Long distance transmission of power

In summary, the reason given for the transmission of power by way of ac rather than by dc is that the ac voltage can be stepped up so that the current can be proportionately reduced. The resistance of the wire is calculated by taking into account the length of the wire and the current drawn. However, my long standing doubt is how the resistance of the transmission cable wire is calculated.
  • #1
ananthu
106
1
The reason given for the transmission of power by way of ac rather than by dc is that the ac voltage can be stepped up so that the current can be proportionately reduced. In that case the power loss is calculated by using the formula I^2 R. But my long standing doubt is how the resistance of the transmission cable wire is calculated? We know that the resistance of a wire increases with length. In that case, if the distance between the power plant and the receiving point, say a town, is 100 km, will not the resitance of a 100 km wire be extraordinasrily high? So, even if the current is very low, when the square of the current is multiplied by the resistance, will not the power loss increse with the increase in the distance? But, in all model calculations, resistance of the wire is kept constant. Certainly the quantity in the power formula is not the specific resistance but only the resistance. For a person well versed in this concept this question may be trivial in nature. But, I couldn't get a convincing explantion for the above doubt. Will anybody thow light on this subject?
 
Engineering news on Phys.org
  • #2
Assuming the wire stays consistent, the resistance increases linearly with length. If the resistance of a transmission wire is 1 ohm per 1000/ft, then the wire to a town 100 km away will be 100 ohms. On the other hand, by inspection of I2R, you can see the watts losses increase with the square of the current. Therefore, its easier (and more cost-effective) to increase efficiency by lowering the transmitted current than trying to decrease the wire resistance.
 
  • #3
Just to add to negitrons reason for resistive loss;
In an alternating current circuit, the inductance and capacitance of the phase conductors can be significant. The currents that flow in these components of the circuit impedance constitute reactive power, which transmits no energy to the load. Reactive current flow causes extra losses in the transmission circuit.
http://en.wikipedia.org/wiki/Electric_power_transmission#Losses"
 
Last edited by a moderator:
  • #4
Hi ananthu-
I believe some of the lowest-loss long-distance power lines are now HVDC, and not HVAC. Although I am no expert in this area, two of the reasons for this are:

1) The high voltage limit for a power line is the peak voltage. The higher the rms voltage, the lower the current and the I^2 R losses. For HVDC power transmission, the peak voltage is the rms voltage, while for HVAC power transmission, the rms voltage is only 0.707 times the peak voltage. So the rms current is lower for a HVDC transmission line. But as everyone knows, transformers (and ac power) are required to step up to HV power transmission line voltages, and down from HV power transmission lines voltages. Nilola Tesla knew this more than a century ago. So efficient and economical ac/dc and dc/ac conversion in HV power transmission systems is very important.

2) AC power transmission systems radiate power. Although 60 Hz is a very low frequency, and a very long wavelength, interstate power lines are antennas; half-wavelength is 250 Km at 60 Hz. Satellites measure significant 60 Hz power electromagnetic radiation over North America, and 50 Hz over western Europe. HVDC transmission would eliminate most of this.

Finally, I think the resististive (I^2 R) power losses for HVAC and HVDC lines is calculated and compared per Km of length, and not for theentire length, e.g., foe 100 Km in your example.
Bob S
 
  • #5
I think the main reason for using DC for long distance links is that you don't need the two distant grids to be in phase, this is especially important if the grids at each end are further linked to other grids.

I don't think radiation losses are significant compared to resistive an capacitive losses.
 
  • #6
Bob S said:
...half-wavelength is 250 Km at 60 Hz.
Bob S

Aren't you forgetting a zero?
 
  • #7
Thank you all for your kind replies. But my doubts remain mostly unanswered. If the reisistance increases with the increase in length of the wire, then the amount of current will all reduce with the length. For example a person at a distance of 100 km from the power station will draw more current than one at a distance of 200 km. But all draw the same constant rms current of 5 ampere only irrespective of their location. Hence, I think that the notion of the resistance increasing with the length does not hold water. Also, when we draw current for our domestic usage, we take one lead from the phase line and the other from the neutral line. Will it mean that every point on the entire length of the wire is at the same potential say, 220 V? In that case no current should flow throgh the wire at all as current can not flow between two points which are at the same potential! The current flows only when the phase wire and neutral wire are connected. These things terribly confuse me and the entire concepts seem vague. Do anybody have a simple explanation for the mechanisms involved in the transmission of current from the generating point and drawing of the current in the receiving points?
 
  • #8
Averagesupernova said:
Aren't you forgetting a zero?
yes, my error. Should be 2500 Km. Bob S.

To Anathu
If the reisistance increases with the increase in length of the wire, then the amount of current will all reduce with the length. For example a person at a distance of 100 km from the power station will draw more current than one at a distance of 200 km. But all draw the same constant rms current of 5 ampere only irrespective of their location. Hence, I think that the notion of the resistance increasing with the length does not hold water. Also, when we draw current for our domestic usage, we take one lead from the phase line and the other from the neutral line. Will it mean that every point on the entire length of the wire is at the same potential say, 220 V??
The I2R losses are roughly 10 % of the power consumed by the end user. If the AC transmission line is say 680 kV rather than 340 kV, then twice as much power can be transmitted on the same line with the same I2R losses. As for the potential between the lines, it is essentially the integral form of Faraday's law, where there is a magnetized rotor on an alternator at a coal-fired power plant creating a voltage between the hot and neutral wires (actually 3 hot wires and neutral), and upconverting it to 340 kV using a transformer.
Bob S
 
  • #9
ananthu said:
If the reisistance increases with the increase in length of the wire, then the amount of current will all reduce with the length.
No - current is the same along the wire, the current you put in must come out at the end.
The voltage does reduce along the wire.
If the wire has a resistance of eg 0.1ohm/Km then with a current of 100A there will be a voltage drop of 10V/km. So the voltage (above ground) at 100km will be 1000V less than at the power station and at 200km it will be 2000V less.


Also, when we draw current for our domestic usage, we take one lead from the phase line and the other from the neutral line.
In a domestic single phase the neutral line is at 0v - it's connected tp Earth at the fuse board. The 220V is between the live phase and ground.

. Do anybody have a simple explanation for the mechanisms involved in the transmission of current from the generating point and drawing of the current in the receiving points?
Does this help http://en.wikipedia.org/wiki/Three-phase_electric_power
 
  • #10
ananthu said:
But my long standing doubt is how the resistance of the transmission cable wire is calculated?

Multiply the resistance per meter of wire times the length of the transmission line.

ananthu said:
We know that the resistance of a wire increases with length. In that case, if the distance between the power plant and the receiving point, say a town, is 100 km, will not the resitance of a 100 km wire be extraordinasrily high?

Yes, the resistance will be high.

ananthu said:
So, even if the current is very low, when the square of the current is multiplied by the resistance, will not the power loss increse with the increase in the distance?

No. The power loss is simply the square of the current (flowing in the transmission line) times the total resistance from point A to point B of the transmission line.

ananthu said:
But, in all model calculations, resistance of the wire is kept constant. Certainly the quantity in the power formula is not the specific resistance but only the resistance.

The resistance of the wire is constant since the length from point A to point B (i.e. the transmission line length) does not change. Again, we are talking about the total length and not an incremental length.

Hope this helps.

CS
 
  • #11
Hi Anathu
Here is something for you to mull over.
A large fraction of end-use power is used for electric motors, especially induction motors. If the voltage on an induction motor drops by say 10%, the current INCREASES by roughly the same amount. So an I2R loss in a transmission line often leads to an INCREASE of current demand.
Bob S
 
Last edited:
  • #12
ananthu said:
For example a person at a distance of 100 km from the power station will draw more current than one at a distance of 200 km. But all draw the same constant rms current of 5 ampere only irrespective of their location.

The load is what determines the amount of current drawn. So if the same load is connected at 100 km as is at 200 km then the current in the line will be the same (i.e. the current flowing in the transmission line is constant for each scenario). However, the voltage drop (and I^2R losses) will be less at 100 km than at 200 km.

ananthu said:
Also, when we draw current for our domestic usage, we take one lead from the phase line and the other from the neutral line. Will it mean that every point on the entire length of the wire is at the same potential say, 220 V?

No. The voltage is dropped along the wire. The current is constant.

CS
 

What is long distance transmission of power?

Long distance transmission of power refers to the process of transferring electrical energy over long distances, typically through power lines and cables. This is necessary in order to bring electricity from power plants to homes, businesses, and other locations that require it for daily use.

How does long distance transmission of power work?

The process of long distance transmission of power involves converting electrical energy into high voltage electricity, which can then be sent through power lines. This high voltage electricity is then stepped down at substations along the way, until it reaches its final destination at a lower voltage that is safe for use.

What are the benefits of long distance transmission of power?

Long distance transmission of power allows for electricity to be distributed to areas that may not have access to their own power plants. It also enables the efficient transport of electricity from remote power sources, such as hydroelectric dams or wind farms, to areas with higher demand for electricity.

What are the challenges of long distance transmission of power?

One of the main challenges of long distance transmission of power is the loss of energy that occurs during transmission. This is due to factors such as resistance in the power lines and environmental conditions. There is also a risk of power outages and disruptions due to damage to the power lines.

How do scientists and engineers work to improve long distance transmission of power?

Scientists and engineers are constantly researching and developing new technologies and techniques to improve long distance transmission of power. This includes finding ways to reduce energy loss during transmission, improving the efficiency of power lines, and finding alternative methods of power transmission, such as wireless energy transfer.

Similar threads

  • Introductory Physics Homework Help
Replies
2
Views
732
  • Electrical Engineering
Replies
10
Views
4K
Replies
11
Views
1K
  • Electrical Engineering
Replies
8
Views
1K
Replies
31
Views
7K
  • Electrical Engineering
Replies
8
Views
2K
Replies
32
Views
11K
Replies
39
Views
7K
  • Electrical Engineering
Replies
9
Views
4K
  • Electrical Engineering
Replies
4
Views
9K
Back
Top