Pressure drop due to friction and condensation

Click For Summary
SUMMARY

The discussion centers on the pressure drop experienced in a vapor line due to friction and condensation when integrating a plate heat exchanger (PHE) into a drying process involving acetone. The calculated pressure drop of 50 mbar from the PHE is deemed excessive, particularly as the blower is already near its operational limits. Key factors affecting pressure loss include frictional losses, momentum losses, and the impact of condensation on flow rate. The consensus is that the 50 mbar figure likely reflects frictional losses, and the actual pressure drop may vary based on the flow rate of vapor and the dryness fraction exiting the heat exchanger.

PREREQUISITES
  • Understanding of plate heat exchanger (PHE) design and operation
  • Knowledge of vapor dynamics and condensation processes
  • Familiarity with pressure drop calculations in fluid systems
  • Experience with blower performance characteristics and limitations
NEXT STEPS
  • Research pressure drop calculations for plate heat exchangers
  • Learn about the effects of condensation on vapor flow rates
  • Investigate blower performance curves and operational limits
  • Explore methods to optimize heat exchanger design for reduced pressure loss
USEFUL FOR

Process engineers, HVAC professionals, and anyone involved in the design and optimization of vapor handling systems, particularly in chemical processing environments.

Meteorrain
Messages
1
Reaction score
0
Hello,

I'm struggling with the following problem. We have a dryer in our plant which evaporates acetone and with a blower the vapour is driven to a scrubber. However the efficiency of the scrubber is not sufficient and that is why I want to place a plate heat exchanger in the vapour line to cool the gas (a portion of the vapour will be condensated).

The blower is almost at its limits and we don't want more pressure loss to prevent a too low flowrate. Now the company of the plate heat exchangers calculated a pressure drop of 50 mbar which is too much.

However a pressure drop due to condensation in the heat exchanger will increase the flowrate. But a pressure drop in the heat exchanger due to friction of the plates will decrease the flow. I tried to explain this to the contact person, but the pressure drop is calculated with their software and all he knows is that it is the pressure drop from inlet to outlet.

So I am wondering if this 50mbar pressure loss should be considered as total energy loss and thus the blower needs to deliver an additional 50mbar pressure to cover this. Or doesn't my point of view makes sense?
 
Engineering news on Phys.org
Im not sure if I understand your problem fully but I have a bit of experience in condensation pressure drop. For your case, you are going to have pressure losses due to a combination of 3 effects; frictional losses, momentum losses and static/gravitational losses. If your hex is mounted horizontally, you can neglect the gravitational losses. In addition, as your flow is condensing, you will have momentum recovery (not loss) although if you say only a small amount of vapour is condensing, this may not matter much. It depends on your dryness fraction leaving the hex. My guess, is the 50mbar given to you is solely based on frictional losses, although to calculate this, it must be based on some flow rate of vapour? Obviously 50mbar is goning to seem excessive if the calculation was based on a high flow rate of vapour
 
I'm afraid condensation will even increase the pressure lost, due to droplets forming inside heat exchanger
 

Similar threads

  • · Replies 2 ·
Replies
2
Views
3K
  • · Replies 10 ·
Replies
10
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 8 ·
Replies
8
Views
8K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 3 ·
Replies
3
Views
2K
Replies
2
Views
4K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 6 ·
Replies
6
Views
3K