Looking for advice on a buck boost transformer....

  • Thread starter Thread starter fastjer
  • Start date Start date
  • Tags Tags
    Boost Transformer
AI Thread Summary
The discussion revolves around modifying a 45kVA GE transformer to convert 248V input to 208V output for tile kilns. The transformer is currently set up for 480V to 208V, and the user seeks guidance on wiring it correctly for the desired voltage. There are concerns regarding compliance with local building codes and NEC regulations, as well as the necessity of pulling a permit for the electrical work. The user has experience in HVAC and electrical wiring, indicating a level of familiarity with the subject matter. The goal is to achieve a functional setup that allows for safe operation of the kilns without incurring high costs for new elements.
fastjer
Messages
5
Reaction score
0
TL;DR Summary
hooking up a 45kva general transformer to buck to 208v
I have a 45kva GE transformer in the pics and here. Its set up for 480 to 208, i need to wire it for 250v to 208v. Could someone please point me to the correct diagrams for this general type of transformer?

Thank you
 
Engineering news on Phys.org
fastjer said:
Summary:: hooking up a 45kva general transformer to buck to 208v

I have a 45kva GE transformer in the pics and here. Its set up for 480 to 208, i need to wire it for 250v to 208v. Could someone please point me to the correct diagrams for this general type of transformer?

Thank you

Welcome to PF. :smile:

It looks like your images are no longer available. Can you use "Attach files" (lower left of window) or provide updated links?

Also, what is the application? What is your background?

Finally, it looks like from your post that you want to do an AC conversion to lower the working voltage of the system, but from your thread title, it sounds like you want to do a DC conversion? Please clarify. Thanks.
 
124154529_10218414252732171_1940717529288357732_o.jpg
124169505_10218414253012178_5948902519190974146_o.jpg
 
So, I have tile kilns that run on 208v, but 248v comes into my business. To replace the elements for 208 is pretty pricy. I purchased this transformer pretty cheap, it works, but just need to figure out how to buck the voltage a little and still pull about 45 amps through. This one is set up for 480, so when I hook it up the the 3 phase at my building i get 56v to neutral, or about 112 across two of the output terminals.
Background: 15 years in hvac, degree in ee (a LONG time ago), been wiring small circuits and diagnosing general stuff for a long time
 
fastjer said:
So, I have tile kilns that run on 208v, but 248v comes into my business. To replace the elements for 208 is pretty pricy. I purchased this transformer pretty cheap, it works, but just need to figure out how to buck the voltage a little and still pull about 45 amps through. This one is set up for 480, so when I hook it up the the 3 phase at my building i get 56v to neutral, or about 112 across two of the output terminals.
Background: 15 years in hvac, degree in ee (a LONG time ago), been wiring small circuits and diagnosing general stuff for a long time
Have you pulled a permit for this electrical work yet? What are your local building codes regarding this upgrade work? Are you familiar with the NEC?
 
berkeman said:
Have you pulled a permit for this electrical work yet? What are your local building codes regarding this upgrade work? Are you familiar with the NEC?
hello berkeman, we are just seeing if it works. If so, i'll pull the permit, not a big deal.
 
fastjer said:
hello berkeman, we are just seeing if it works. If so, i'll pull the permit, not a big deal.
Great, thanks.

fastjer said:
So, I have tile kilns that run on 208v, but 248v comes into my business. To replace the elements for 208 is pretty pricy. I purchased this transformer pretty cheap, it works, but just need to figure out how to buck the voltage a little and still pull about 45 amps through. This one is set up for 480, so when I hook it up the the 3 phase at my building i get 56v to neutral, or about 112 across two of the output terminals.
Background: 15 years in hvac, degree in ee (a LONG time ago), been wiring small circuits and diagnosing general stuff for a long time

So can you say which NEC regulations apply to the new installation? What do you need to install in your business to support this new electrical feed? Also, have you talked with your business insurance agent about this electrical change to your business?
 