Source strangulation for an instant water heater?

Click For Summary

Discussion Overview

The discussion revolves around the performance issues of an electric instant water heater, particularly in relation to water pressure and flow rates during different seasons. Participants explore the implications of plumbing design, including pipe sizes and potential clogs, on the heater's operation.

Discussion Character

  • Technical explanation
  • Debate/contested
  • Exploratory

Main Points Raised

  • One participant notes that the heater shuts down in summer due to low inlet pressure when mixing hot and cold water, suggesting that higher house water pressure could prevent this.
  • Another participant questions whether the issue could be due to clogged pipes, asking about the age of the plumbing and the hardness of the water supply.
  • It is proposed that the incoming cold water temperature in summer affects the heater's performance, requiring a higher flow rate to achieve the same output temperature.
  • Some participants discuss the concept of "strangulation" versus "resistance" in plumbing, with one suggesting that larger pipes would reduce resistance and potentially improve flow.
  • Concerns are raised about the possibility of a bottleneck effect, where a narrow section of pipe could restrict flow despite larger pipes being installed elsewhere.
  • One participant emphasizes the importance of measuring water pressure before making any changes to the plumbing system, suggesting that assumptions about low pressure may be unfounded.
  • Details about the specific water heater model are shared, including its flow rate specifications and the importance of checking for clogs in the internal filter.

Areas of Agreement / Disagreement

Participants express differing views on the cause of the heater's performance issues, with some attributing it to low pressure and others questioning whether pressure measurements have been adequately assessed. There is no consensus on the best course of action or the validity of the assumptions made regarding the plumbing system.

Contextual Notes

Participants highlight the need for pressure measurements and further investigation into the plumbing system before concluding that pipe size changes will resolve the issues. There are unresolved questions about the effects of temperature and flow rates on the heater's operation.

  • #31
Jonathan212 said:
It completely switches off the heating when you try to mix in too much cold water. What it needs is higher flow in both the hot and cold paths.
Higher flow through the heater decreases the temperature of the water output from the heater.
Jonathan212 said:
In the summer low flow is a good thing for the hot water. Still not low enough.
Lower flow through the heater increases the temperature of the water output from the heater.

You seem to be unclear about the following (from the manual):

To regulate the water temperature: Open the tap fully, the appliance switches on. Now​
increase the temperature by reducing the water flow volume.​
[emphasis added]​

This refers not to the temperature of the water emerging from your shower head, but only to the temperature of the water coming out of the heater.

Please re-read what @JBA said, and also please carefully re-read my post #29,

You seem to not be grasping that unlike in a conventional system, in which the temperature of the hot water does not depend on flow rate, in the instant water heater system the hot water temperature does depend on flow rate.

This is because the 6k watt heating element can either heat less water to a higher temperature, or heat more to a not-as-much higher temperature. It's called 'instant' because it does that 'on the fly'. You're not just drawing however much water from a pre-heated reservoir.

With a flow-regulated hot water temperature, it's a bit trickier to manage the temperature and flow rate at your shower head. If you're not trying too hard to conserve water, and you want a cool but not too cold summer shower at a not too high flow rate, max out the hot water to its body-temperature 3 liter per minute flow, then add some cold water -- maybe 1 liter per minute -- to get somewhere around swimming pool cool. If you want a fuller flow (many Americans, especially in the great lakes regions, use around 8 liters per minute) for your shower, get another heater, and run the two of them in tandem, and merge their outputs before the hot water tap, but be aware that with the resultant 12kw electric power use, if your electricity cost is 25 cents per kilowatt hour, that's a nickel a minute, a dollar for a 20 minute shower, and that's without considering the water bill.
 
  • Like
Likes   Reactions: Asymptotic
Engineering news on Phys.org
  • #32
I said MIX IN too much cold water, not pass through the heater too much cold water. There is only one place where you mix water. What the manual says applies when you have enough pressure at the place where plumbing separates into cold and hot. Several people have got it, what is going on. No time to explain over and over what others have written over and over.
 
  • #33
Jonathan212 said:
I said MIX IN too much cold water, not pass through the heater too much cold water. There is only one place where you mix water. What the manual says applies when you have enough pressure at the place where plumbing separates into cold and hot. Several people have got it, what is going on. No time to explain over and over what others have written over and over.
If you max out the hot water to 3 liters per minute, without turning any cold water on, it's going to give you around 37°, i.e. around body temperature. If you then add a flow rate of less than 1 liter per minute of cold water, you'll get acceptably cool water. Would that produce a less than 2 liter per minute flow into the heater?

As @essenmein said:
I bet this is what's going on. Easy way to test, run the shower at 100% hot and see if it shuts off.​

If you try that and it's warmer than you are when it's fully on, then yes, your supply line flow rate is less than 3 liters per minute, and that's too low.
 
  • Like
Likes   Reactions: Asymptotic
  • #34
No it is not going to give me 37 degrees, it is going to give me burns because the input water is already a little warm and certainly not as cold as when the 37 degrees in the spec was measured. Asymptotic is one of the people who got it:

heater flow rate drops below 1.8 LPM after you've adjusted cold water flow setting to get the desired outlet water temperature
 
  • #35
Jonathan212 said:
No it is not going to give me 37 degrees, it is going to give me burns because the input water is already a little warm and certainly not as cold as when the 37 degrees in the spec was measured. Asymptotic is one of the people who got it:
I was going by what the manual said. It's still going to less warm when fully on than when more restricted. And if it's fully on then you could presumably add more cold water to make it cool enough without too much lowering of the flow rate. I'll re-read what @Asymptotic wrote.
 
  • #36
Gosh, it is really simple. There ain't enough water to keep the heater running and the cold flow fast enough to compensate for the heat.
 
  • #37
Jonathan212 said:
Gosh, it is really simple. There ain't enough water to keep the heater running and the cold flow big enough to compensate for the heat.
Do you know what the combined flow rate from the 2 taps is when you max both of them after the heater turns off? (a wristwatch and a bucket can tell you that) (then you can try them one at a time)
 
  • Like
Likes   Reactions: Asymptotic
  • #38
How are you going to use such figures? I'd rather have some figures for pressure loss as a function of pipe size and length in order to predict what will happen with a tank or a thicker pipe or a pump of given specs.
 
  • #39
Jonathan212 said:
How are you going to use such figures? I'd rather have some figures for pressure loss as a function of pipe size and length in order to predict what will happen with a tank or a thicker pipe or a pump of given specs.
I want to know how much water you get from each pipe -- you said it was simple, and that "there ain't enough water", so I wondered how much deficiency there might be. You still haven't acknowledged that the temperature of the hot water increases when you decrease the flow rate through the heater, and I was wondering whether if you max out the hot, does it still go below 2 LPM if you then cool the mix with cold, or did you first try to reduce the flow through the hot pipe, and then get too slow a flow after adding enough cold to cool the hot.
 
  • #40
You start with just hot at maximum flow which is rather slow. You wait a little for it to stabilise to its maximum temperature. Then begin to add cold in the mix till you can stand it. Which is fine in the winter, and fine in the summer too most of the time. But occasionally it is not, the heater switches off as you increase the cold water in the mix. Must be because the public water is a little warm when the weather is warm. Another theory is that too many people are having a shower or watering gardens. Either way, the solution is to increase both cold and hot flow.
 
  • #41
the temperature of the hot water increases when you decrease the flow rate through the heater

The temperature of the hot water increases, the temperature of the mixed water decreases. This is equivalent to pumping more water through the heater while the cold tap is closed.
 
  • #42
Jonathan212 said:
I'd rather have some figures for pressure loss as a function of pipe size and length
Have you looked at the Hose Water Flow - Pressure Loss graph at The Engineering Toolbox?

I digitized it and generated the following equation, as I didn't see one listed:
pressure drop[psi] / 100 ft = 10^(1.848 * (log_10(gpm)) + ( -2.1041 * ln(pipe diameter[inches]) - 1.3211))

It seems to generate numbers consistent with the graph, so I think it's correct.
 
  • Like
Likes   Reactions: sysprog
  • #43
What is the formula at 90 degree turns?
 
  • #44
Jonathan212 said:
What is the formula at corners?
I do not know what your sentence means. Is English your first language?
 
  • #45
I meant 90 degree turns of the pipe.

long-radius-long-turn-elbows-det__83058.1527098566.jpg
 
  • #46
If I understand your question there are factors for determining the added loss at elbows in terms of equivalent pipe length to be added. According to Crane Fittings the factor for a std 90° elbow is L/D = 20-30 so the maximum equivalent pipe length to be added to your current pipe length is L = 30 x pipe I.D.
 
  • Like
Likes   Reactions: sysprog and Asymptotic
  • #47
  • #48
Jonathan212 said:
No it is not going to give me 37 degrees, it is going to give me burns because the input water is already a little warm and certainly not as cold as when the 37 degrees in the spec was measured. Asymptotic is one of the people who got it:
It is one of the possibilities. I'm a proponent of measuring things then sorting out what is happening based on the results.

@sysprog's "timed bucket" flow measurement method is cheap and easy, and one of the things I'd be doing if investigating a similar problem. How to go about pressure measurement depends on pipe accessibility and similar peripheral issues ("I want to measure pressure at X location, but can't get at the pipe, so what can I do?").

Assuming the shower head is threaded, I might cobble together a tee fitted with a pressure gauge, and ball valve to go between the pipe and shower head. Measure static pressure with the ball valve closed. Measure pressure (and flow rate; temperature too, if you have a way to measure it) with ball valve open for cold water only, hot water only, and at desired mixture.

Caveat: Static pressure will be the only high quality measurement possible in this configuration. With the pressure gauge located nearly at the water outlet, it will read considerably lower values than if it were located just upstream of the heater unit.​

Solving a problem is a lot easier if you've made a bunch of measurements and developed a sense of what really is going on. Going at it the other way isn't generally as effective.
 
Last edited:
  • Like
Likes   Reactions: sysprog
  • #49
To what @Asymptotic just said, I would add that cooking and weather thermometers are also inexpensive, and that with the right set of measurements, and @Jonathan212's self-identified comfort zones, one could establish sets of linear and non-linear inequality constraints, formulate LP (Linear Programming) problems, and run Simplex on them, and then do the sensitivity analyses to learn how far one can push one or more of the constraints without departing from a feasible region.
 
  • Like
Likes   Reactions: Asymptotic
  • #50
Jonathan212 said:
The temperature of the hot water increases, the temperature of the mixed water decreases. This is equivalent to pumping more water through the heater while the cold tap is closed.
If you put 3 LPM through the heater the temperature of the water coming out of it will be lower than if you had put 2 LPM through it. The calorimetric output should be about the same. Is there any tap in your place, cold or hot, that doesn't have what you would think of as a slow flow compared to what you've encountered at, say a hotel room sink?
 
Last edited:
  • #51
Asymptotic, you do not really have an alternative that fits the observations in #40. Can't blame it on heater malfunction, it is almost new. Can't blame it on a clogged filter, the little mesh filter inside the heater is clear. Can't blame it on anything other than low TOTAL flow. Those 6 kW of power end up in the mixed water, that mixed water must be x LPM for the required temperature rise from 23 to 37 degrees caused by 6 kW (exercise: work out x).

If you ain't got x LPM available, forget it, can't have a 37 degree shower. The heater is only trying to protect itself from too low flow through it that would damage it.
 
Last edited:
  • #52
the factor for a std 90° elbow is L/D = 20-30 so the maximum equivalent pipe length to be added to your current pipe length is L = 30 x pipe I.D.

Actually I have both elbows and turns in the path, what is the formula for turns of a given radius and internal diameter?
 
  • #54
The average flow rate for an American shower is about 8 LPM, usually with more available. The 37° in the manual was for 3 LPM through the heater only. Asked and not answered: what is the observed flow rate at your place? I don't see a good reason for your being unwilling to do the simplest of measurements, and report the actual numeric values. The heater starts, so the flow rate initially must be over 1.86 LPM. How much over? Does the cold water line alone show a faster flow than the hot water line alone, or are they about even? What are the numbers? Or at least what is your estimate of the percentage compared to a commonly known range of acceptable values, such as that of a normal hotel room sink cold water line?
 
  • #55
I don't see a good reason for your being unwilling to do the simplest of measurements

How about this for a reason: you do not grasp that the 37 degrees is up to the taste of the user, that the 23 degrees is up to the weather, that the maximum flow available at the balcony varies depending on what the city is consuming, and that the problem does not always occur and cannot be reproduced at will. So taking measurements without a mathematical foundation to use them would be akin to playing.
 
  • #56
Jonathan212 said:
How about this for a reason: you do not grasp that the 37 degrees is up to the taste of the user, that the 23 degrees is up to the weather, that the maximum flow available at the balcony varies depending on what the city is consuming, and that the problem does not always occur. So taking measurements without a mathematical foundation to use them would be akin to playing.
According to the manual, the "typical" (##\leftarrow## that word is there due in large part to the variations in input water temperature) warm water temperature of 37 degrees depends on whether you ran 3 LPM through the heater. If your "taste" is for a hotter temperature, you can use a lower flow rate. The mathematical foundation for using such measurements is anything from 4th grade arithmetic, through linear programming, through multivariant linear regression analysis, etc.; however, having a numeric sample of the 'typical' flow rates gives your readers here a better idea of the situation than does use of such subjective words as "slow", or sometimes not as slow. And by the way, where do you live that's not equatorial (inferred by your having a winter and a summer, as distinguished from year-round hot) that has a municipal water supply that runs at 23° in the summertime?
 
  • #57
You are misapplying the manual: the 37 degrees-3 LPM pair assumes a standard input temperature that is not available here so it is a pointless thing to say or test for.
 
  • #58
Jonathan212 said:
You are misapplying the manual: the 37 degrees-3 LPM pair assumes a standard input temperature that is not available here so it is a pointless thing to say or test for.
So where do you live (I'm not asking for your hometown) that has a 23° water supply?
 
  • #59
I do not know if I have 23 degrees water supply, that was an example for the mathematically challenged.
 
  • #60
Jonathan212 said:
I do not know if I have 23 degrees water supply, that was merely an example.
[edited]

Is that what you meant? You could get a regular thermometer and run the cold water over it and then you'd know what the input temperature to your heater is and you could then tell us.
 
Last edited:
  • Like
Likes   Reactions: Asymptotic

Similar threads

  • · Replies 66 ·
3
Replies
66
Views
6K
  • · Replies 15 ·
Replies
15
Views
4K
  • · Replies 6 ·
Replies
6
Views
6K
  • · Replies 2 ·
Replies
2
Views
4K
Replies
21
Views
9K
  • · Replies 3 ·
Replies
3
Views
4K
  • · Replies 6 ·
Replies
6
Views
3K
  • · Replies 4 ·
Replies
4
Views
7K
Replies
8
Views
2K
  • · Replies 21 ·
Replies
21
Views
11K