Selection of solar panels and batteries

AI Thread Summary
To select solar panels and batteries for a 12 V 100 W DC motor operating intermittently, the minimum battery requirement is approximately 8.3 Wh, translating to about 0.69 Ah. Given the intermittent use, a larger battery capacity is advisable to ensure adequate power supply, especially during cloudy days. A 20 W solar panel paired with a 24 Ah battery is deemed sufficient for this setup, considering an average of 5 hours of intense sunlight per day. It's crucial to use a charge controller to manage the battery charging within the appropriate voltage and current range. Both 12 V 12 Ah and 12 V 24 Ah batteries are suitable options for this application.
subakumaran
Messages
8
Reaction score
0
is there any procedure ( formulae ) to select the power rating of solar panels and ampere hour rating of batteries ?
 
Engineering news on Phys.org
It depends on the application.
 
mfb said:
It depends on the application.

it is to charge a battery which inturn provides the supply for a 12 V 100 W DC motor ... the operating time of the motor is 5 minutes intermittent cycle of 4 cycles in a day
 
Well, that helps a bit, but it is still a bit vague:

100W for 5 minutes are 100W*300s= 30kJ = ~8.3Wh. This is the minimum requirement for your battery, unless you want to rely on sunshine directly at the time of the motor operation.
8.3Wh at 12V correspond to 8.3Wh/(12V) = .69 Ah.

In general, your battery won't get fully charged between cycles, so I guess you'll need more capacity. If your solar cells are sufficient to provide the power for a day even if it is cloudy, a capacity for 4 cycles could be sufficient. Otherwise, you could need more capacity.

The required peak power rating of the solar cells depends on the amount of sunshine you get, and the battery capacity. The average energy per day has to be at least the required energy for the motor operation, but there should be some additional safety factor for cloudy days/weeks.

Matching the voltage is another thing you have to take care of - if the output voltage of the solar cells is not 12 Volts, you get some conversion losses.
 
mfb said:
Well, that helps a bit, but it is still a bit vague:

100W for 5 minutes are 100W*300s= 30kJ = ~8.3Wh. This is the minimum requirement for your battery, unless you want to rely on sunshine directly at the time of the motor operation.
8.3Wh at 12V correspond to 8.3Wh/(12V) = .69 Ah.

In general, your battery won't get fully charged between cycles, so I guess you'll need more capacity. If your solar cells are sufficient to provide the power for a day even if it is cloudy, a capacity for 4 cycles could be sufficient. Otherwise, you could need more capacity.

The required peak power rating of the solar cells depends on the amount of sunshine you get, and the battery capacity. The average energy per day has to be at least the required energy for the motor operation, but there should be some additional safety factor for cloudy days/weeks.

Matching the voltage is another thing you have to take care of - if the output voltage of the solar cells is not 12 Volts, you get some conversion losses.


can a 20 W solar panel and a 24 Ah battery will be more than enough for this operation ? considering our place in India we get a minimum 5 hrs of intense sunshine a day ...
 
20W*5h = 20J/s*5*3600s = 360kJ. Should be more than sufficient, especially with the large battery that can store enough energy for a few days.

Just keep in mind that you need some controlled way to charge the battery with the right voltage and current range.
 
mfb said:
20W*5h = 20J/s*5*3600s = 360kJ. Should be more than sufficient, especially with the large battery that can store enough energy for a few days.

Just keep in mind that you need some controlled way to charge the battery with the right voltage and current range.

hmm yes ... i'll be using a 12 V 10 A charge controller ...
can i go for a 12 V 12 Ah or a 12 V 24 Ah battery ?
 
Sorry for the late reply: both should work.
 
Back
Top