Reinforced Concrete: Calculating Irregular Shapes

  • Thread starter Thread starter derryck1234
  • Start date Start date
  • Tags Tags
    Concrete
AI Thread Summary
To calculate reinforcement for irregularly shaped reinforced concrete beams, first establish the horizontal compressive and tensile forces due to bending. Next, locate the neutral axis, which is initially unknown, and denote it as a distance from the top surface. Solve for the neutral axis position by equating the compression and tensile moments. Distribute the compression force over the concrete and determine the required steel area based on maximum allowed steel stress. If the concrete area is insufficient, incorporate compression reinforcement and use the modular ratio to allocate compression between the reinforcement and concrete.
derryck1234
Messages
55
Reaction score
0
In my reinforced concrete textbook, we only have formulas and procedures for rectangular, or webbed and flanged beams. What do I do if I have an irregular shaped beam? How do I calculate the reinforcement?
 
Engineering news on Phys.org
Exactly the same way as with any other rc beam.

1) Establish the horizontal compressive and tensile forces due to bending

2) Locate of the neutral axis. This will be an unknown at the outset, give it a symbol as a distance from the top (compressive) surface.

3) Solve for the position of the neutral axis by equating the compression moment (= conc area x conc stress x compression level arm) to the tensile moment (= steel area x steel stess x tensile lever arm)

4) Distribute the compression force over the concrete in the compression zone, using either a rectangular block.

5) Use the tensile force to determine the required area of steel from max allowed steel stress.

6) Set the steel a distance equal to the cover from the bottom of the beam and choose suitable bars to achieve the area calculated in step 3.

7) If there is insufficient concrete area (ie compressionn is too great) then you will have to repeat, adding in compression reinforcement and using the modular ratio (1:15) apportion the compression between the upper (compression ) reinforcement and the concrete.
 
Thread 'Physics of Stretch: What pressure does a band apply on a cylinder?'
Scenario 1 (figure 1) A continuous loop of elastic material is stretched around two metal bars. The top bar is attached to a load cell that reads force. The lower bar can be moved downwards to stretch the elastic material. The lower bar is moved downwards until the two bars are 1190mm apart, stretching the elastic material. The bars are 5mm thick, so the total internal loop length is 1200mm (1190mm + 5mm + 5mm). At this level of stretch, the load cell reads 45N tensile force. Key numbers...
After over 25 years of engineering, designing and analyzing bolted joints, I just learned this little fact. According to ASME B1.2, Gages and Gaging for Unified Inch Screw Threads: "The no-go gage should not pass over more than three complete turns when inserted into the internal thread of the product. " 3 turns seems like way to much. I have some really critical nuts that are of standard geometry (5/8"-11 UNC 3B) and have about 4.5 threads when you account for the chamfers on either...