vanesch said:
In France, this is done as follows: the frequency of the grid is used as a measure of the balance of power into power consumed (if there's less power in than consumed, the frequency, 50 Hz, will reduce slightly), and the steam drawn from the steam generators is regulated as a function of this (using a proportional, or an integrating/proportional regulation scheme).
vanesch,
You are quite correct. Let me elaborate a little.
In any AC electrical grid - the generators have to turn in unision so that they are all on the same portion
of the 50 Hz {France] or 60 Hz[USA] wave.
Suppose we have a PWR - and PWRs will "load follow" or "follow the turbine". Suppose a big factory
turns on and starts to demand more power from the grid. That will cause an increased current in the
windings of the PWR plant's generator. The increased current flow means that there will be a greater
resistive torque - the turbine will see a generator that is more difficult to turn. This only makes sense;
with more current in the generator windings, and the generator voltage is constant - the increased current
means increased power out of the generator - and that power has to come from the turbine.
If nothing were done - the turbine and generator would slow down since it is harder for the turbine to turn
the generator. If the generator slowed down - it would go out of phase with the rest of the generators on
the grid. Recall I stated above that the generators on the grid turn in unision.
There's a controller or feedback mechanism on the turbine generator that monitors the turbine / generator
speed and corrects for any deviation by opening or closing the turbine throttle valve. In the case above,
the controller will open up the turbine throttle in order to increase the turbine power so that it can turn the
generator at the proper speed under the increased load.
The increased steam flow to the turbine means that more energy is leaving the steam generator; and
hence the primary water leaving the steam generator going back to the reactor will be a little cooler than
it was at equilibrium conditions prior to the factory powering up.
That cooler water will lower the reactor moderator temperature. The reactor responds via the moderator
temperature reactivity coefficient - a cooling moderator gives you an increased reactivity and hence
increased reactor power. The reactor power will increase until the increase in power matches the
increased power being drawn from the steam generator. When the reactor reaches this new power level;
then coolant temperatures will be back at their equilibrium values.
The temperatures will be back at equilibrium - but the reactor is producing more power which is equal to
the increased power being drawn from the steam generator which gives you the increased power of the
turbine which gives you the increased power from the generator - which is what is needed to meet the
demand by the factory that just fired up.
Dr. Gregory Greenman
Physicist