Negative sequence (Symmetrical component)

Join the discussion
Registration is free. Ask a follow-up in this thread, or start your own.
2 replies · 2K views
sarayut
Messages
2
Reaction score
0
I'd like to know how do i find I2 (Negative sequence current) if I know Ia, Ib and Ic but don't know angle (in normal system_not fault)? My system's 3 phases 3 wires.
 
Last edited:
Engineering news on Phys.org
You need to specify what you mean by "normal system_not fault"?

Is the load balanced? If so, you know the angles relative to each other. You can then use the symmetrical transformation to find if there is a negative sequence current.

http://en.wikipedia.org/wiki/Symmetrical_components
 
Thank you very much for answer!, "Normal system_not fault" mean imbalance situation in distribution system. For example Ia= 85 A, Ib= 92 A and Ic= 90 A. I'd like to know I2 for set the I2 pick up to detect low fault current.