Power Plant Load Spike: Get Advice Now

  • Thread starter Thread starter Asghar Hussain
  • Start date Start date
  • Tags Tags
    Generator Load
Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
5 replies · 2K views
Asghar Hussain
Messages
3
Reaction score
0
Dear All,

one of our power plant has load spike when engine is running in parrell operation 7 * (3.5MW) capacity.

one engine suddenly down the load at zero kw in three seconds again load pick at full load .
this engine had an accident of generator blast last year.
please advise
 
Engineering news on Phys.org
Are you saying the one generator rejected load after a system load spike and then attempted to take on load again? Or did you mean the load reduction on one generator caused a spike in the other six generator loads?

Also define sudden. Do you mean a few cycles or seconds?
 
Are you running in Island mode or connected to a grid? What type of fuel control do you have, mechanical, electronic? Are you running in droop or load control?
 
Dear All,

plant is running droop mode not connected with grid
fuel type HFO heavy furnace oil engines, this engine is software control,
during operation communication failure appeared and all parameters held (hang) emergency stop does not work.
this engine one accident of over speed alternator rotor poles broken

today we found that control system hardware panel Earth (ground) is not connected may have this reason for this issue, please give your comments.
 
this engine is software control, ...
during operation communication failure appeared and all parameters held (hang) emergency stop does not work.

I never trust a computer with anything important.

I hope it has a centrifugal overspeed trip. If not, stay physically away from it.