Which Power System Design Is Optimal for Mixed Frequency Plants?

AI Thread Summary
The discussion revolves around the optimal power system design for a facility with two 50 Hz plants and one 60 Hz plant. Two main configurations are proposed: using separate generators for each frequency or employing a single 50 Hz generator with variable frequency drives (VFDs) for the 60 Hz plant. Key considerations include system reliability, maintenance costs associated with VFDs, and the impact on mean time between failures (MTBF) for generators. The group emphasizes the importance of engineering design constraints, suggesting that if cost is not a factor, the choice should focus on reliability and efficiency. Ultimately, the decision hinges on balancing the trade-offs between complexity, maintenance, and operational efficiency.
khamoshie
Messages
2
Reaction score
0
:confused: I am currently working on a university assignment and am quite confused in the following design problem...

Assume that a new in a facility 3 new plants are being setup. 2 of these plants have all motors rated at 50 hz while the third one has all motors operating at 60 hz. the first two plants require electrical power of around 40 MW and the 60 hz plant requires 6 MW. Which would be a better solution for the configuration of power generation...

(1) Setting up two suitably rated generators one that generates output at 50 Hz for the 50 hz plant and the other one generates output @ 60hz for the other plant...

(2) Or Setting up a single generator of 50 Hz and all motors of the 60 hz plant to be connected via VFD's...


note :Standard LV voltage @ 50hz is 400V p-p
All motors in the 60 Hz plant (180 total) operating at 480V p-p ,60hz

My Understanding of this problem is that exactly what would be the impact of using so many VFD's in the Plant...

Any help would be highly Appreciated...
 
Engineering news on Phys.org
Looks like you need to work out the costs for each configuration.
Do you need VFD for each motor?
Can you use one for the entire plant?
 
Thanks for ur reply...

Yes Cost may be a factor but the initial concern is the reliability of the system design...I mean using a single 50 hz generator will simplify the power generation system but at the same time it will also introduce more maintenance cost for the VFD's...

And if we do it the other way, this would simply mean that there would be a dedicated generator for the 60 hz system...no VFD's would be required but now the power generation will be at two different frequencies...

Simpy if we initially disregard the cost overheads what would be a better Engineering design...?
 
You have to chose your design constraints.
If not cost, then you get into MTBF for generators vs VFD
or conversin effiency.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...