Temperature rise in power transformers atheistrical

Click For Summary
SUMMARY

The discussion centers on the temperature rise in power transformers, specifically addressing a winding temperature of 73°C, which is deemed safe. However, if this temperature refers to a rise of 73°C, it indicates potential issues. The thermal capability of a transformer is defined by the KVA load that causes the winding hot spot to reach a limiting temperature, which is critical for determining the transformer’s lifespan. Advances in insulating materials have allowed for a 10°C increase in average temperature limits.

PREREQUISITES
  • Understanding of transformer thermal dynamics
  • Knowledge of KVA ratings and their implications
  • Familiarity with winding temperature measurements
  • Awareness of insulating materials and their advancements
NEXT STEPS
  • Research the impact of winding hot spot temperatures on transformer lifespan
  • Learn about thermal capability calculations for power transformers
  • Explore advancements in insulating materials for electrical applications
  • Investigate the relationship between KVA ratings and temperature rise in transformers
USEFUL FOR

Electrical engineers, power system designers, and maintenance professionals focused on transformer performance and longevity will benefit from this discussion.

Carl Pugh
Messages
384
Reaction score
3
The post "Temperature rise in power transformers was locked, however there may be a simple safe answer.

The post said the winding temperature was 73 deg C.
73 deg C is safe for winding temperature.

If it was winding temperature RISE of 73 deg C, then there may be problems.

So which was it?
 
Engineering news on Phys.org
The thermal capability of a transformer is defined in a slightly different way from the rated KVA. Thermal capability is the KVA load applied to the output of a transformer that causes the hottest area in the windings, called the winding hot spot, to reach some limiting temperature. The hot-spot temperature determines the rate of loss of life of the transformer as a whole, which is a cumulative effect. Therefore, the hot-spot temperature limit is usually based on a loss-of-life criterion. The KVA rating of a transformer is simply the steady-state KVA load applied to the output of the transformer at the voltage rating of the output winding that produces an average winding temperature rise (above the ambient temperature) equal to 65 (degree C.). Advances in insulating materials allowed a 10 (degree C.) increase in average temperature.



-----------------------------------------------------------------
Creative thinking is enjoyable, Then think about your surrounding things and other thought products. http://electrical-riddles.com
 

Similar threads

  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 19 ·
Replies
19
Views
2K
  • · Replies 6 ·
Replies
6
Views
18K
  • · Replies 15 ·
Replies
15
Views
3K
  • · Replies 5 ·
Replies
5
Views
1K
Replies
1
Views
2K
  • · Replies 5 ·
Replies
5
Views
6K
  • · Replies 1 ·
Replies
1
Views
4K
Replies
12
Views
2K
Replies
14
Views
3K