Synchro Signal Frequency changes

  • Thread starter Thread starter grasscut
  • Start date Start date
  • Tags Tags
    Frequency Signal
Join the discussion
Ask a follow-up here, or get your own question answered by working scientists, mathematicians and engineers — people, not an autocomplete.
Real named experts · corrections over time · the nuance an AI answer skips
36 replies · 4K views
Is it possible that it has been rewired wrongly, or the wrong cables are being used to make the connections.
My suspicion is that the connections to one phase has been reversed by connection to the wrong terminals, or is shorted to ground.
That would give a completely different set of V(s1-s2), V(s2-s3), V(s3-s1) voltages.
Check the connections.
Measure the three voltages relative to the common centre voltage which may not be ground.
 
  • Like
Likes   Reactions: sophiecentaur and jim hardy
Engineering news on Phys.org
grasscut said:
I honestly do not have the information. and i really wish i could share more.
i try to make do with what i have and the information you guys had shared with me thus far.
Are you saying that neither unit has a name plate on it? Even a few photos would help. We are too much in the dark to be of real help.
 
Baluncore said:
Is it possible that it has been rewired wrongly, or the wrong cables are being used to make the connections.
My suspicion is that the connections to one phase has been reversed by connection to the wrong terminals, or is shorted to ground.
That would give a completely different set of V(s1-s2), V(s2-s3), V(s3-s1) voltages.
Check the connections.
Measure the three voltages relative to the common centre voltage which may not be ground.
It might be the cause where the glide slope indicator itself has wired the S1S2S3 wrongly, but i don't know what's the configuration like. Even if the connection is wrong, will it affect the frequency? because the frequency seems to be quite a drastic change though. I have measured my system output with an angle position indicator and my outputs are correct. Even at the end of the system, i measured the wires of my outputs and it seems fine too. However, the voltage and frequency just changed when its connected to the glide path indicator terminal.

sophiecentaur said:
Are you saying that neither unit has a name plate on it? Even a few photos would help. We are too much in the dark to be of real help.
I just got to know the brand is AGI.
 
The lack of certification plates with manufacturer and model numbers suggests it has been scrapped. That may be because it was faulty.
Where did you get it from? Scrapped? Stolen? Junk shop?
The frequency might be bad because you are not measuring the wrong signal or relative to the wrong reference.
When you measure the voltage and frequency, what do you measure it relative to?
What actually is the instrument? Ground or aircraft based? Attitude indicator, turn and bank or glide slope indicator.
Is there a similar instrument on google immages? Can you give us a link or a pictures of your unit?
 
Baluncore said:
The lack of certification plates with manufacturer and model numbers suggests it has been scrapped. That may be because it was faulty.
Where did you get it from? Scrapped? Stolen? Junk shop?
The frequency might be bad because you are not measuring the wrong signal or relative to the wrong reference.
When you measure the voltage and frequency, what do you measure it relative to?
What actually is the instrument? Ground or aircraft based? Attitude indicator, turn and bank or glide slope indicator.
Is there a similar instrument on google immages? Can you give us a link or a pictures of your unit?

I measured the voltage and frequency across S1S2, S2S3, S1S3. i did mention that it is glide slope indicator in my previous post