Transformer connected in parallel question

Click For Summary
SUMMARY

This discussion focuses on the calculation of percentage overload on Transformer B when connected in parallel with Transformer A. Transformer A is rated at 300 kVA with an impedance of (0.09+j0.18)Ω, while Transformer B is rated at 200 kVA with an impedance of (0.09+j0.23)Ω. The solution involves assuming a voltage of 1000 V and using the formula kVA a = kVA total (Zb/(Za+Zb)) and kVA b = kVA total (Za/(Za+Zb)) to determine the load distribution. The key takeaway is that the voltage drops across the impedances must be equal since both transformers supply a common load.

PREREQUISITES
  • Understanding of transformer ratings and impedances
  • Knowledge of parallel circuit analysis
  • Familiarity with power factor calculations
  • Basic proficiency in electrical engineering concepts
NEXT STEPS
  • Study transformer load sharing in parallel configurations
  • Learn about calculating power factor and its implications
  • Explore the concept of impedance in AC circuits
  • Research methods for analyzing voltage drops in parallel circuits
USEFUL FOR

Electrical engineering students, power system engineers, and professionals involved in transformer design and analysis will benefit from this discussion.

eddievic
Messages
47
Reaction score
0

Homework Statement


The question is as per my attachment

Homework Equations


The Attempt at a Solution



I found the following help of the internet but do not know where to start any assistance would be appreciated:
you don't need to be concerned about matched turns ratio. You can assume that the turns ratio is 1:1 and that the transformers are single-phase or that you have per-phase, wye data. Since the answer is to be given as a percentage, you can assume a convenient voltage like 1000 V. That reduces the problem to a relatively simple network of (0.09 + j0.18) in parallel with (0.09 + j0.23) and that parallel combination in series with (R + jX). With the assumed voltage, the power factor of the current in one branch, and the kva of the load supplied by that branch.
 

Attachments

Physics news on Phys.org
Can't open your file. (I have office 2003).
Convert to pdf?
 
For some reason i can't upload the attachment anyways the question is as follows:

Transformer A is rated at 300 kVA with an impedance of (0.09+j0.18)Ω

Transformer B is rated at 200 kVA with an impedance of (0.09+j0.23)Ω

if these transformers are connected in parallel to supply a common load, determine the percentage overload on B when A supplies its full load at p.f. 0.45 lag
 

Attachments

We need input and output impedances of both transformers.
 
rude man said:
We need input and output impedances of both transformers.

This is the complete question as i have it
 
Looking at this again and i have found

Full load current presuming 1000v and at single phase:
Transformer A = 300000/1000 = 300A
Transformer B = 200000/1000 = 200A

I know that power factor is 0.45 lag so this is cos^-1 0.45 = 63.25 degrees

kVA a = kVA total (Zb/Za+Zb)
kVA b = kVA total (Za/Za +Zb)

I think I have everything to solve but cannot figure out the methodology on this one can anyone assist?
 
With any luck, this may not be as complicated as it might seem. You know the voltage drops across the impedances must be identical, since the transformers are working into a common load voltage.

Focus on just magnitudes of the drop across the impedances. These must be equal.

Are you provided with the correct answer, so we can check?
 
NascentOxygen said:
With any luck, this may not be as complicated as it might seem. You know the voltage drops across the impedances must be identical, since the transformers are working into a common load voltage.

Focus on just magnitudes of the drop across the impedances. These must be equal.

Are you provided with the correct answer, so we can check?

Thanks for your help.

I worked out the loads on the two Transformers connected in parallel and then worked out the difference in percentage overload and submitted my answer and this came back correct.

I think it was just the question that was puzzling me I was not sure what it was asking. :)
 
Hi eddievic I'm stuck on the same question have been for days, how did you work out the loads without the total KVA or total wattage or is it just as simple as adding the 2 KVA's of the transformers together
 

Similar threads

  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 7 ·
Replies
7
Views
2K
  • · Replies 33 ·
2
Replies
33
Views
10K
  • · Replies 8 ·
Replies
8
Views
3K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 6 ·
Replies
6
Views
2K
  • · Replies 2 ·
Replies
2
Views
1K
Replies
44
Views
6K
  • · Replies 31 ·
2
Replies
31
Views
5K