Line and Phase voltages differences

  • Thread starter Thread starter PhysicsTest
  • Start date Start date
  • Tags Tags
    Line Phase
Click For Summary
SUMMARY

The discussion focuses on the differences between line and phase voltages in three-phase systems, specifically in Star connections where the line voltage is calculated as √3Vϕ and leads the phase voltage by 30 degrees. It highlights that in inverter designs, the relationship between line-to-ground and line voltages differs, with line voltages being 120 degrees apart. The conversation raises questions about the applicability of traditional three-phase AC system principles to inverter outputs and the impact of transformer configurations, such as star to delta, on phase shifts and harmonic content.

PREREQUISITES
  • Understanding of three-phase AC systems
  • Knowledge of Star and Delta transformer configurations
  • Familiarity with inverter design principles
  • Basic concepts of harmonics in electrical systems
NEXT STEPS
  • Study the effects of harmonics on inverter output using oscilloscopes
  • Learn about the implications of phase shifts in transformer connections
  • Investigate the differences between ideal sinusoidal and non-ideal inverter waveforms
  • Explore advanced topics in three-phase system analysis, including phasor diagrams
USEFUL FOR

Electrical engineers, inverter designers, and students studying three-phase systems who seek to deepen their understanding of voltage relationships and harmonic effects in practical applications.

PhysicsTest
Messages
256
Reaction score
27
TL;DR
I want to understand the difference between the line and phase voltages.
When i study the 3 phase systems, this is want i understand for a Star connection Line voltage is ##\sqrt 3 V_\phi## and leads the phase voltage by 30Degrees.
1611981341120.png
1611981358866.png
----> eq1
So, from above we can conclude that both Line voltages and phase voltages are sine waves with phase difference.
But in case of Inverter design in place of the 3 phase system, if i refer the application note i attached, the Line to Ground or phase voltage is different from line voltages as shown below. The line voltages are sine waves with 120 degrees apart which is as expected.

1611981571108.png
1611981899883.png

Fig1 Fig2
a. Is the eq1 still applicable?
b. If the terminals coming out of the inverter let us say are R1, Y1, B1, and if i observe the waveform of R1,Y1,B1 on an oscilloscope, will i see the waveform of Fig1? and I can see the waveform of Fig2 only with differential probe?
The topic i read for 3 phase AC systems may not be directly applicable to motors alone, it is applicable to house hold supply as well. I am confused if i can compare them ?
 

Attachments

Engineering news on Phys.org
PhysicsTest said:
When i study the 3 phase systems, this is want i understand for a Star connection Line voltage is √3Vϕ and leads the phase voltage by 30Degrees.
A star to delta transformer can introduce a phase shift of ±180°±30° depending on how it is connected.
Harmonics of the fundamental may be phase shifted or canceled differently in different transformers. So the high harmonic content of the inverter voltages and currents will not necessarily allow you to follow the rules you use on an ideal sinusoidal 3PH supply.
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
3K
  • · Replies 15 ·
Replies
15
Views
6K
Replies
8
Views
4K
Replies
14
Views
5K
  • · Replies 77 ·
3
Replies
77
Views
8K
Replies
2
Views
2K
  • · Replies 39 ·
2
Replies
39
Views
5K
  • · Replies 26 ·
Replies
26
Views
3K
  • · Replies 8 ·
Replies
8
Views
4K
  • · Replies 4 ·
Replies
4
Views
1K