Space Requirements for Industrial Cabinets

  • Thread starter Thread starter Som_P
  • Start date Start date
  • Tags Tags
    Industrial Space
AI Thread Summary
Manufacturer specifications for clearance in industrial cabinets typically indicate the need for actual open space to ensure proper airflow. In the case of Watlow Power Controllers requiring 4 inches of clearance, having only 2 inches with wireways above and below may restrict airflow. This could potentially impact the performance of the equipment and may raise concerns about warranty validity. The effect of wireways on airflow depends on their design and fullness, with slotted wireways being less restrictive. Given the tight layout specified by the customer, it is advisable to consult the manufacturer or a legal expert regarding warranty implications.
Som_P
Messages
6
Reaction score
0
Quick question. If the manufacturer's specs ask for clearance top and bottom when mounting in the cabinet, does that usually mean actual open space? For example, I am using Watlow Power Controllers that require 4 in. of clearance top and bottom. I have about 2 in. spacing with a 2x3 in. wireway above and below. The Watlows are probably 5-6 inches deep and the wireway is 3 in. deep. Would this affect the air flow and nullify any manufacturer warranties?
 
Engineering news on Phys.org
Som_P said:
Quick question. If the manufacturer's specs ask for clearance top and bottom when mounting in the cabinet, does that usually mean actual open space?
Usually.
For example, I am using Watlow Power Controllers that require 4 in. of clearance top and bottom. I have about 2 in. spacing with a 2x3 in. wireway above and below. The Watlows are probably 5-6 inches deep and the wireway is 3 in. deep. Would this affect the air flow
depends on the designs and the room - does the wireway affect air-flow? - is it your information that the clearance is needed for air-flow?
and nullify any manufacturer warranties?
That would be a legal question - you should put it to the manufacturer or their agents... or a lawyer.
 
That's what I was hoping to find out; if the wireways affect air flow. Using wireways that are slotted and also will only be about 50% full.
The problem is the overall layout. Customer specified cabinet size so space is limited. May be a tight squeeze for all components. Electrician may not be happy.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...