Troubleshooting No Working Outlets in Room: Tips Before Calling an Electrician

  • Thread starter Thread starter Greg Bernhardt
  • Start date Start date
  • Tags Tags
    Work
Click For Summary

Discussion Overview

The discussion revolves around troubleshooting a situation where no electrical outlets are functioning in a room. Participants share various diagnostic approaches and potential causes, focusing on practical steps to take before involving an electrician. The conversation includes technical insights into wiring and circuit behavior.

Discussion Character

  • Exploratory
  • Technical explanation
  • Debate/contested
  • Mathematical reasoning

Main Points Raised

  • One participant suggests using an outlet tester to diagnose the issue, though another questions its utility given the outlets are already known to be non-functional.
  • Discussion about the presence of GFI switches and the possibility of resetting them, especially if an outdoor outlet is involved.
  • Another participant emphasizes the importance of checking circuit breakers, noting that even if a fuse appears intact, it may still be faulty.
  • A technical explanation is provided regarding the daisy-chain wiring of receptacles, with suggestions for testing connections by banging on outlets to check for intermittent faults.
  • One participant shares a personal anecdote about discovering hidden wiring configurations in an older home, highlighting the complexity of electrical systems.
  • Concerns are raised about safety hazards related to reversed hot and neutral connections, with recommendations for checking voltage and continuity.
  • Several participants share their experiences and offer various troubleshooting methods, including visual inspections and using a radio to detect power fluctuations.
  • Ultimately, one participant mentions that they decided to call an electrician after gathering information from the discussion.

Areas of Agreement / Disagreement

Participants generally agree on the need for systematic troubleshooting before calling an electrician, but multiple competing views and methods are presented without a consensus on the best approach. The discussion remains unresolved regarding the specific cause of the outlet failures.

Contextual Notes

Some participants mention the potential for multiple issues, such as reversed hot/neutral connections and open circuits, indicating that the situation may not be straightforward. There are references to older wiring practices and the reliability of modern electrical components, which may affect troubleshooting outcomes.

Who May Find This Useful

This discussion may be useful for homeowners experiencing electrical issues, DIY enthusiasts interested in troubleshooting electrical systems, and individuals seeking to understand common electrical problems and solutions.

Messages
19,911
Reaction score
10,928
I have a room where no outlets work. The fuse looks ok. What are some things I can test for or look for before I call an electrician?
 
Engineering news on Phys.org
Get an outlet tester from the local hardware store (they are really cheap) and back-track from there. Good luck.
 
turbo said:
Get an outlet tester from the local hardware store (they are really cheap) and back-track from there. Good luck.

What information will that give me? I already know they don't work :)
 
Is there a GFI switch on any of them (ground fault interrupt)? Try to push the button (usually has an 'R') to reset. Could be an outside outlet that is on the room circuit (which is normally a code violation around here) that has the GFI.
 
BTW, the most productive (and cheapest) way to test such a failure is to reset any breakers and see if that fixes your issue. Most modern homes don't have fuses, but breakers are ubiquitous. Give it a shot and tell us what happened.
 
Greg,
Receptacles are usually wired in a daisy-chain fashion. Wires enter a receptacle on the line side, feed the socket, then separate wires exit the receptacle on the load side to feed downstream receptacles.

In the old days the line-side and load-side wires were attached to the receptacle using brass screw terminals, very reliable.

At some point some builders decided they could save a few dollars in labor: receptacles became available with a push-in contact. All the electrician had to do was strip the wire and jam it in the hole, no bending the wire, no screwdriver. Problem is these are unreliable and opens are not uncommon after some years.

Try this:
Plug incandescent lights into the dead receptacles.
Look at the layout of the room and try to guess which dead receptacle is at the "head" of the daisy-chain. Bang on the receptacle with your hand/fist and see if any light flashes on.

Next, try to guess which *working* receptacle is just upstream of the chain of dead receptacles. Bang on it. (bad connection is just as likely the load-side feed from a "good" receptacle as it is the line-side wires feeding into the first "dead" receptacle).

If this does not help, are you comfortable removing a receptacle and probing voltages with a multimeter?
 
Last edited:
Hi Greg,

I just want to echo what Turbo said. Most of the time it's the fuse/breaker. Even though the fuse looks good, try taking out a fuse that you know works (with similar trip rating) and plug that one into the guilty circuit. Also, sometimes receptacles can be wired to a standard wall switch, check those out to ensure they're on (not to insult your intelligence!). I did electrical work for 6 years and anytime everything in a circuit stopped working, you could bet it was a switch/breaker/fuse.

Good luck and let us know how it goes!
Jim
 
Greg Bernhardt said:
What information will that give me? I already know they don't work :)

LOL. It can tell you stuff like you have an open ground, or reversed hot/neutral, stuff like that.
 
EMI guy's advice is sooooo perfect here...
Try to imagine the room before the walls were covered - what's shortest distance between receptacles?

Last time I had that trouble in one whole room it was an outlet in adjacent room, call it room zero.. Room zero's outlets all worked but all of next room over (room one) was daisy chained from that one outlet, and banging in room one didn't show it. I had to laboriously find it by individual inspection of everything in that whole part of the house..
It was the infamous "Load Side Open" as described by EMI guy. Fortunately in the hot wire.
In hindsight, the two receptacles were only about a foot apart , but in separate rooms on opposite sides of interior wall. Shoulda been obviouser than it was.. I put the wires back under the screws instead of the 'lazyman's push-in terminus.'

The WalMart $5 outlet tester is great because it'll find an open neutral, too, which could be dangerous.

http://www.walmart.com/ip/21192894?...1=g&wl2=&wl3=21486607510&wl4=&wl5=pla&veh=sem

oops last year they were $5. But there's no inflation, right ?

Anyway - get a tester and bang away at recaptacles on both sides of the walls before placing that call.

old jim
 
Last edited:
  • #10
Bought an outlet tester and no light turned on when I plugged it into the sockets. The rooms next to it work and show hot/neu reverse.
 
  • #12
Got one word for you, son. Electrician. :smile:
 
  • #13
Those swapped H-N outlets ought to be fixed. It's a shock hazard when changing bulbs in lamps plugged into them - the tin colored base is "hot" even with switch off.
 
  • #14
Greg Bernhardt said:
I have a room where no outlets work. The fuse looks ok. What are some things I can test for or look for before I call an electrician?

The fuse "looks" ok?
Is it a screw in type?
Have you tried unscrewing it and screwing it back in?
If that doesn't fix it, do you have a multimeter to test it with?
Or do as Jimbo57 stated, and simply swap fuses and see if the power goes out somewhere else.

One last thing.
When I bought my house, the electricity was turned off at the meter box.
So I turned off all of the circuit breakers and called the electric company to have them turn it on while I was at work.
When I got home from work, the house was incredibly warm.
So I went into the kitchen and the burners on my stove were on high.
How could that be, with all the breakers open?

It turned out that the kitchen was powered by the original, fused box, hidden inside one of the lower kitchen cabinets. The rest of the house was powered by the breaker box.

My house was built in 1945, and my guess is the breaker box was added during the 70's.

ps. Good luck!
 
  • #15
OmCheeto said:
... kitchen was powered by the original, fused box, hidden inside one of the lower kitchen cabinets. The rest of the house was powered by the breaker box.

My house was built in 1945, and my guess is the breaker box was added during the 70's.
You're lucky. This is what I have to deal with in my parents old house.

Knob_and_Tube_Wiring438-DFs.jpg
 
  • #16
At least cables are kept properly distanced from the wood :wink:
 
  • #17
The rooms next to it work and show hot/neu reverse.

hmmm - nobody said there's only one thing wrong.

Are there any big loads in that room, say an airconditioner?
I'm suspicious whether that reversed hot/neutral indication is a symptom of second open circuit in a neutral wire.
Carefully check your "dead" room outlets for first zero voltage, then continuity between neutral slot and ground hole. If the wires to panel are intact it should read less than an ohm. You can make that test with breaker or fuse out if you like.



Could be it's time to plug in a radio with volume set loud to a wall outlet in that room,
start opening receptacles and switches for visual inspection of wires.
Radio is to announce when you perturb a loose connection and power briefly flashes on.
You want to see black wire into shorter of the two slots that's the hot
it's always the brass colored screws, or rear push-in holes on that side
longer slot is neutral, white wire to white screws,
2012-05-05_032025_duplex.jpg
 
  • #18
Borek said:
At least cables are kept properly distanced from the wood :wink:
If only I could the wood as a safety ground. :biggrin:
 
  • #19
Thanks for all your help! I learned a little bit, but in the end we called an electrician to come out tomorrow :)
 
  • #20
Let us know what he finds !

old jim
 
  • #21
Does the light work in the room? Generally they are on the same circuit. If the light works, then I would pull out each receptacle and inspect the wiring connections. More than likely, someone did not use "rat tails" and a wire slipped out along the way.

If it is the panel, simply remove that fuse and check for power. If there is power, inspect the fuse and possibly replace. If there isn't power, a wire came lose in the fuse panel. Reconnect that wire.

Now let's see what your electrician finds...
 
Last edited:
  • #22
psparky said:
Does the light work in the room? Generally they are on the same circuit.

Around these parts, the lights are supposed to be on their own circuit, per code.

This is so when you run the toaster, microwave, coffee pot, dishwasher, crockpot, coffee grinder, and blender, all at the same time, and blow the breaker, you aren't left in the dark.
If the light works, then I would pull out each receptacle and inspect the wiring connections. More than likely, someone did not use "rat tails" and a wire slipped out along the way.

If it is the panel, simply remove that fuse and check for power. If there is power, inspect the fuse and possibly replace. If there isn't power, a wire came lose in the fuse panel. Reconnect that wire.

Now let's see what your electrician finds...

I would have posted the fact that it was possible to check for a loose wire at the fuse panel, but that would have been extremely dangerous for a non-electrician to fix. (Some of us like having Greg around)

Another unlikely scenario happened at my mothers house about 30 years ago. One of the 120 volt hot lines became disconnected somehow, prior to entering the house. I scratched my head for a while with that one. Fortunately, it cost us nothing to fix, as everything prior to the post that sticks out of the roof where the wires enter, is the electric company's problem.
 
  • #23
You could try the Confucian approach and invite all your friends round. "Many hands make light work".
(Sorry - too good to miss and the old ones are the best.)
 
  • #24
OmCheeto said:
Around these parts, the lights are supposed to be on their own circuit, per code.

This is so when you run the toaster, microwave, coffee pot, dishwasher, crockpot, coffee grinder, and blender, all at the same time, and blow the breaker, you aren't left in the dark.

I would have posted the fact that it was possible to check for a loose wire at the fuse panel, but that would have been extremely dangerous for a non-electrician to fix. (Some of us like having Greg around)

Another unlikely scenario happened at my mothers house about 30 years ago. One of the 120 volt hot lines became disconnected somehow, prior to entering the house. I scratched my head for a while with that one. Fortunately, it cost us nothing to fix, as everything prior to the post that sticks out of the roof where the wires enter, is the electric company's problem.


Insteresting consideration about the light, but this sounds like a recent addition to code so most homes are not going to be wired this wire. But certainly a consideration.

And yes, please disconnect or turn off main breaker in panel before re-wiring. Unfortunately we will need the panel on for any voltage checks. Some people don't like them, but the fully insulated test light is probably the safest. Uninsulated voltage meter leads can cause HUGE arcs if shorted!
 
  • #25
A few years ago I was having outlet problems. I finally found a neutral wire broken inside the insulation 2" before the outlet. I found it while doing a outlet to outlet inspection. The wire just bent funny.
 

Similar threads

Replies
18
Views
2K
Replies
24
Views
3K
  • · Replies 36 ·
2
Replies
36
Views
6K
  • · Replies 5 ·
Replies
5
Views
1K
Replies
12
Views
4K
  • · Replies 3 ·
Replies
3
Views
2K
  • · Replies 12 ·
Replies
12
Views
2K
  • · Replies 32 ·
2
Replies
32
Views
4K
  • · Replies 7 ·
Replies
7
Views
3K
  • · Replies 83 ·
3
Replies
83
Views
8K