Is My Three Phase Meter Giving Accurate Measurements?

AI Thread Summary
The discussion revolves around concerns regarding the accuracy of a three-phase meter measuring power in an office setting. The user reports unusual readings, including a negative power factor (PF) for a duct heater and zero voltage on phase C, raising questions about the meter's functionality and wiring. It is noted that lights do not require three-phase power, but can be distributed across phases for balance, which appears to be an issue in this case. The user seeks confirmation of potential faults before proceeding with repairs, emphasizing the need for clarity on how the meter interprets phase angles and loads. Overall, the conversation highlights the complexities of three-phase power measurement and the importance of proper transformer and meter setup.
Shant
Messages
3
Reaction score
0
Hello all,

Recently one of the power meters on one of our office's panelboards has been giving sensor garbage, calling the others' measurements into question.

I have two 277/480Y transformers, one going to a two phase 480V duct heater and one going to the lighting (the meter reads three phase).

The duct heater reads as follows:
Load:.1KW
A 277.8V 0A 0%PF
B 280.2V .6A -23.9%PF
C 281.8V .5A 72.2%PF

And the lighting:
Load: .4KW
A 280V 0A 0%PF
B 278V 1.5A 99.9%PF
C 0V 0A 0%PF


There definitely seems to be at least one thing wrong: Why am I getting a negative PF for a duct heater? Apart from that, I'm unsure why I'm reading 0V on phase C for a supposed 3 phase unit. It isn't mislabeled; the meter is telling me three phase on the display. I'm not sure why lights would need 3PH power in the first place.

I would like to be sure that something is wrong before I call for repairs again. Anything seem off?
 
Engineering news on Phys.org
For the heater, the line-to-line load for 480 volts also means the current phase angles will be different relative to the line-to-neutral voltage sensing connections for B and C. The phase angle should be the same, but of opposite direction, on each. Technically, you're still consuming power through both, so the PF should still be positive. But with a resistive load, your PF should be nearly 100%, yet a L-to-L phase angle difference can confuse the readings. Combined, it should show the equivalent of 100%. But I don't really know how the meters work to handle that situation.

Lights don't need three phase. But lights can be distributed among phases to keep things in balance. Yours apparently are not. And it appears that either phase C is not even connected, or the meter connection is not there. Everything is coming on over phase B (which is not necessarily the same phase as phase B on the heater). One way to approach balance is to have the heater on 2 phases like it is, and the lights on the remaining phase. How your transformer phase (mis-)wirings are rotated could in fact do that, anyway.

How big are these transformers and meters? Got photos?
 
The meter is the e-mon-d-mon 3000 series.

http://www.emon.com/products_class3000.html"

Pictures on the way.
 
Last edited by a moderator:
So this is not utility measurements, but just internal monitoring? Are the transformers utility transformers or smaller internal units? If non-utility, I'd like to know the primary voltage and type (delta or wye).
 
They're utility. The monitors are set up to measure the office's (it's a leased space within a complex) individual consumption.
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
Thread 'Beauty of old electrical and measuring things, etc.'
Even as a kid, I saw beauty in old devices. That made me want to understand how they worked. I had lots of old things that I keep and now reviving. Old things need to work to see the beauty. Here's what I've done so far. Two views of the gadgets shelves and my small work space: Here's a close up look at the meters, gauges and other measuring things: This is what I think of as surface-mount electrical components and wiring. The components are very old and shows how...
Back
Top