Natural convection from hot pipe in water

AI Thread Summary
The discussion revolves around calculating the heat transfer rate from a copper coil in water for a defrost water tray model. Initially, a convection coefficient of 1500 W/m^2.K was calculated, which seemed excessively high compared to the expected range of 20-100 W/m^2.K. The error stemmed from incorrectly assuming the coil's temperature was 60 degrees Celsius, when it was actually around 42 degrees due to convection resistances. After correcting this assumption, the heat transfer rates were found to be more realistic at 20-30 watts. The conversation highlights the importance of accurate temperature assumptions and understanding convection resistances in heat transfer calculations.
prageet
Messages
2
Reaction score
0
Hey,

I was having this very silly problem in heat transfer. Please could you see what's going wrong !

I am working on defrost water tray modelling. In that, the water collected during defrost is heated by the compressor o/p coil so as to aid evaporation. I was trying to find out the heat transfer rate, in watts between the coil and water . It is given that the coil is at 60 deg Celsius.


When I try to calculate the h value and the Q value using natural convection correlations, I am getting a convection coeff (h) as large as 1500 W/m^2.K. Whereas it should be in the range of 20-100 for natural convection in water.

Its basically a copper tube in water. Its OD is 5mm. Length of coil is 75cm. For natural convection calculations I have taken charateristic length as its OD ie 5mm. Is that correct. ? The correlations that I apply are for horizontal pipe in fluid.

The value of Nusselt no. I land up with is 15. This give me h value of 1500 W/m^2 K (Q~600 Watts), which is very huge.. ! (using h=(nu*k)/d). k(thermal conduct. ~.5 W/m.K)

Which of these assumptions do you think could have made this go so off.. ?

Could anyone point out where I am going wrong with this !

Thanks !
Urmil
 
Engineering news on Phys.org
First, a Nusselt no of 15 for natural circulation is not unreasonable. So for a 5mm tube, it is what it is. On the other hand, the smaller surface area should affect your heat transfer rate.

This was for the outside surface of the tube correct? What are the conditions inside the tube? How many tubes? How long are the tubes? What is the temperature difference driving heat flow?
 
I agree with edgepflow. Copper tubes in water will transfer heat at pretty good rates, so 1500 W/m^2*K is reasonable.
 
Hey,

Thank you for your response..

Yes, I too verified, that a copper coil 5mm od and 75cm length at 60 deg cels. when placed in water at 40 deg cels. can provide heat rates as high as 1500 watts.

In my case, my mistake was in assuming the coil to be at 60 deg cels. This coil is actually the condenser in the refrigerator. The ref. fluid that flows through it is at 60 deg cels. and I wrongly assumed that to be the temperature of the coil.

On accounting for the 2 convection resistances (1/hA) at the ref. and water surface, I found that the coil (whose resistance is negligible) is at a temperature of 42deg, only 2deg greater than the temperature of water.

This gives me heat rates of 20-30 watts which is realistic for the case of the condenser coil in the defrost water tray.

Thanks,
Urmil
 
I need some assistance with calculating hp requirements for moving a load. - The 4000lb load is resting on ball bearing rails so friction is effectively zero and will be covered by my added power contingencies. Load: 4000lbs Distance to travel: 10 meters. Time to Travel: 7.5 seconds Need to accelerate the load from a stop to a nominal speed then decelerate coming to a stop. My power delivery method will be a gearmotor driving a gear rack. - I suspect the pinion gear to be about 3-4in in...
Thread 'Calculate minimum RPM to self-balance a CMG on two legs'
Here is a photo of a rough drawing of my apparatus that I have built many times and works. I would like to have a formula to give me the RPM necessary for the gyroscope to balance itself on the two legs (screws). I asked Claude to give me a formula and it gave me the following: Let me calculate the required RPM foreffective stabilization. I'll use the principles of gyroscopicprecession and the moment of inertia. First, let's calculate the keyparameters: 1. Moment of inertia of...
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...
Back
Top