Test a cheap Surge Protector Power Strip (US 110V)?

  • Context: Electrical 
  • Thread starter Thread starter NTL2009
  • Start date Start date
  • Tags Tags
    Power Test
Click For Summary

Discussion Overview

The discussion revolves around testing a cheap surge protector power strip designed for US 110V systems. Participants explore methods for evaluating the performance and safety of surge protectors, particularly focusing on their ability to clamp high voltages and the implications of MOV (Metal Oxide Varistor) failure modes.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Experimental/applied

Main Points Raised

  • One participant suggests connecting a high voltage source with high impedance to verify the surge protector's clamping ability, considering safety precautions.
  • Another participant notes that MOVs typically fail short circuit, implying that a cheap surge protector may be a one-shot device after it conducts.
  • Concerns are raised about the difference between surges and temporary overvoltages, emphasizing that MOV failure is temperature dependent.
  • There is speculation about the specifications of MOVs in the surge protector and whether they can handle certain voltage conditions without tripping.
  • A participant mentions the lack of upstream series impedance in cheap surge protectors, suggesting that adding impedance could improve performance.
  • Experiences are shared regarding MOV failures, including the potential for loud failures and the importance of circuit breakers in preventing damage.
  • Reference is made to authoritative organizations like UL, which specify wiring requirements to enhance surge protection effectiveness.

Areas of Agreement / Disagreement

Participants express various concerns and hypotheses about the performance and safety of cheap surge protectors, with no clear consensus on the best testing methods or the reliability of these devices.

Contextual Notes

Participants acknowledge limitations in their testing methods and the need for careful consideration of safety when dealing with mains voltage. There are also unresolved questions regarding the specifications and effectiveness of MOVs in the discussed surge protectors.

NTL2009
Messages
637
Reaction score
393
TL;DR
A cheap surge protector doesn't have the LED monitoring for the MOVs/circuitry. Can I test it myself? I have an idea.
I figure I could connect a high voltage source with a high impedance, and verify that it clamps that voltage. The easy way would require very careful consideration to keep it safe - that would be to use a 220V outlet connected through a 220K Ohm Resistor on each leg.

Apply the current limited 220V to Hot-N; then Hot-GND; then N-GND. I think my meter will read peak V, but I should also see some reduction of RMS with the power strip connected.

Is there an easier/better way? Obviously, one must be aware and careful when dealing with line (mains) voltage, but I am familiar with the precautions, and this would be safe if normal precautions are taken. I could build little switcher and run it from a battery, but I really don't want to invest the time right now. Hmmm, maybe charge a couple caps to the 110V peak ( ~ 150V), put them in series, and monitor with a scope (assuming my meter can't catch that fast peak), or charge from a 220V sorce (small transformer, current limited, isolated).

I tried a search, either special equipment was used (not practical for a consumer), or the non-helpful advice of "don't take a chance, throw it out!".

TIA -
 
Physics news on Phys.org
Of course safety is first priority, but utility is second.

As I understand it, MOVs failure mode is short circuit. A cheap surge protector with MOV, I would expect to be a one-shot device. Once it conducts, that is end of life.

You might also consider the difference between a surge and a temporary overvoltage. It is important because MOV failure is temperature dependent.
Here's an article on that topic.EDIT: here is the belated link.

https://interferencetechnology.com/...oxide-varistors-in-end-use-equipment-designs/
 
Last edited:
anorlunda said:
Here's an article on that topic.

I don't think the article made it (maybe Greg's experimenting right now...)
 
NTL2009 said:
A cheap surge protector doesn't have the LED monitoring for the MOVs/circuitry. Can I test it myself? I have an idea.
What are the specs on the MOVs? I would expect the fire voltages to be (maybe) high enough to not be tripped by just 220V...
 
Thanks for the replies - that link looks great, I will look in more detail later, but yes, it appears these are for protecting against much higher voltage spikes, not a 2x over-voltage condition.

Hah, I just looked closely at my power strip, it says "Type 3 SPD 800V(L-N)". So I assume it has an 800V MOV L-N only, nothing from either to ground.

The switch has a built in circuit breaker, so if the MOV did fail short, that would keep tripping. I'm more concerned with a fail open, as then you have no real protection. I should look at how the indicators work.

Will read more later...
 
  • Like
Likes   Reactions: berkeman
The problem with cheap 'surge protectors' (which should just be called 'switchbars,' IMHO) is the lack of upstream series impedance. Tying a couple of tight knots (or clamp-on ferrites, if you have them laying around) in the surge protector power cord can improve performance by a surprising amount.
 
NTL2009 said:
The switch has a built in circuit breaker, so if the MOV did fail short, that would keep tripping. I'm more concerned with a fail open, as then you have no real protection. I should look at how the indicators work.
Yeah, the MOV should clamp a few times to protect against transients, and eventually (sooner for cheaper MOVs) it will fail short, which will open the breaker. Usually MOVs fail short (in my testing experience), and then fail open if they are subjected to more hits (often with a very loud bang).

I learned the "loud bang" part the hard way in our test lab a few years ago. Another engineer was running life tests on various brands of MOVs so that we could recommend the best part to our customers in our powerline communication reference design. Unfortunately he would often leave the Surge tester unattended while running these tests, but at least he would put a thick Lexan cover over the test fixture. Too many times I would be working in the lab on something, and I'd hear the "tick" sound of the Surge tester firing every couple of minutes. Then sometimes you would hear a little louder "tick", which it turned out was the MOV failing short on that hit. Then a couple minutes later, "BANG!" it would destroy itself on the next hit. Sacred the Bejeezus out of me too many times... o0)
 
  • Like
Likes   Reactions: anorlunda
Dullard said:
The problem with cheap 'surge protectors' (which should just be called 'switchbars,' IMHO) is the lack of upstream series impedance.
I can't find it at the moment, but there was a thread several months ago involving Surge Suppressors. Here in the States, the authoritative organizations specified that (at least consumer grade) surge protected outlet strips are have at least 10 meters of wiring between them and the overcurrent device (circuit breaker).

Ahh, found the old thread, but it's pretty long winded. https://www.physicsforums.com/threads/surge-protector-specs.955697/post-6062621

The 'authoritative organization' is UL (Underwriter Laboratories). The reason for the 10 meters of wiring is it adds 10uH of inductance, thereby supplying an impedance to drop the surge voltage when the Surge Suppressor conducts.

Cheers,
Tom
 
  • Like
Likes   Reactions: berkeman and Dullard

Similar threads

  • · Replies 10 ·
Replies
10
Views
4K
  • · Replies 5 ·
Replies
5
Views
3K
Replies
1
Views
4K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 29 ·
Replies
29
Views
20K
  • · Replies 1 ·
Replies
1
Views
3K
  • · Replies 19 ·
Replies
19
Views
5K
Replies
20
Views
35K
  • · Replies 8 ·
Replies
8
Views
6K