Measuring Phase to Phase voltage using Multimeter

AI Thread Summary
Measuring phase-to-phase voltage with a multimeter involves connecting the positive probe to one phase and the negative probe to another, resulting in an RMS voltage reading that reflects the difference between the two sinusoidal voltages. Digital multimeters sample the voltage several times per AC cycle to calculate this RMS value, while analog multimeters may yield inaccurate readings at higher frequencies. The discussion emphasizes the importance of correct terminology, noting that "line-to-line voltage" is the appropriate term instead of "phase-to-phase voltage." Observations of voltage changes in a testing setup suggest that adjustments to one phase voltage can affect others, indicating potential imbalances in the system. Understanding the relationships between phase voltages and their implications for system balance is crucial for accurate measurements and analysis.
PhysicsTest
Messages
246
Reaction score
26
TL;DR Summary
Measuring the phase to phase voltage using multi meter
I want to understand the concept of measuring the phase to phase voltage using multi meter. For example if i want to measure R-Y voltage, i connect the positive probe of the multi meter to the R phase and the negative probe to the Y phase. But both phases will be sinusoidal, so how does it measure? Does it take difference? Will it consider the phase angle, is it RMS value? Please advise.
 
Engineering news on Phys.org
All multimeters do reject common mode voltage, and their output in AC mode is RMS voltage unless specified otherwise. In particular, digital multimeter measure momentary voltage difference between two phases, sampling it several times per AC period. Then the onboard MCU calculate the RMS voltage difference. Analog multimeter frequency response is slower, and RMS readings of these my be inaccurate if frequency is over 100 Hz.
 
Last edited:
  • Like
Likes berkeman
PhysicsTest said:
i connect the positive probe of the multi meter to the R phase and the negative probe to the Y phase. But both phases will be sinusoidal, so how does it measure?
In a 'clean' three phase system between phases there will be also a sinusoidal voltage. With an average multimeter it measures the same way that the single phase (to ground). Just the voltage will be higher.

In general sinusoidal voltages measured in 'AC' mode. Multimeters can use several different trick to measure AC voltage. Usually, with DC component rejected, but that's not always happens, sadly...
Also, AC measurement is expected to measure the equivalent DC value (also not always the case...)

Since you have only two points of reference, you can't measure angle (directly, with a common multimeter).

A simple example: if you have 230V AC between phase and ground, you will measure 400V AC between phases. These values are the equivalent DC voltages for a sinusoidal voltage with 325V and 565V peak.
 
Here is one cycle of three-phase voltage, with the difference between red and yellow.
The individual phases are each 230 VRMS to Neutral.
Red-Y.png
 
Last edited:
Could you please help me to replicate the same what you have created, i think it is done is Ltspice? Could you please share the model? This is the circuit i have created.
1653391192077.png

There is a related question i wanted to ask before that i want to clear this, to get difference of the sine signals, do i need to use opamp circuit in Ltspice?
The output is simple sine waves with 120 Deg phase shift.
1653391503736.png
 
PhysicsTest said:
Could you please share the model?
There is no op-amp needed. To plot a differential voltage, click and hold the node, then drag to your choice of reference voltage. You can also edit the graph titles and equations in the plot window.

Attached are .asc and .plt files. Remove the extra .txt extension that allows the text files to be attached to the post, then they will run as LTspice.

Note that I used Run, then Tools, Copy Bitmap to Clipboard, then I edited the image to relabel millisec to degrees, using the degree symbol from my Neutral label.
Also, it may be needed to set the horizontal axis to 30 deg ticks.
 

Attachments

Considering that a voltage is thought of as a DIFFERENCE in potential you can think of a voltmeter as a subtractor. Apply the probes to the points in question and it tells you the voltage between.
 
Thank you for the help, the main question i am facing is, i am involved in a testing and the setup has knobs to change any of Phase - Phase voltages ex: RY, YB, BR. The corresponding voltages are displayed on the same unit, so it is power supply and a display unit. Now i have taken few readings which i am not able to understand,
RY YB BR
481V 478V 482V -> Initial set voltages
452V 478V 452V -> Changing the RY voltage to 452V changes BR to 452V automatically, YB remains same.
400V 478V 400V -> Changing the RY voltage to 400V changes BR to 400V automatically.

Similar phenomenon happens for other phases if i change one particular phase, one other particular voltage changes and one voltage does not change.
I don't see the 3 phase voltages add up to 0 in the 2nd case and 3rd case. Does it mean the 3 phase voltage is imbalanced or anything that i am missing? The RY, YB, BR are assumed notations.
 
PhysicsTest said:
Does it mean the 3 phase voltage is imbalanced or anything that i am missing?
Draw a triangle with all internal angles equal to 60°. Label the corners R, Y and B. Make the edge lengths equal to the phase-phase voltages. Since the triangle must close and the phases or angles are fixed, there is a dependence between the edge lengths or voltages.

The neutral will be near the centre of the triangle. If you change one neutral to phase voltage, then two associated phase-phase voltages must also change.
 
  • Like
Likes PhysicsTest, Averagesupernova and DaveE
  • #10
Sorry for delay, i tried hard to understand how do i approach, when i have to maintain 60 degrees,
1653704618628.png

if i shift the Neutral point to Neutral1 point, the lengths of L_RY, L_BR, L_YR will still remain the same. Can you please give one hint to proceed further, I am struck.
 
  • #11
PhysicsTest said:
Sorry for delay, i tried hard to understand how do i approach, when i have to maintain 60 degrees,
View attachment 302009
if i shift the Neutral point to Neutral1 point, the lengths of L_RY, L_BR, L_YR will still remain the same. Can you please give one hint to proceed further, I am struck.
While 60o is the nominal phase difference, it won't always be that in unbalanced cases. A triangle with 3 60o angles must be equilateral. You have a triangle with 400, 478, and 400 sides, that one will have angles of 53o, 53o, and 73o.

https://www.calculator.net/triangle...&vy=400&va=&vz=478&vb=&angleunits=d&x=69&y=16
 
  • #12
PhysicsTest said:
Can you please give one hint to proceed further, I am struck.
I may have confused you with the deviation from the ideal equilateral triangle.

Start with neutral at the origin. The reference phasor is drawn along the +x-axis. The other two phasors, lie on radial lines from the origin, spaced 120° from the x-axis.

Measure the three phase-neutral voltages, then plot each along the appropriate 120° radial. Join those three points to make a triangle. The edge lengths should then equal the phase-phase voltages.

If you have only the phase-phase voltages, you can draw a triangle with those edge lengths. Then drop that triangle, so the corners fall on the 120° radials. The distances from the origin to the points are then the phase-neutral voltages.
 
  • #13
PhysicsTest said:
Thank you for the help, the main question i am facing is, i am involved in a testing and the setup has knobs to change any of Phase - Phase voltages ex: RY, YB, BR.
It appears that when you change the RY voltage, it is actually changing the RN voltage, which is why the BR voltage also changes in the same direction as RY.

Maybe the knob on the power supply that you thought changed RY, actually changes RN only, with implications to both the displayed RY and BR.
 
  • Like
Likes DaveE and PhysicsTest
  • #14
trurle said:
All multimeters do reject common mode voltage, and their output in AC mode is RMS voltage unless specified otherwise. In particular, digital multimeter measure momentary voltage difference between two phases, sampling it several times per AC period. Then the onboard MCU calculate the RMS voltage difference. Analog multimeter frequency response is slower, and RMS readings of these my be inaccurate if frequency is over 100 Hz.
Your terminology is incorrect. There is NO SUCH THING as a 'phase to phase voltage. The correct term is 'line to line'. Phase voltages are measured ACROSS phases; line voltages are measured BETWEEN lines. The same applies to labelling. Lines and line terminals are labelled A,B,C (etc.); phases are labelled A-B, B-C, and C-A.
 
  • Like
Likes Averagesupernova
  • #15
awaygood said:
The correct term is 'line to line'.
Or "phasor to phasor", since the electrical conductor is a phasor in the mathematics.
 
  • #16
awaygood said:
Your terminology is incorrect. There is NO SUCH THING as a 'phase to phase voltage. The correct term is 'line to line'.
Electrical energy is commonly distributed using a three-phase transmission line. The balanced 3Φ transmission line has three conductors, called phases. The system is specified by “line voltage” which, for an ideal line, is the voltage difference measured between any two of the three phases.
https://en.wikipedia.org/wiki/Three-phase_electric_power#Principle

Since there is only one "transmission line", the concept of a line-to-line voltage does not seem to be meaningful.
 
  • #17
As it's used here, the 'line voltage' is the voltage of a phase relative to ground (so it's about everyday appliances).
The 'phase voltage' usually refers to a phase-to-phase voltage (thus clarifying that it's usually some serious machinery with all three phase present).
 
  • #18
Rive said:
As it's used here, the 'line voltage' is the voltage of a phase relative to ground (so it's about everyday appliances).
That use is restricted to the domestic world of a single phase.

Rive said:
The 'phase voltage' usually refers to a phase-to-phase voltage (thus clarifying that it's usually some serious machinery with all three phase present).
I disagree with that statement.
A phase voltage is a phasor, measured relative to the neutral origin.
That is the mains voltage as measured by a single phase residential contractor.
 
  • #19
Baluncore said:
I disagree with that statement.
The 'here' above refers to the country (where I live).
May be right or wrong, but the down to earth wire cutter people will give you only the funny look, you know...

Well, the point actually was that before a general 'terminology is incorrect' statement it may wort to clarify the actual environment/context it's based on, since terminology do vary - while the meaning not so often.
 
  • #20
I agree that the terms are to some extent flexible and colloquial. In this postmodernist world, there are as many truths as there are observers, and no one is wrong.

But the mathematical basics and terms are reasonably well-accepted, and are used in the Wikipedia article.
https://en.wikipedia.org/wiki/Three-phase_electric_power#Principle
 
  • #21
If you examine a three-phase line diagram, delta or wye, it should be obvious that while you can measure the voltage across phase (phase voltage), you cannot measure a 'phase to phase' voltage. The expression, 'phase to phase' is widely used but completely incorrect... the correct expression is 'line voltage' or 'line to line voltage'. I suggest visiting www.professorelectron.com for an article on the correct terminology for describing three-phase measurements.
 
  • #22
Baluncore said:
Electrical energy is commonly distributed using a three-phase transmission line. The balanced 3Φ transmission line has three conductors, called phases. The system is specified by “line voltage” which, for an ideal line, is the voltage difference measured between any two of the three phases.
https://en.wikipedia.org/wiki/Three-phase_electric_power#Principle

Since there is only one "transmission line", the concept of a line-to-line voltage does not seem to be meaningful.
No, the three conductors are called 'lines'. The 'phases' are the three windings of a generator or transformer and the three loads which are connected in wye or delta. Which is why you CANNOT measure a 'phase to phase' voltage -it simply doesn't exist. See article on this subject www.professorelectron.com
 
  • Like
Likes Averagesupernova
  • #23
awaygood said:
No, the three conductors are called 'lines'.
Or legs. I at one time was very guilty of incorrectly using the word phase instead of leg or line.
-
@Baluncore line-to-line voltage is phase voltage.
 
  • #24
awaygood said:
If you examine a three-phase line diagram, delta or wye, it should be obvious that while you can measure the voltage across phase (phase voltage), you cannot measure a 'phase to phase' voltage. The expression, 'phase to phase' is widely used but completely incorrect... the correct expression is 'line voltage' or 'line to line voltage'. I suggest visiting www.professorelectron.com for an article on the correct terminology for describing three-phase measurements.
OK, I won't argue with the pedantry, because I don't know or care what's precisely correct, nor do I even know who would decide. But, in my experience as a practicing EE with 3 phase fed power supplies, everyone in the lab will know exactly what you are referring to if you say "line to line", "phase to phase", "leg to leg", etc.

Part of our job as EEs is to communicate well with others. Some of those people learn at different schools, different times, different countries, in different languages, etc. Sometimes it's a rectifier, sometimes a diode, sometimes a valve. Sometimes it's a phase, line, leg. Whatever, I'll do my best to adjust and communicate as needed, even with the grammar police.
 
  • Like
  • Love
Likes hutchphd, Tom.G and anorlunda
  • #25
DaveE said:
OK, I won't argue with the pedantry, because I don't know or care what's precisely correct, nor do I even know who would decide.
Yet you felt the need to reply. Start dealing with rotary phase converters and you may change your opinion.
 
  • #26
Averagesupernova said:
Yet you felt the need to reply. Start dealing with rotary phase converters and you may change your opinion.
Spec'd some, but never really worked with them. But, no, I don't think I will change my opinion. In fact, I think it adds to my argument. It's not enough for you to know the correct phrase, you have to know that the other guy knows it too. So, in my experience the answer is either obvious, like a 4-wire WYE where different styles can be accommodated; or you must have a more detailed description like "H1-H3 Voltage" presumably with a drawing associated with it. The grammar pedantry is either overkill or insufficient.

However, you are correct that I tend to overreact when I think people stress learning jargon over understanding concepts and then communicating as necessary. I spent some time working with really good engineers that learned their material well, but in different countries with different phrases. We did not waste time on who was right, but we did ask for clarification from time to time.
 
  • Like
Likes hutchphd and Tom.G
  • #27
DaveE said:
It's not enough for you to know the correct phrase, you have to know that the other guy knows it too.
Well that's generally how good communication works.
-
Single phase requires 2 conductors. In the USA we have split phase so there are two hots and a neutral but that is irrelevant. Two lines or legs, whichever is prefer, gets you one phase. A phase converter manufactures one extra line/leg but in doing so gains two phases. The original single phase source provides two lines/legs (one phase) for the three phase motor load. The final output looks like a high leg delta. Doubt you've ever heard it called a high phase delta. A high leg delta has one winding of a transformer center tapped and grounded. This allows single phase 120 or 240 volt loads the same way we have single phase in most residential services.
-
Then we also have corner grounded delta. This type of service is exactly as it sounds. Three transformer windings are configured in a delta with one corner grounded. We still have voltage between A-B, A-C, and B-C. But we only can measure voltage between ground and two legs. More than one newb electrician has scratched their heads over that configuration.
-
If you prefer to mix and match your vertices with the sides of a triangle I guess that's your business. You or your approach will not be taken seriously by those who work with three phase routinely.
 
  • #28
Averagesupernova said:
Well that's generally how good communication works.
-
Single phase requires 2 conductors. In the USA we have split phase so there are two hots and a neutral but that is irrelevant. Two lines or legs, whichever is prefer, gets you one phase. A phase converter manufactures one extra line/leg but in doing so gains two phases. The original single phase source provides two lines/legs (one phase) for the three phase motor load. The final output looks like a high leg delta. Doubt you've ever heard it called a high phase delta. A high leg delta has one winding of a transformer center tapped and grounded. This allows single phase 120 or 240 volt loads the same way we have single phase in most residential services.
-
Then we also have corner grounded delta. This type of service is exactly as it sounds. Three transformer windings are configured in a delta with one corner grounded. We still have voltage between A-B, A-C, and B-C. But we only can measure voltage between ground and two legs. More than one newb electrician has scratched their heads over that configuration.
-
If you prefer to mix and match your vertices with the sides of a triangle I guess that's your business. You or your approach will not be taken seriously by those who work with three phase routinely.
Oh yea, I know those monstrosities. OK for air conditioners in west Texas. We absolutely forbade it for our Ion Lasers, Applied Materials and such forbade it for their semiconductor processing equipment. I trained our field service engineers to first off always measure 6 voltages under load, 3 line to line, plus 3 line to ground (we were Δ, so they could ignore the neutral). Then if they weren't balanced, tell us the numbers. No special names, no trusting the facilities guy, just 6 measurements for starters. I don't care what they called it, I want the data, which was really easy to get, often by just asking the customer to measure it for us.

You did a nice job of describing a couple of power systems in this case. It was clear and didn't take too long to do. I didn't have to learn what a "high leg delta" was or wonder if we agreed. It was more efficient in this case than using slightly obscure names. Good engineers know lots of stuff without knowing what it's called by the other guy.
 
  • Like
Likes hutchphd and Rive
  • #29
Averagesupernova said:
Or legs. I at one time was very guilty of incorrectly using the word phase instead of leg or line.
-
@Baluncore line-to-line voltage is phase voltage.
No. A 'line to line' voltage is a 'line voltage'. There is NO SUCH THING as a 'phase to phase voltage'. See explanation at www.professorelectron.com
 
  • #30
awaygood said:
There is NO SUCH THING as a 'phase to phase voltage'.
"Two fundamental terms which frequently cause confusion, when studying three-phase alternating-current systems are: ‘phase‘ and ‘line‘. This is hardly surprising, because the terms are often used quite incorrectly, not only in the field, but very often, unfortunately, in textbooks too!" - professorelectron

But, you see, those terms do exist, you and this professor guy just don't like them and wish they would be used "properly". Good luck with that. I, for one, won't say you're wrong. I also won't help you fix it.

Kind of like how I hate the word irregardless. I doubt that I'll fix that either.
 
  • #31
I can work with professorelectron. I just need a couple of different hats that I can change as I think about the different parts of the system.

A phase voltage and a phase current refer to a single physical internal phase-winding of a generator, transformer, or a load. Those three internal phases can be connected in wye or delta to the terminals. The internal term “phase” does not reach the line terminals.

I must remember that a line voltage is measured between two lines, but a line current is measured on only one line.
 
  • #32
DaveE said:
"Two fundamental terms which frequently cause confusion, when studying three-phase alternating-current systems are: ‘phase‘ and ‘line‘. This is hardly surprising, because the terms are often used quite incorrectly, not only in the field, but very often, unfortunately, in textbooks too!" - professorelectron

But, you see, those terms do exist, you and this professor guy just don't like them and wish they would be used "properly". Good luck with that. I, for one, won't say you're wrong. I also won't help you fix it.

Kind of like how I hate the word irregardless. I doubt that I'll fix that either.
I absolutely agree that these terms DO exist, particularly in the field. But they simply don't make sense and those who wish to learn about three-phase circuits would be better off if they learned to use the correct terminology. And as this is a science/engineering site, doesn't it also make sense if everybody used the correct terminology? So, let's think about it. There are three windings in a wye connected transformer. These are the 'phases' of that wye connection. So what ARE you describing when you say 'phase to phase'? Are you describing the voltage cross the outer limbs of two phases? There are three windings in a delta connected transformer. These are the 'phases' of that delta connection. So what ARE you describing when you say 'phase to phase'? Are you describing the voltage cross one of those three phases? When you take about a 'phase-to-phase' voltage, I assume you are describing a 'line voltage' as opposed to a 'phase voltage'? So does't it make sense to describe a 'line voltage' as the 'voltage between lines', and a 'phase voltage' as a voltage across phases? The terms 'line to line voltages' and 'phase voltages' are absolutely clear with no room for misunderstanding. If you look at either a wye or a delta connection, 'phase to phase' is ambiguous... especially for those learning about three phase ac theory.

.
 
  • #33
awaygood said:
I absolutely agree that these terms DO exist, particularly in the field. But they simply don't make sense
The really interesting part is, that whether the participants of an international educational forum, with very heterogeneous knowledge, origin and background should be spammed to use a terminology which you think makes sense, or should they be allowed to keep the terminology what their local mentor (and likely: safety supervisor) and team/labmates thinks makes sense.
 
  • Love
Likes Tom.G
  • #34
Rive said:
The really interesting part is, that whether the participants of an international educational forum, with very heterogeneous knowledge, origin and background should be spammed to use a terminology which you think makes sense, or should they be allowed to keep the terminology what their local mentor (and likely: safety supervisor) and team/labmates thinks makes sense.
I have heard electricians saying that 'Ohm's Law is universal', 'energy is delivered to a load by electrons', 'work and heat are forms of energy', and numerous other misconceptions. Are you suggesting that, because a concept is widely misunderstood, it should not be challenged? Regarding the terminology of three-phase circuits, it's not a matter of what I think is correct. I'd LOVE to hear your explanation of why a 'line voltage' should be expressed as a 'phase to phase voltage' and why students wouldn't be confused between 'phase to phase voltage' and 'phase voltage'?

Incidentally, I assume you use the terms 'line current' to describe a current passing along a line conductor, and 'phase current' to describe a current passing through a phase winding or load. If so, why not 'line voltage' to describe voltages across pairs of lines, and 'phase voltage' to describe voltages across phase windings or loads?
 
Last edited:
  • #35
awaygood said:
No. A 'line to line' voltage is a 'line voltage'. There is NO SUCH THING as a 'phase to phase voltage'. See explanation at www.professorelectron.com
Could you please show me where I said phase to phase voltage?
 
  • #36
Averagesupernova said:
Could you please show me where I said phase to phase voltage?
I didn't say YOU, specifically, said that. I was referring to the general thread.
 
  • #37
awaygood said:
I didn't say YOU, specifically, said that. I was referring to the general thread.
Then don't quote me.
 
  • #38
If you didn't say it, then how could I have quoted you?
 
Last edited:
  • #39
awaygood said:
If you didn't say it, then how could I have quoted you?
Your post #29 did quote @Averagesupernova. He is saying that your response was not appropriate to the post of his that you quoted, post #23, since in that post he did not use the phrase "phase to phase voltage".
 
  • Like
Likes Averagesupernova
  • #40
Here is a definition of the term "phase voltage" as a conductor voltage relative to neutral.
https://en.wikipedia.org/wiki/Three-phase_electric_power#Terminology
Throughout the article that follows, the terms “phase”, "phases", and "phase voltage" are used to refer to the 3φ line conductors.

Where is there something more reliable than the professorelectron blog, that defines these terms?
 
  • #41
Unfortunately, the Wikipedia article contradicts itself with its terminology. I would simply argue that the term 'line voltage' defines the voltage between any pair of the three supply conductors and, therefore, 'line voltage' describes the voltage between any pair of LINES (i.e. 'line voltage' = 'line-to-line voltage'). The term 'phase-to-phase' is confusing because lines aren't phases, they're lines! The expression 'phase-to-phase' is confusing... e.g. does 'phase-to-phase' apply to both delta AND wye, or one but not the other? Again, I would argue that newcomers to the subject will be confused by 'phase-to-phase' if you are measuring voltages between lines. I fully realize that this term (phase-to-phase) is widely used in the field, but our duty as educators is to be more precise than that.
 
  • #42
awaygood said:
Phase voltages are measured ACROSS phases; line voltages are measured BETWEEN lines.
I have just read this and I suspect you think you have made it totally clear. However, any 'Voltage' is measured relative to something. When you say "across phases", do you mean the volts between pairs of 'phases' or phase-ground volts? Measuring volts implies attaching your meter to two physical points on lines so what are you trying to highlight in that sentence?

Is all this not just basic theory? A diagram with agreed notation could help.
 
  • #43
awaygood said:
I fully realize that this term (phase-to-phase) is widely used in the field, but our duty as educators is to be more precise than that.
I am not interested in the opinion of the many players.
I am asking for a highly reliable reference, that defines the terminology.
If that can be found, then Wikipedia may need to be corrected.
 
  • #44
Sophiecentaur, 'Voltage' is NOT measured 'relative to something'. Voltage is absolute. You are confusing 'potential' with voltage. Voltage is simply another word for 'potential difference', not 'potential'. Potential is always expressed as being 'with respect to' some fixed reference point. Potential is analogous with 'height' because height is always expressed relative to some arbitrary fixed point (e.g. 'above sea level', or from 'the base of a mountain') -change the reference point you change the height (potential), whereas voltage (potential difference) is analogous with a 'difference in height' which is fixed.
When I say 'across phases', I mean across opposite ends an individual phase winding (in the case of a transformer or generator) or across opposite sides of an individual load... whether they be wye or delta connected. You ask for a diagram, so can I direct you to this topic discussed on the blog: www.professorelectron.com? There, you will find diagrams which describe exactly where 'lines' start and end and where 'phases' start and end. Finally, I would suggest that 'line voltage' describes the voltage between any (pair) of lines... i.e. it's a 'line-to-line voltage', and NOT a 'phase-to-phase' voltage.
 
  • #45
Bulancore... Well, I could refer you to the IEC (International Electrotechnical Commission) definitions, in which 'line voltage' is defined as 'the voltage between two line conductors', and where 'phase-to-phase voltage' is described as 'deprecated'? Or to the UK's BS 7671 'Electrical Wiring Regulations' which after years of describing the 'hot' conductor as 'phase wire', now describes it as 'line'.
 
  • #46
@awaygood
If you were to question members over their statements there might be some education possible, but if you insist they are wrong, then you make yourself look like a gaslighter, one who operates by undermining rather than educating or accepting. The gaslighter is a particularly dangerous species of troll and will need to be banned.
To be part of this community, you must produce more solid references to definitions, so members can see where they are wrong, not be told that they are wrong.
https://en.wikipedia.org/wiki/Gaslighting
 
  • Like
Likes BvU
  • #47
awaygood said:
Bulancore... Well, I could refer you to the IEC (International Electrotechnical Commission) definitions, in which 'line voltage' is defined as 'the voltage between two line conductors', and where 'phase-to-phase voltage' is described as 'deprecated'? Or to the UK's BS 7671 'Electrical Wiring Regulations' which after years of describing the 'hot' conductor as 'phase wire', now describes it as 'line'.
Perhaps you can provide a link ? I find their website particularly chaotic and every time I am almost where I think I want to be -- a login is required
:frown:

And a reference for
awaygood said:
'Voltage' is NOT measured 'relative to something'. Voltage is absolute. You are confusing 'potential' with voltage. Voltage is simply another word for 'potential difference', not 'potential'. Potential is always expressed as being 'with respect to' some fixed reference point.
would be nice too.

I have a firm impression the participants are in full agreement, just unable to communicate that.

##\ ##
 
  • Like
Likes anorlunda
  • #48
BvU said:
I have a firm impression the participants are in full agreement, just unable to communicate that.
I am NOT in agreement w/ his statement that 'Voltage' is NOT measured 'relative to something'

What does he think is the voltage on the + terminal of a AA battery? According to him you can't measure it relative to the negative terminal, because that WOULD be measuring it relative to something. So ... what could it possibly be?
 
  • #49
Bulancore... Well, I could refer you to the IEC (International Electrotechnical Commission) definitions, in which 'line voltage' is defined as 'the voltage between two line conductors'.
Baluncore said:
I can work with professorelectron. I just need a couple of different hats that I can change as I think about the different parts of the system.

A phase voltage and a phase current refer to a single physical internal phase-winding of a generator, transformer, or a load. Those three internal phases can be connected in wye or delta to the terminals. The internal term “phase” does not reach the line terminals.

I must remember that a line voltage is measured between two lines, but a line current is measured on only one line.
Spot on!
 
  • #50
phinds said:
I am NOT in agreement w/ his statement that 'Voltage' is NOT measured 'relative to something'

What does he think is the voltage on the + terminal of a AA battery? According to him you can't measure it relative to the negative terminal, because that WOULD be measuring it relative to something. So ... what could it possibly be?
Let me put it this way. The 'potential difference' (voltage) across an AA cell is 1.5 V. Period! The 'potential' of the positive terminal, RELATIVE TO THE NEGATIVE TERMINAL, is +1.5 V. The 'potential' of the negative terminal, RELATIVE TO THE POSITIVE TERMINAL, is -1.5 V. Better still, let's consider two AA cells in series. The potential difference (voltage) across this arrangement is 3 V. Period! The potential at the positive end, WITH RESPECT TO THE NEGATIVE TERMINAL OF THE SECOND CELL is +3 V. The potential at the positive end, WITH RESPECT TO THE CONNECTION BETWEEN THE TWO CELLS, is +1.5 V. The potential at the centre, with respect to the positive terminal, -1.5 V, whereas the potential at the centre, with respect to the negative end is +1.5V. So, 'potentials' are very much dependent on where the reference point is, whereas the potential difference (voltage) is fixed.
 