I am not versed in those industry standards.
When starting, i go to manufacturers datasheets to learn the terminology. So, here we go.Here's one company's explanation of the term "Pilot Duty"
http://www.macromatic.com/blog/relays/what-are-pilot-duty-ratings-and-which-macromatic-products-have-them/Note they describe interposing relays, relays that drive relays not motors.I don't know anything about that table or where it's from.
If i don't answer that question i might be thought ignorant , but if i do answer it'll probably remove all doubt.
So here's best i can do for you:
This continuation of Macromatic's tutorial
http://www.macromatic.com/blog/relays/how-to-apply-pilot-duty-ratings/
says
and i
think that is industry practice. Does your source say they tested to those conditions ? If so, probably that
particular type of relay contact has passed such a test.Hmmm. Where did that table come from ?
According to Macromatic's tutorial, " A " means 10 amp thermal current (continuous) and B means 5 amp. No mention of horsepower.
But note these are for Pilot Duty relays, one ought really use a contactor for a motor. That's because it might be asked to break LRA .
Yes, going strictly by the rules.
I would prefer for a design with my name on it, that LRA be within thermal current because the motor could stall .
FLA should certainly be within break current.
But as i said above, i think i wouldn't use a pilot relay for powering a motor of significant size. Should the motor stall the relay might be asked to interrupt LRA.Answer: Briefly it should withstand it. 7200 is its maximum 'make' rating, observe that amps is always 7200 / voltage. That's because on "make" a contact bounces and arcs and might weld. At higher voltage they reduce the allowed current to discourage contact welding...
.....
Aha! I finally see it ... your table tells us an A600 contact should be
equivalent to a switch rated
under other standards for 1hp motor or 720 VA coil . But 7200 VA exceeds the thermal rating of the contact. It can take that for only a short interval. See Note 3 at Macromotion tutorialPilot Duty relay should control the motor starter(contactor)'s coil.
I'd have no fear of using one for a smaller motor, though, one whose LRA is within relay BREAK current.
See recent thread Snubber Circuit. Control relays driving a motor were burning up.
Well i learned something about those relay ratings today . Thank you !
here's a snip from an Allen-Bradley catalog . I hope to find and read the NEMA standard.
View attachment 105360
Corrections are welcome.
old jim