Question on live and neutral wire

  • Context: High School 
  • Thread starter Thread starter Lim Y K
  • Start date Start date
  • Tags Tags
    Neutral Wire
Click For Summary
SUMMARY

The discussion centers on the critical safety reasons for placing electrical switches on the live wire rather than the neutral wire. It highlights that switching the live wire ensures that appliances are fully de-energized, reducing the risk of electric shock, especially in hazardous situations like wet environments. The UK regulations prohibit neutral switching, emphasizing that the live wire must be switched first to maintain safety. The conversation also touches on the implications of switched neutrals and the importance of grounding in electrical systems.

PREREQUISITES
  • Understanding of electrical wiring, specifically live and neutral conductors.
  • Knowledge of electrical safety standards and regulations, particularly in the UK.
  • Familiarity with grounding techniques and their importance in preventing electric shock.
  • Awareness of the implications of switching devices in electrical circuits.
NEXT STEPS
  • Research UK electrical regulations regarding live and neutral switching.
  • Learn about grounding techniques and their role in electrical safety.
  • Explore the design and safety features of ground fault circuit interrupters (GFCIs).
  • Investigate the implications of using double-pole switches in electrical systems.
USEFUL FOR

Electricians, electrical engineers, safety inspectors, and anyone involved in residential or commercial electrical installations will benefit from this discussion.

Lim Y K
Messages
26
Reaction score
0
Why must a switch be at the live wire instead of the neutral wire?
 
Physics news on Phys.org
... and, to cut off leakage paths.
 
In what way does that make the appliance safe?
 
Lim Y K said:
In what way does that make the appliance safe?
Take the classic example of an electric toaster and a person in a bathtub. If you turn off the wall outlet with a switch on the live wire, the person in the bathtub is (reasonably) safe. If you turn off the wall outlet with a switch on the neutral wire, the person in the bathtub is at risk.
 
Lim Y K said:
Why must a switch be at the live wire instead of the neutral wire?
In addition, if the wall outlet had its switch break the neutral line and not the active, then every unoccupied socket even though switched to "off" would expose a dangerous voltage to the idle probing of inquisitive toddlers (and pets).

Notwithstanding the hazard, some countries, I understand, do allow wall outlets without an associated switch; you have to plug and unplug from a constantly "live" socket. So try to keep fingers clear!
 
NascentOxygen said:
Notwithstanding the hazard, some countries, I understand, do allow wall outlets without an associated switch; you have to plug and unplug from a constantly "live" socket. So try to keep fingers clear!
In the UK all domestic sockets must be fitted with shutters which prevent contact with the live (or neutral) supply unless there is a pin in the Earth socket. The idea that a socket is made safer from an inquisitive child's fingers by providing a switch which the same child can easily operate is ludicrous.
 
Lim Y K said:
In what way does that make the appliance safe?
The most basic hazard with electricity is providing an alternate path to ground. If you grab a grounded wire then your body is just part of the ground. If you grab a live wire then your body may form a path to ground. By switching on the live side you make most of the wiring grounded when it is off, and only a small part of the wiring is live. Thus if you grab a random section of wire you are less likely to have grabbed a live wire if the switch is on the live side.
 
Last edited:
  • Like
Likes   Reactions: Tony Rebeiro
Lim Y K said:
In what way does that make the appliance safe?
the simple answer is if the circuit is switched on the neutral, then when the circuit is 'OFF' the load is still "LIVE" (at mains voltage).

Neutral switching is (generally) illegal in the UK.

In very special circumstances, you can use double-pole devices, but they must break the live conductor first and make the neutral conductor first (this could be a "suitable precaution")EAWRs
Integrity of referenced conductors

9. If a circuit conductor is connected to Earth or to any other reference point, nothing which might reasonably be expected to give rise to danger by breaking the electrical continuity or introducing high impedance shall be placed in that conductor unless suitable precautions are taken to prevent that danger.ESQCRs
No generator or distributor shall introduce or retain any protective device in any supply neutral conductor or any earthing connection of a low voltage network which he owns or operates.
 
  • #10
The hot wire can supply full voltage and power to any true ground. If you touch a 3 prong appliance the odds are that the metal parts are grounded. The neutral wire gets connected to ground in the circuit breaker box. Thus putting a switch in the neutral wire leaves the hot wire hot all of the time and if you touch it and ground at the same time you could be killed. That is why the hot wire must be switched and not the neutral.

BTW just because a wire is white that does not mean it is a neutral. Here in the US it is very common to have 220V wiring that has black and white hot wires. The black measures 110v to ground and the white measures 110v to ground. They are 180 degrees out of phase so you measure 220V across the black and white wires.
 
  • #11
There was a time when some electrical equipment had internal fuses in both the live and the neutral lines. I can't think why that idea ever caught on. I have actually used such equipment which had been modded to eliminate the neutral fuse.
 
  • #12
mr166 said:
BTW just because a wire is white that does not mean it is a neutral. Here in the US it is very common to have 220V wiring that has black and white hot wires. The black measures 110v to ground and the white measures 110v to ground. They are 180 degrees out of phase so you measure 220V across the black and white wires.

There's a similar problem with switch loops even in 110V circuits... Local code where I live (US) says that hot whites must be marked at both ends (usually by putting a piece of black tape on the end of the insulation).
 
  • #13
NascentOxygen said:
Notwithstanding the hazard, some countries, I understand, do allow wall outlets without an associated switch; you have to plug and unplug from a constantly "live" socket. So try to keep fingers clear!
One of those countries is the US. Switched outlets are unusual.
 
  • #14
insightful said:
One of those countries is the US. Switched outlets are unusual.
To compensate for this, some of the outlets like ones in a bathroom or laundry room (any room that could have water on the floor) have ground fault interrupters. Wiki article:

http://en.wikipedia.org/wiki/Residual-current_device

Also in the US, the neutral wires can have some small voltage since they are only grounded at the junction box, while the optionally used third ground wire is apparently grounded in more locations in a household.
 
  • #15
sophiecentaur said:
There was a time when some electrical equipment had internal fuses in both the live and the neutral lines. I can't think why that idea ever caught on. I have actually used such equipment which had been modded to eliminate the neutral fuse.

I know that US military ships use floating AC for power, there is no neutral wire so both wires (single phase) are 'HOT' and are fused.
 
  • #16
Oh ok got it. Thanks
 
  • #17
nsaspook said:
I know that US military ships use floating AC for power, there is no neutral wire so both wires (single phase) are 'HOT' and are fused.
And what is the rationale behind that? If the two conductors are truly floating then 1. how does the fuse provide a protection against shock and 2. How does an extra fuse in series do a better job of overload protection? There must be some scenario that prompted double pole fusing but I can't think of one at this minute.
 
  • #18
sophiecentaur said:
And what is the rationale behind that? If the two conductors are truly floating then 1. how does the fuse provide a protection against shock and 2. How does an extra fuse in series do a better job of overload protection? There must be some scenario that prompted double pole fusing but I can't think of one at this minute.
My two cents:
I can think of two possible reasons: water danger and battle damage.
1) Residential building standards require ground fault breakers where there might be water (kitchen, bath, outdoors). So it makes sense for a ship to assume there might be water dangers everywhere. It's probably cheaper to add normal fuses on every line than to put ground fault breakers on every line.
2) Battle damage might short out wires all over the place. So maybe they want to assume that any wire can become hot at any time.
3) The combination of both. Battle damage causing water danger anywhere on board.
 
  • #19
sophiecentaur said:
rationale behind that?
Damage control? Never know which side of a circuit's going to be open to salt water?
 
  • Like
Likes   Reactions: FactChecker
  • #20
Simple example... I once repaired a spotlight lamp in a garage. When you operated the switch, it would go from bright to dim instead of from on to off. I found that the switch had been wired into the neutral side. The lamp current was obviously finding another path to ground when the neutral was interrupted. I moved the switch to the hot side, problem solved.
 
  • Like
Likes   Reactions: Drakkith
  • #21
nsaspook said:
I know that US military ships use floating AC for power, there is no neutral wire so both wires (single phase) are 'HOT' and are fused.

Google found this..

http://www.brighthubengineering.com/marine-engines-machinery/38231-electrical-grounding-on-ships/

The requirement ashore is the safety of human beings. So, inorder to prevent human-electrical accidents, the neutral is earthed. The priority is neither the safety of the machinery nor the continuous necessary operation of the machinery. But the scenario onboard ship is totally different. The priority is the continuous operation of the machineries which are classed "essential". The distribution system followed onboard is "insulated neutral" system. The main priority onboard is the safety of ship which includes navigation & fire safety..etc. If due to Earth fault, the machinery classed as"essential" gets isolated, say for eg: steering gear, then the safety of ship is at question, which may lead to collison, grounding, fire & pollution etc..So the priority onboard ship is to maintain the continuity of the supply to the machinery in the event of "single Earth fault occurring". Continues..
 
  • Like
Likes   Reactions: FactChecker
  • #22
sophiecentaur said:
There was a time when some electrical equipment had internal fuses in both the live and the neutral lines. I can't think why that idea ever caught on. I have actually used such equipment which had been modded to eliminate the neutral fuse.

In the UK there are STILL many old cast iron cut-outs with a very heavy fuse-wire in the neutral.

Hangover from the days of DC.

The DNOs were given until end-2013 to comply with the ESQCRs; but many still remain and get noticed every so often when the cut-out blows, or when an electrician is doing some work on the consumer unit and notices it.
 
  • #23
tfr000 said:
Simple example... I once repaired a spotlight lamp in a garage. When you operated the switch, it would go from bright to dim instead of from on to off. I found that the switch had been wired into the neutral side. The lamp current was obviously finding another path to ground when the neutral was interrupted. I moved the switch to the hot side, problem solved.
That sounds dangerous. Like the kind of thing where you might touch the spotlight with one hand and something correctly grounded with the other and get a serious shock.
 
  • #24
FactChecker said:
That sounds dangerous. Like the kind of thing where you might touch the spotlight with one hand and something correctly grounded with the other and get a serious shock.

No kidding that's dangerous. It's one of the many reasons why switched neutrals are evil.

My first switched neutral story involves standing on damp concrete while working on an overhead fixture. The experience was exciting, and not in a good way.
 
  • Like
Likes   Reactions: FactChecker
  • #26
An ungrounded electrical system is probably safer than a grounded one when you are in total control of the entire system. In theory, in a system powered by an isolation transformer you could stand in water and touch either leg and not get a shock. In a grid you have no such controls and one leg or the other will become grounded someplace so it is better to define which leg is grounded. Also, using the Earth as one conductor, does reduce wiring costs for the power companies.
 
  • #27
There are installations that have to be isolated from "grid" Earth - explosive atmospheres for example (petrol station pits).

Using the Earth as a return path (SWER) is used in remote areas in countries like Australia.
 
Last edited:
  • #28
WW you are 100% wrong. In the US the average home is fed by a 11KV or so feeder line in which one leg is grounded. This 11KV is fed to one leg of a transformer whose other leg is grounded. The secondary consists of a 220-240 volt winding with a grounded center tap. Thus the average home is fed with 2 110-120 volt legs that are both referenced to ground.
 
  • #29
Lim Y K said:
Why must a switch be at the live wire instead of the neutral wire?
Alternating current travels in a circular path along the "hot" and the neutral conductor. The switch breaks the circuit in the hot.

The purpose of the hot conductor is to feed the device (outlet, appliance, electrical panel etc...) with voltage. The purpose of the neutral is to carry the electricity BACK to the source. (The transformer. Many of them are on poles or in big green boxes on the ground.) if the neutral was broken, the device being controlled by the switch would still be energized because the electricity had already reached it. Hope that makes sense!
 
  • #30
mr166 said:
WW you are 100% wrong.
where?
 
Last edited:

Similar threads

  • · Replies 22 ·
Replies
22
Views
2K
  • · Replies 7 ·
Replies
7
Views
22K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 13 ·
Replies
13
Views
4K
  • · Replies 10 ·
Replies
10
Views
3K
  • · Replies 10 ·
Replies
10
Views
2K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 36 ·
2
Replies
36
Views
6K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 49 ·
2
Replies
49
Views
22K