Sizing Power Supply in Electrical Cabinet

AI Thread Summary
When selecting a power supply for an electrical cabinet, it is essential to consider the total current requirements of all devices, including pushbutton lights, alarm horns, and solenoid valves. Peak inrush current and average holding current should be evaluated, especially for large solenoids and motors that may draw significant inrush currents. For a 24V DC power supply fed by 120VAC, the current can be calculated using the formula Amps = VA / Voltage, while 3-phase calculations require different considerations based on whether the devices are connected as single-phase or three-phase. It is crucial to ensure the selected power supply has adequate current capacity to handle all connected devices. Proper sizing of the power supply is vital for reliable operation and to prevent overloads.
Som_P
Messages
6
Reaction score
0
What things do I need to consider when selecting a proper sized power supply? Basically this is control power, ouputs are pushbutton lights, alarm horn, and solenoid valves. Do I look at the peak inrush current? Average holding current?
 
Engineering news on Phys.org
You literally may want to make a list of all of the devices being fed and add their current requirements- in our systems this exercise is part of our design requirements. Be wary of large solenoids and motors as they may have large inrush currents - as you have alluded to.
 
So basically I would be adding up the total current? Then simply select a power supply with enough current capacity? If a spec sheet list inrush current in VA, what formula would I apply to find Amps(A)? This is 3-phase by the way.
 
Last edited:
Yep, but when you said power supply I was think of a DC supply - is it DC with a 3 Phase AC source? Or describe what it is a little more.

For DC the Amps will just be x VA / Voltage. EG 300VA and 24 V ... 12.5A...

3 ph AC is a little more complicated - but for VA it will depend if the device is being connected as a 3 phase device or a single phase device. Single phase same as above, 3 phase √3*V* A(in one phase)
 
I apologize for not being clear, well not proof reading my comments. Anyway, I need to get a 24VDC power supply, this is being fed by 120VAC. My main question was to select the 24VDC power supply as it relates to total current?
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...