Engineering Shady data from a transformer’s short-circuit test

AI Thread Summary
The discussion focuses on calculating the per-unit parameters from a short-circuit test of a transformer with given voltage, current, and power values. The rated current is determined to be approximately 21.7 A, while the short-circuit current is 20.2 A, leading to an error ratio of 1.076. To adjust the test data, the voltage and current are multiplied by this ratio, while the power is adjusted by squaring the ratio. It is noted that the per-unit parameters remain consistent regardless of whether the adjustments are applied. The conversation emphasizes the importance of correcting the short-circuit test data for accurate per-unit calculations.
Kamakiri
Messages
12
Reaction score
0

Homework Statement


Data from the short-circuit test of a 60-Hz, 100-kVA, 4600–230-V transformer are:

VSC = 172.3 V
ISC = 20.2 A
PSC = 1046 W

Get the per-unit parameters.

2. Relevant equations

ISC ≠ Irated, so how will I solve the problem?

The problem is from the book with ISBN 0130612103.
 
Last edited:
Physics news on Phys.org
Kamakiri said:
I_(SC) is unequal to the rated current, so how will I solve the problem?

Rated current is about 100 kVA / 4.6 kV = 21.7 A, so the error-ratio is 21.7 A / 20.2 A = 1.076

So you multiply Vsc and Isc by 1.076.

Multiply Psc by 1.0762. ( P = R * I2. )
 
The per-unit parameters are the same whether or not I multiplied the data by 1.076 or 1.0762.
 