1.3 mSv is exceeded in 3 months.
This.
let's itemize:
1. workers STILL don't have personal dosimeters
2. the areas were not checked by a health physicist, radiation safety engineer or generally anyone with a counter prior to being designated "rest stations"
3. there is no radiation map of the entirety of the work-site. Only of the immediate environs of the NPP itself
4. monitoring is absent from areas not known to be already contaminated
Therefore, external dose estimates provided by TEPCO are based on hopium.
  • #11,544
Hello all. Long time lurker, first time poster, ETC.
I have been waiting with great interest to see Marco Kaltofen from WPI's presentation on environmental radioactivity in Japan and the US from the Fukushima disaster. This came out yesterday - http://www.fairewinds.com/content/marco-kaltofen-presentation-apha .
I have not seen the raw data, and if anyone has, a link would be great. But a couple things strike me as odd right away - first, that he reports detection of Cs-134 and Cs-137 in US soil only in two isolated locations (page 19). That seems very odd, since there's Cs-137 nearly everywhere from pre 3/11, and also there had been Cs-134 found in nearly every sample that the UC Berkeley team has tested. The second thing is that his abstract stated that an isolated soil sample in the US came back at 8nCi/kg of combined cesium activity - http://fukushimaupdate.com/radiation-exposure-to-the-population-in-japan-after-the-earthquake/. 8nCi/kg is much higher than what anyone else has reported.
Thoughts anyone?
  • #11,545
Thoughts anyone?
If I were waiting to see this presentation I would have been disappointed. I have judged high school science and engineering fair entries that had better focus and provided more cogent hypotheses to analysis to conclusion. The conclusion he draws in the last slide is not a logical result of the information he presents, but it was probably what motivated Fairewinds to post it. He presented a result of testing automobile air filters by contact on photographic or xray plates which is interesting, but withoiut quantification is pretty worthless.
Do yourself a favor and take the time to read through this thresd. You will find much more in depth discussion and analysis here than Arnie Gundersen provides at Fairewinds. If you take time to read back through this thread you will find most of the information was here already, so you really didn't need to wait.
  • #11,546
zapperzero said:
This.
let's itemize:
ZZ, did you translate the article provided by Tsutsuji to draw those conclusions, or is that the pesimistic opinion of the zapperzero we've come to know and love here? I saw nothing in the article that indicated a shortage of dosimeters. I saw nothing that indicated any worker exceeded dose limits because of the mistake. The article reported that TEPCO admitted the mistake and "poor management." Obviously they found the problem so they were monitoring the rest areas, even if it was later than the law required.
During the Great Depression American humorist Will Rogers said he never wrote a joke, he just read the newspapers and repeated the facts. We can all take that as a hint. There is so much fact about Fukushima to criticize we don't need to stretch this stuff so far. Maybe a dose of hopium would balance us all.
  • #11,547
Nuceng - Yes, I have to admit that I was dissapointed too. I expected more, mostly because this guy has done some great work. Google his name - it seems to me that his work on finding tiny amounts of plutonium etc. in dusts is pretty much in a league of its own.
I have read most of the info here on PF, and appreciate it very much, no tinfoil here.
  • #11,548
http://www.asahi.com/national/update/1102/TKY201111020003.html (2 November 05:02 AM) "Fukushima Daiichi unit 2 - Possibility of nuclear fission - Borated water injection". Short-lived Xenon was detected at unit 2. Tepco started injecting borated water at 02:50 AM on 2 November. No change was observed at monitoring posts inside plant premises.
http://www3.nhk.or.jp/news/html/20111102/t10013667531000.html (2 November 06:38 AM) Xe-133 and Xe-135 (U-235 fission products) were detected on 1 November on the measuring instruments installed near the exit of unit 2's PCV gas extraction system. As nuclear fission cannot be ruled out, Tepco started injecting borated water shortly before 03:00 AM. Reactor pressure and temperature, plant site monitoring posts are stable. Even if nuclear fission is occurring it must a small scale reaction.
  • #11,549
Thank you for the quick linking! Reading both articles, it is still not clear to me whether the installation of the gas management system allowed the measurement of the fission products, revealing a process which might have been already continuing for some time, or whether the xenon is a totally new development. Is it clearer to you?
  • #11,550
Looks like from the second article that the gas filtering and measurement system was only started on 10/28, and this was the first measurement result from that. So this may have been going on all along.
Could this provide a source term for those transient mini-spikes seen throughout the Kanto area when it is raining and the wind is coming from the power plant? (Still waiting to see an example of such a spike when the wind is not coming from Fukushima Daiichi.)