Transmission Line, Max Real Power Transfer

Click For Summary
SUMMARY

The discussion centers on the calculation of maximum real power transfer in a 230kV, 160km transmission line with specific parameters: R = 0.0151, X = 0.1476, and Y = 0.288. The Thevenin equivalent is established as V_{Th} = 1.022 ∠ -0.13° and Z_{Th} = 0.0158 + j0.15077. Participants express confusion regarding the appropriate method for calculating the maximum real power transfer, particularly whether to use the conjugate of the Thevenin impedance or to incorporate the load's lagging power factor of 0.8. The conversation suggests that power factor correction may be a relevant consideration for optimizing power delivery.

PREREQUISITES
  • Understanding of Thevenin's theorem in electrical engineering
  • Familiarity with transmission line parameters and their significance
  • Knowledge of power factor and its impact on real power transfer
  • Basic concepts of impedance and complex power in AC circuits
NEXT STEPS
  • Study the application of Thevenin's theorem in power systems analysis
  • Learn about maximum power transfer theorem and its implications in transmission lines
  • Research power factor correction techniques and their benefits in electrical systems
  • Explore the effects of load impedance on real power transfer in AC circuits
USEFUL FOR

Electrical engineers, power system analysts, and students studying transmission line theory and optimization of power delivery.

jegues
Messages
1,085
Reaction score
3

Homework Statement



A 230kV, 160km long transmission line has the following parameters expressed on a 230kV, 100MVA base.

R = 0.0151
X = 0.1476
Y = 0.288

The sending end voltage of the line is held constant at 1.0 pu. The load at the receiving end has a lagging power factor of 0.8.

Show that the Thevenin equivalent yields,

V_{Th} = 1.022 \angle -0.13^{\circ}

Z_{Th} = 0.0158 + j0.15077

Homework Equations





The Attempt at a Solution



See figure attached for my attempt.

I'm confused regarding the maximum real power transfer limit.

Is this supposed to be calculated assuming,

Z_{load} = Z_{Th}^{*}

or are we supposed to use the PF of the load stated in the question somehow?

Thanks again!
 

Attachments

  • TlineAt.JPG
    TlineAt.JPG
    42.9 KB · Views: 525
Physics news on Phys.org
While it may seem to be hinting at conjugate matching, as far as power transmission goes that sounds unrealistic to me. Who would be happy to have a load voltage just half of what the power station was supplying? With half of the station's power output going to heat in the powerline? It's overdoing the de-icing just a tad.

Maybe they are asking what power you could get to that load if you used powerfactor correction?

When in doubt, ask your professor for clarification.
 

Similar threads

Replies
3
Views
3K
Replies
8
Views
3K
  • · Replies 4 ·
Replies
4
Views
3K
  • · Replies 7 ·
Replies
7
Views
6K
  • · Replies 1 ·
Replies
1
Views
2K
  • · Replies 5 ·
Replies
5
Views
6K
  • · Replies 5 ·
Replies
5
Views
2K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 7 ·
Replies
7
Views
4K
  • · Replies 4 ·
Replies
4
Views
4K