  1. Mar 24, 2016 #1

    cnh1995

    User Avatar
    Homework Helper

    When an alternator is synchronized to the grid, its voltage and frequency are same as those of the grid. So, it shouldn't take any load at that instant. How is it brought into operation then? What is the procedure followed practically? My book says prime mover is given some extra energy so the alternator advances in angular position and then takes up load. No further explanation is provided. What happens to the excitation? Is it also increased? Also, why is terminal voltage of the alternators connected to a grid constant? Doesn' t armature reaction affect the terminal voltage? Please explain. I'm having a hard time relating the behavior of an individual alternator to the one connected to an infinite bus.( Sorry if the questions sound dumb...)
     
  2. jcsd
  3. Mar 24, 2016 #2

    anorlunda

    User Avatar
    Science Advisor
    Gold Member

    Normally it is given a small positive power at the start, just to avoid being tripped by reverse power relays (if any). Thereafter, power ramps at a rate and to levels according to a plan that fits the grid needs.

    The voltage regulator manipulates field voltage to hold terminal voltage constant. Changing terminal voltage changes VAR flow. That is done according to dispatch instructions, to serve the needs of the grid as a whole.

    My recommendation is to forget the individual case. Forget the case where is serves only one load. The only interesting case is when it is connected to the grid, and all the basic principles are revealed when studying one machine to an infinite bus.

    p.s. To toot my own horn, the PF Insights article AC Power Analysis: Part 1, Basics, and parts 2 and 3 which will follow in the next 2 weeks, give insight about grid operations from the grid's viewpoint.
     
  4. Mar 24, 2016 #3

    cnh1995

    User Avatar
    Homework Helper

    Thanks a lot for the reply.

    Does that decide the value of load angle δ?
    This is done automatically, right? So is it correct to say:without a voltage regulator, it wouldn't be possible to hold the terminal voltage constant?
    How is "need of the grid" analysed? Using SCADA?
    That would be really great!:smile: I'm eagerly waiting..
     
  5. Mar 24, 2016 #4

    cnh1995

    User Avatar
    Homework Helper

    In theory, we have studied alternators assuming balanced loading(equal load per phase). In practice, is it possible that the load is always balanced? What happens when the load is not balanced?
     
  6. Mar 24, 2016 #5

    anorlunda

    User Avatar
    Science Advisor
    Gold Member

    Real power delivered to the grid is proportional to angle, and that relationship between power and angle is perhaps the most important thing to know. Read part 2 of the insights article next week.

    That's complicated. It gets you into positive/negative/zero sequence three-phase currents that are difficult to explain or understand.

    Suffice it to say, in normal operation the phases are always nearly balanced. It is when we get a short circuit on one phase that they get very seriously out of balance.
     
  7. Mar 24, 2016 #6

    cnh1995

    User Avatar
    Homework Helper

    But balancing of phases depends on the load, right? So, is it right that the phases are "kept" balanced by some automatic system? I mean if phase R is feeding power to three loads A,B and C and if A is switched off, then some power of phase A is diverted to some other load such that the phases are balanced..something like that.?
     
  8. Mar 24, 2016 #7

    anorlunda

    User Avatar
    Science Advisor
    Gold Member

    No, not actively. Distribution engineers try to assign houses to circuits in such a way as to hopefully balance the phases most of the time. We also transpose the conductors of very long lines every X miles to help keep balance.

    AAEAAQAAAAAAAAPPAAAAJDU2OGE2YTk1LTBkMmUtNDkyMC1iOGYzLWZmZjRhZjhjNzVkOA.png

    It is far from perfect. There is no automatic system.
     
  9. Mar 26, 2016 #8

    anorlunda

    User Avatar
    Science Advisor
    Gold Member

    http://i.imgur.com/YbSVvRW.gif
    Here is a dramatic way to get unbalanced phases.
     
  10. Mar 26, 2016 #9

    jim hardy

    User Avatar
    Science Advisor
    Gold Member
    2016 Award

  11. Mar 26, 2016 #10

    cnh1995

    User Avatar
    Homework Helper

    Thanks a lot Jim! That was really helpful, especially the third thread.
    y.php?image=http%3A%2F%2Fi232.photobucket.com%2Falbums%2Fee289%2Foldjimh%2Fugenetic2_zpsb383c1b1.gif
    This simple little diagram has helped me more than once:smile:. Your way of explaining things is really amazing!
    Just a couple of questions..
    When steam supply to the turbine is increased, mechanical torque on the rotor is also increased, which makes it advance in angular position and take up the load. But what makes it rotate at a constant speed after providing extra torque? Is it the "motor action" of injected reactive current that creates an opposing torque?
    Also, when the grid injects reactive current into the machine, total flux remains constant and hence, terminal voltage remains constant. Then when exactly are AVRs used? The voltage is kept constant by the grid itself. I know AVRs change field excitation and changing the excitation changes the power factor but since the voltage is held constant by the grid itself(by injecting reactive currents), how are AVRs used practically?
     
  12. Mar 27, 2016 #11

    jim hardy

    User Avatar
    Science Advisor
    Gold Member
    2016 Award

    Motor action is exact right term but the current that produces torque is the real component not the reactive....
    Note in that phasor sketch above armature and field fluxes are nearly perpendicular so torque results. Were they aligned, they simply aid or oppose instead of making torque.



    AVR is on nearly all the time.
    Have you studied "Armature Reaction" ?
    If not it's okay.

    AVR holds terminal voltage constant when load on the grid changes.
    If you just hold constant excitation, terminal voltage will sag when customers get home and switch on their airconditioners.
    In simplest terms, a utility generator is like any other voltage source it has internal impedance. In fact, quite a bit of it and it's mostly inductive.
    Think of the generator as a Thevenin, an internal ideal voltage source in series with that internal impedance.
    The AVR measures terminal volts and adjusts the internal source so as to cancel the drop across that internal impedance.
    That keeps customers' voltage nearly constant.


    Hmmmm i sorta think the other way
    the grid is held constant by the combined actions of the hundreds of AVR's working to that end.
    Were a generator actually tied directly to an infinite bus you're right, it could not change terminal volts.

    Go back to the thevenin idea for a moment

    InfBus.jpg

    Vbus is fixed, so is Zinternal

    If you change Vinternal by changing excitation,
    machine amps will change by ΔVinternal / Zinternal
    and Zinternal being (mostly) inductive and fixed, Δmachine amps will be reactive. That's why voltage regulator controls Vars. AVR's keep each machine's Var contribution constant, too

    All the AVR's acting in concert is what keeps Vbus nearly constant.and the system stable.

    There are whole books on this subject
    i hope this helps prepare you for Anorlunda's insight article. I'm no power engineer , just try to help folks over the basic stumbling blocks i crawled across.
    You'll get to where you work the system in your head. Hang in there. Does your school have a machinery lab? It is very instructive to shine a stroboscope on a generator shaft and watch the angle change with load and excitation, then figure out why.. That was my favorite EE course - we had ~10hp machines and dynamometers.....

    old jim
     
  13. Mar 27, 2016 #12

    cnh1995

    User Avatar
    Homework Helper

    Right, I was confusing ideal infinite bus with a practical grid.:doh:
    So, in armature reaction, component of armature mmf which aligns with the field mmf is responsible for the sag in terminal voltage(due to demagnetizing action). Increasing the excitation will generate a reactive current in the machine.
    This reactive current will compensate for the demagnetization and keep the terminal voltage constant. Is this correct?
     
  14. Mar 27, 2016 #13

    cnh1995

    User Avatar
    Homework Helper

    We have all the equipment in the lab but unfortunately, no one's curious enough to be interested in such experiments. Everyone's just satisfied with the lecture notes and routine practicals(which are nothing but rote "procedure", followed by blind copying of the readings and somehow completing and submitting the journals so that the term is granted..). Sometimes I think they're making lab sessions as useless as possible.
     
  15. Mar 27, 2016 #14

    jim hardy

    User Avatar
    Science Advisor
    Gold Member
    2016 Award

    Chicken-egg ?

    Talk it through
    the thought experiment was machine tied to infinite bus with fixed voltage on bus
    so terminal volts are fixed as an initial condition
    let's say we raised excitation
    for our mental model the Thevenin internal voltage is what we raised and that pushed vars into the infinite bus
    but Thevenin voltage exists only in our mind (and on the phasor diagrams i used to dread).

    I'd say it this way

    Because the terminal voltage is fixed by the bus. , this reactive current will compensate for the cause a demagnetization or a remagnetization that offsets the change in field current.

    Maybe magnetizing or demagnetizing effect, i dont know - i polish words for days afterward....

    Anyhow if you grasp that concept you have a leg up on Armature Reaction. Most texts just give you formulas but when you can work it in your head the formulas seem almost intuitive.

    Over for the night - TTFN

    old jim
     
  16. Mar 27, 2016 #15

    cnh1995

    User Avatar
    Homework Helper

    Thanks a tonne Jim for putting up with me for so late! Google showed me it's almost 2:00 am in Arkansas.. Have a good night:star:!:smile:
    :dademyday:
     
  17. Mar 27, 2016 #16

    sophiecentaur

    User Avatar
    Science Advisor
    Gold Member

    Speed of the slowest ship, probably.
    Look around you and you will often see teachers who just couldn't handle the really interesting experiments that can be done with receptive students. In the UK, 'Science' can still be taught by non-specialists who only know about Biology or Chemistry and virtually nothing about Physics. Hence, the programmes of study include only rock bottom practical exercises and there's virtually no time for an inspired teacher to fit anything else in.
    (Glad I'm out of it, to be honest).
     
Know someone interested in this topic? Share this thread via Reddit, Google+, Twitter, or Facebook

Have something to add?
Draft saved Draft deleted



Similar Discussions: Synchronization of an alternator to the grid
  1. Synchronous generator (Replies: 18)

  2. Synchronous machine (Replies: 4)

  3. Synchronous machine (Replies: 4)

Loading...