Spacing between Electrical Sockets

  • Thread starter Thread starter Simon Clement
  • Start date Start date
  • Tags Tags
    Electrical
Click For Summary

Discussion Overview

The discussion revolves around the minimum spacing requirements between electrical sockets according to various standards, particularly comparing UK regulations with the US National Electrical Code (NEC). Participants explore specifications, compliance, and differences in electrical installation rules between the two regions.

Discussion Character

  • Debate/contested
  • Technical explanation
  • Conceptual clarification

Main Points Raised

  • Some participants inquire about the minimum spacing between sockets as per BSI standards or other UK regulations, similar to the NEC's 12-foot rule in the US.
  • Others assert that there are substantial differences between US and UK electrical installation rules, emphasizing the necessity to comply with local codes.
  • One participant mentions that the 12-foot rule in the US is a maximum distance, not a minimum, and questions the rationale behind this regulation.
  • Another participant clarifies that in the UK, there seems to be no minimum separation requirement, but there are restrictions regarding proximity to wet areas.
  • Participants discuss the 17th Edition of the IET Wiring Regulations as a relevant standard in the UK for electrical installations.
  • Some contributions highlight that the Building Regulations differ across England, Scotland, and Wales, which may affect socket installation practices.

Areas of Agreement / Disagreement

Participants generally agree that local regulations must be followed, but there is no consensus on specific minimum spacing requirements for sockets in the UK. Multiple competing views exist regarding the interpretation of the NEC and its application in different contexts.

Contextual Notes

Limitations include the lack of specific references to UK standards regarding minimum socket spacing and the potential for differing interpretations of the NEC rules. The discussion also notes that regulations may vary by region within the UK.

Simon Clement
Messages
18
Reaction score
3
Hello here,

Please, what is the minimum spacing between sockets is based on the BSI standard or any other standard being used in the UK. I was wondering maybe there is such specification just like in the NEC which required 12 feet between sockets.

Also please, is there any major difference between rules governing electrical installation in the US and in the UK? I have read the NEC, but now I was told that was America standard and to go get acquainted with the British way.

Thank you lots
 
Engineering news on Phys.org
Simon Clement said:
Also please, is there any major difference between rules governing electrical installation in the US and in the UK? I have read the NEC, but now I was told that was America standard and to go get acquainted with the British way.

Yes, there are substantial differences. You have no choice, you must comply with the local codes. Do not attempt to rationalize your way around the rules. Just comply.
 
  • Like
Likes   Reactions: dlgoff
Simon Clement said:
I was wondering maybe there is such specification just like in the NEC which required 12 feet between sockets.

WOW seriously ?

I don't know what country you are from ? ... but that's pretty restrictive ... does that mean you cannot have double outlets, like we do here in Australia and New Zealand

124000-full.jpg

I am not aware of any minimum spacing requirements in our two countries. The sockets are places where needed.
Along a workshop workbench like mine I have 3 double outlets within an 8ft workbench length
Dave
 
  • Like
Likes   Reactions: Simon Clement
I don't know about minimum distances only. My point was that you can't apply one country's rules in another country. You have to look up the local rules, whatever they are.
 
  • Like
Likes   Reactions: jim mcnamara
anorlunda said:
My point was that you can't apply one country's rules in another country

totally agree :)
 
The 12 foot rule between receptacles is a maximum here in the USA. There are exceptions in some hallways and etc.
 
Averagesupernova said:
The 12 foot rule between receptacles is a maximum here in the USA. There are exceptions in some hallways and etc.
OK that is opposite to what the OP was thinking/stating where they were implying that that was the minimum
as in they couldn't be spaced closer

I am desperately trying to understand why there is a maximum distance ?
what is the point ?

I think the specific ruling needs to be stated from the USA NEC just to see if something is being lost in translation ?
 
davenn said:
I am desperately trying to understand why there is a maximum distance ?
what is the point ?
Convenience.
http://www.mcgarryandmadsen.com/ins...uld_the_electrical_receptacles_be_placed.html
The maximum spacing between receptacles, according to the National Electric Code, has been set at 12-feet since 1956--with no point along a wall being more than 6-feet from a receptacle. The logic behind that number is that an appliance with a standard length cord could then be plugged-in anywhere along the wall.
 
  • Like
Likes   Reactions: Simon Clement and davenn
No minimum spacing here, but an implied maximum of 12 feet
NEC210.52
(1) Spacing
Receptacles shall be installed such that no point measured horizontally along the floor line of any wall space is more than 1.8 m (6 ft.) from a receptacle outlet.
This rule provides for receptacle outlets to be installed so that an appliance or lamp with a flexible cord attached may be placed anywhere in the room near a wall and be within 6 ft. of a receptacle, minimizing the need for occupants to use extension cords. Although not an enforceable requirement, receptacles may be placed equal distances apart where there is no specific room layout for the general use of electrical equipment. Section 210.52(A)(1) does not prohibit a receptacle layout designed for intended utilization equipment or practical room use. For example, receptacles in a living room, family room, or den that are intended to serve home entertainment equipment or home office equipment may be placed in corners, may be grouped, or may be placed in a convenient location. Receptacles that are intended for window-type holiday lighting may be placed under windows. Even if more receptacles than the minimum required are installed in a room, no point in any wall space is permitted to be more than 6 ft. from a receptacle.
 
  • Like
Likes   Reactions: dlgoff, berkeman, Simon Clement and 1 other person
  • #10
thanks guys :)
 
  • #11
Ooh yeah, sorry guys, I meant to write maximum. Thanks for the correction.

So is there any such rule in the UK (like the NEC210.52 for America), that talks about spacing between sockets ?

Also please what is the book that talks about wiring regulations, british standard ?
 
Last edited:
  • #13
  • #14
Simon Clement said:
Please, what is the minimum spacing between sockets is based on the BSI standard or any other standard being used in the UK. I was wondering maybe there is such specification just like in the NEC which required 12 feet between sockets.

I live in the UK.

I don't think there is any minimum separation here. At least the electrician that wired our house had no objection to anything I proposed regarding spacing. In the UK most (but not all) houses are wired with "ring" rather than "radial" wiring. The number of sockets on each ring or radial will matter but the proximity to each other shouldn't. There are restrictions on the proximity to wet areas such as baths, showers etc

The height of sockets and switches above the floor is controlled by Approved Document Part M of the Building Regulations to make it easier for disabled people. I think this applies to new houses. Changes to existing houses are covered by a catch all that they should not make things worse for disabled people.

Part P makes some electrical work "notifiable" under the Building Regulations. In theory you can still do everything yourself (DIY) and pay a fee to notify Building Control but in practice it might work out cheaper to use a qualified electrician.

I think there might be a requirement in the Building Regulations to make "adequate provision" for electrical sockets but what section that's in I've no idea.

All the Approved Documents can be found here..

https://www.planningportal.co.uk/info/200135/approved_documents

Bandit has already linked to the 17th Edition of the wiring regs.
 
Last edited:
  • #15
PS Also worth noting that the Building Regulations differ in England, Scotland and Wales.
 
  • #16
Bandit127 said:
The "book" I think you are asking about is the 17th Edition of the IET Wiring Regulations.
https://en.wikipedia.org/wiki/BS_7671
The electrical home page of the Institution of Engineering Technology states they are the publisher of BS 7671:
The IET publishes the IET Wiring Regulations: BS 7671, the industry standard for electrical installations.

For those interested in having access to this standard, they provide a digital access. There is also have a Student's hub.

@berkeman These may be good references for the Useful EE Links and Search Engines sticky.
 
  • #17
  • Like
Likes   Reactions: dlgoff

Similar threads

  • · Replies 8 ·
Replies
8
Views
4K
Replies
3
Views
3K
  • Sticky
  • · Replies 704 ·
24
Replies
704
Views
120K
  • · Replies 11 ·
Replies
11
Views
2K
  • · Replies 12 ·
Replies
12
Views
3K
  • · Replies 30 ·
2
Replies
30
Views
3K
  • · Replies 3 ·
Replies
3
Views
1K
Replies
34
Views
5K
  • · Replies 95 ·
4
Replies
95
Views
8K
  • · Replies 1 ·
Replies
1
Views
4K