Metering a Single Phase 208 VAC Circuit

  • Thread starter Thread starter aemla
  • Start date Start date
  • Tags Tags
    Circuit Phase
Click For Summary
To measure a single-phase 208 VAC circuit using a three-phase energy meter, understanding the phase angle between voltage and current is crucial for calculating active power. The discussion highlights the challenges in finding meters that can measure the phase angle between line-to-line voltage and current without a neutral reference. While traditional electromechanical meters are still used, digital meters offer more data but often lack the capability to measure phase angles directly between phases. The conversation emphasizes the importance of measuring real power for billing purposes, with some participants confirming that the PowerLogic PM5300 can effectively measure active power in this configuration. Accurate calculations require careful consideration of the phase relationships and the limitations of the measuring instruments used.
  • #31
Averagesupernova said:
This is not true. 3 phase delta connected secondaries can have a different load on each phase with no neutral required.
You're right, I was referring to the 3 phase wye, should of read up on delta too:0
 
Engineering news on Phys.org
  • #32
Windadct said:
The issue here is yu need to see the vector relationship of the two phases - you can not just ADD apparent power like that, sorry that is just not how it works.

The 1 A you show as L-N is not the same phase angle as L-L.

The wiring of the meter - and the specific connection of the Voltages and the CTs - sets an expected phase shift between the measurements.

In a meter set up with Phase CTs ( current) and L-N Voltages the calculation per phase has no phase shift due to the connections - BUT when you look at Phase to Phase (L-L) voltages vs the Phase CT - there is a 30 Degree shift in the SENSING - that the meter accounts for.

View attachment 285556

I am quite sure if you look at REAL power (active) using data from the meter - they WILL sum properly.
I attached an example of real measurements (please ignore the highlights and incorrect L2 data [must of been a bad CT installation]). Point being, meter summed up individual phase results for the final totals.

Are you referring to phase shift of two voltage waves? I was referring to the phase shift between a voltage and a current wave. I suspect that's why there is an actual reading for "Phase Angle L1" and "...L2".

1625622733219.png
 
  • #33
Since you are using a WYE-connected source, is there a reason you can not connect that meter 'N' to the center (common) of the source?

According to the datasheet for the meter, the Neutral is used only for its internal power supply. Then you can use a connection as shown on the pages around page 22 on the datasheet.

For this to work the current measurement would have to sense only the desired load, that is measure at or in the specific load in question. Since Current Transformers are assumed, you would need only signal wires back to the meter.

Cheers,
Tom
 
  • #34
I would have expected the results your attachment shows. If you connect a load between L1 and N that is what it is. Between L2 and N and that is also whatever it is. The power dissipated in the two separate loads add up. There is no reason to worry about phase.
-
I'll throw another curve at you. In the real world example in question, there is neutral current. However, it will not be the difference in current between leg one and leg two. Phase difference will come into play here. In a previous post you said that current imbalances in 3 phase wye guarantees neutral current. This is also not necessarily true. If the loads are connected between the legs and neutral then yes, current imbalances will cause current to flow in the neutral. But if the loads are connected only between the legs, it doesn't matter. There will be no neutral current.
 
  • #35
Tom.G said:
Since you are using a WYE-connected source, is there a reason you can not connect that meter 'N' to the center (common) of the source?

According to the datasheet for the meter, the Neutral is used only for its internal power supply. Then you can use a connection as shown on the pages around page 22 on the datasheet.

For this to work the current measurement would have to sense only the desired load, that is measure at or in the specific load in question. Since Current Transformers are assumed, you would need only signal wires back to the meter.

Cheers,
Tom
I believe below is what you are describing.

1625629722079.jpeg
 
  • #36
Averagesupernova said:
I would have expected the results your attachment shows. If you connect a load between L1 and N that is what it is. Between L2 and N and that is also whatever it is. The power dissipated in the two separate loads add up. There is no reason to worry about phase.
-
I'll throw another curve at you. In the real world example in question, there is neutral current. However, it will not be the difference in current between leg one and leg two. Phase difference will come into play here. In a previous post you said that current imbalances in 3 phase wye guarantees neutral current. This is also not necessarily true. If the loads are connected between the legs and neutral then yes, current imbalances will cause current to flow in the neutral. But if the loads are connected only between the legs, it doesn't matter. There will be no neutral current.
Right, if there were two loads between L1 and N, and L2 and N then that would make sense.
Second paragraph also makes sense. Although, seems to be a bad practice not to use a neutral on unbalanced loads, can't that ruin equipment (hence the need for neutral)?

Unfortunately, meter doesn't provide any measurements when the neutral is disconnected.
 
  • #37
aemla said:
Although, seems to be a bad practice not to use a neutral on unbalanced loads, can't that ruin equipment (hence the need for neutral)?
Suppose I have three different resistive loads attached to a three phase wye system. L1 & L2, L1 & L3, and L2 & L3. Water heaters all of different wattages for example. Exactly how could we include a neutral even if it made sense to do so? Btw, this is scenario is done all the time in the real world.
 
  • #38
aemla said:
I believe below is what you are describing.
Yes, precisely that.
1625629722079-jpeg.jpg


Cheers,
Tom
 
  • #39
Tom.G said:
Yes, precisely that.
View attachment 285580

Cheers,
Tom
This is how the wiring has been since day one. The results shared earlier are based on this wiring
 
  • #40
This is nuts...
 
  • Like
Likes russ_watters, aemla and berkeman
  • #41
To me this thread has been very confusing. In my opinion the real world example you gave above does NOT reflect the hand drawn schematic you have drawn. On top of that, you mention to ignore L2 and the highlights. More confusion. You have implied that a neutral is involved, but the very first post of this thread implies not. I have given my 2 cents on why the neutral needs to be forgotten about and that it is possible and common to ignore it in a 208 volt wye situation. The way the hand drawn schematic exists, I would expect that if the power meter was configured correctly it would give you leg to leg voltages, not leg to neutral. The apparent power in the load is quite simply the voltage across it multiplied by the current through it. If this power disagrees with what your power meter tells you it is likely it is configured wrong. You are hooking it up one way, and telling it you have hooked it up a different way.
 
  • Like
Likes russ_watters and berkeman
  • #42
Averagesupernova said:
To me this thread has been very confusing. In my opinion the real world example you gave above does NOT reflect the hand drawn schematic you have drawn. On top of that, you mention to ignore L2 and the highlights. More confusion. You have implied that a neutral is involved, but the very first post of this thread implies not. I have given my 2 cents on why the neutral needs to be forgotten about and that it is possible and common to ignore it in a 208 volt wye situation. The way the hand drawn schematic exists, I would expect that if the power meter was configured correctly it would give you leg to leg voltages, not leg to neutral. The apparent power in the load is quite simply the voltage across it multiplied by the current through it. If this power disagrees with what your power meter tells you it is likely it is configured wrong. You are hooking it up one way, and telling it you have hooked it up a different way.
Haha, couldn't agree more. This is my first time dealing with power circuits. I'm used to control circuits.
The actual load is an EV charger which takes L1, L2, and ground. I mentioned to ignore highlights because that's the only screenshot I had available on hand. I mentioned to ignore L2 because I believed L2 CT was not installed correctly. The point of the datasheet screenshot was to show how this particular meter sums up powers.

I have found a meter that has the following configuration:
1625696607282.png

DIRIS A10

I believe this meter will work perfectly fine.

Previous meter did not have this configuration at all. The next best thing it had was the following:
1625696956099.png

I only have this second/previous meter and was wondering if L-L power can be calculated from data provided by this second configuration where only L-N power powers are given.
 
  • #43
Trust me, I am pretty sure the previous meter had a configuration that takes care of what you need. It is obvious in the top diagram that the unit would be measuring the correct way because it only uses one current transformer. It is implied by this that L1 and L2 are the same current. So why can't you use configuration 3 phase 4 wires any load on the lower pic/previous meter? Isn't one load across two legs considered any load? The other two phases happen to have no load. I don't see how that can be invalid.
 
  • #44
Averagesupernova said:
Trust me, I am pretty sure the previous meter had a configuration that takes care of what you need. It is obvious in the top diagram that the unit would be measuring the correct way because it only uses one current transformer. It is implied by this that L1 and L2 are the same current. So why can't you use configuration 3 phase 4 wires any load on the lower pic/previous meter? Isn't one load across two legs considered any load? The other two phases happen to have no load. I don't see how that can be invalid.
Would you happen to know which one? There are only couple pages of wiring diagrams to look at.

Yeah I agree, that top diagram makes more sense for the wiring of the actual load, however, the previous meter does not have such configuration.
I did try 3 phase 4 wire (as shown below) configuration, results were the same as shown in the previous screenshot.
1625706096885.png
 
  • #45
The pic in post #44 should do it. I assume there are configuration setting you need to set to match the connections.
 
  • #46
Averagesupernova said:
The pic in post #44 should do it. I assume there are configuration setting you need to set to match the connections.
I did try that, results were the same.
 
  • #47
I am quite certain you have a CT polarity wrong, the only way to get a -105 phase angle.
 
  • #48
At this point I need to know more about the setup. To get any more help here you are likely going to have to get some known resistive loads and try various things.
 
  • #49
Okay thank you, I'll check the setup in more detail when I can. What about a hypothetical situation? When I have readings with respect to N (L1-N voltage, L1 phase angle, L1 current AND L2-N voltage, L2 phase angle, L2 current), is it possible to calculate active power between L1 and L2?
 
  • #50
aemla said:
Okay thank you, I'll check the setup in more detail when I can. What about a hypothetical situation? When I have readings with respect to N (L1-N voltage, L1 phase angle, L1 current AND L2-N voltage, L2 phase angle, L2 current), is it possible to calculate active power between L1 and L2?
I'm not following. You have two separate loads between 2 separate legs and the neutral. Those powers add up. Is this what you mean? Never forget that a voltage across a device multiplied by the current through the device will get you apparent power without fail.
-
Edit: By device in this case I mean whatever you have as a load.
 
  • #51
Averagesupernova said:
I'm not following. You have two separate loads between 2 separate legs and the neutral. Those powers add up. Is this what you mean? Never forget that a voltage across a device multiplied by the current through the device will get you apparent power without fail.
-
Edit: By device in this case I mean whatever you have as a load.
Added power would be considered two phase power (or so I think). I'm looking for single phase L-L. If my question makes no sense (very possible) then I take it the answer is no.

I believe internal meter calculations heavily rely on configuration.
Given that my meter is setup for 3 phase 4 wire, I don't think I can get L-L data out of it. If I could could, meter would have it as an option. I did find few other meters that offer L-L data/configuration.
1626180374144.png
 
  • #52
I'll say it again:
Averagesupernova said:
So why can't you use configuration 3 phase 4 wires any load on the lower pic/previous meter? Isn't one load across two legs considered any load? The other two phases happen to have no load. I don't see how that can be invalid.
 
  • #53
Link below was an interesting read. Wiring configuration/setup is everything. Per the document, 3 phase 4 wire configuration calculates (not measures) voltages between phases (I'm guessing this is why instantaneous voltage between phases is not measured, hence, active power across phases is not provided). As previously suspected, active power is calculated by measuring instantaneous voltages and currents, like oscilloscopes.
https://www.testworld.com/wp-content/uploads/fundamentals-of-3-phase-power-measurements.pdf
 
  • #54
Averagesupernova said:
I'll say it again:
I believe by "Any Load", document refers to unbalanced or balanced loads. It does not mean any amount of phases.
 
  • #55
With instantaneous measurements of V and I, you can calculate the instantaneous P=VI. Square it, sum the squares for N samples of a whole cycle, then take the square root of sum/N. Now you have RMS real power without measuring any phase angles.

Phase measurements are noisy.

@Windadct poinligh out that the integral of instantaneous P divided by elapsed time is average P. RMS is not needed. I stand corrected.
 
Last edited:
  • #56
aemla said:
I believe by "Any Load", document refers to unbalanced or balanced loads. It does not mean any amount of phases.
So just exactly what is your definition of a balanced load and an unbalanced load?
 
  • #57
Averagesupernova said:
So just exactly what is your definition of a balanced load and an unbalanced load?
Exactly as you've mentioned before. If my wiring was single phase L-N with 3 phase 4 wire configuration/setup of the meter then it would work (as you've said other two phases would just so happened to have no loads). But my wiring is L-L single phase. With 3 phase 4 wire configuration, meter sees this wiring as 2 phases with load and 3rd phase has no load.

I should of said "It does not mean L-L measurements are supported."
 
  • #58
aemla said:
But my wiring is L-L single phase. With 3 phase 4 wire configuration, meter sees this wiring as 2 phases with load and 3rd phase has no load.
I seriously doubt it. This is why I've asked you to get some various loads and try them.
-
I'm not sure you grasp that 3 different loads across 3 different leg combinations can be considered 3 single phase loads. Yet you seem to be accepting that your meter will read this.
 
  • #59
Averagesupernova said:
I seriously doubt it. This is why I've asked you to get some various loads and try them.
-
I'm not sure you grasp that 3 different loads across 3 different leg combinations can be considered 3 single phase loads. Yet you seem to be accepting that your meter will read this.
This is what the internal wiring of the meter suggests. There are no sensing elements between phases, all of that is calculated. Unfortunately, I'm unable to test with various loads, just have the one 208VAC load.
-
Sure, I understand that. In a three phase system using a three wattmeter method, you can simply add all powers together to get the total power. This is what the meter is doing. This can also be considered as 3 single phase loads (L-N loads).

If you actually have single phase L-L but configure the meter for three phase system with a three wattmeter method then you won't get correct results. I've previously showed the power calculation example.
 
  • #60
You do not need to sense L-L, this is where the vector diagram and understanding it is so important. The sensing elements are looking at the waveform, not just a V measurement like a DMM.

if you draw the 2 L-N vectors, the L-L voltage is fully defined, it is the vector sum.

If you measure the three L-N voltages, you can define the entire 3 Phase situation.
 

Similar threads

  • · Replies 5 ·
Replies
5
Views
3K
Replies
9
Views
2K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 17 ·
Replies
17
Views
3K
Replies
2
Views
4K
  • · Replies 15 ·
Replies
15
Views
6K
  • · Replies 7 ·
Replies
7
Views
5K
Replies
38
Views
6K
  • · Replies 10 ·
Replies
10
Views
6K