Understanding the Safety of Domestic Shaver Sockets: Explained

  • Thread starter Thread starter Adz
  • Start date Start date
AI Thread Summary
Shaver sockets are equipped with an isolating transformer that reduces the risk of electric shock by decoupling the circuit from ground. While this design minimizes shock hazards when using devices like razors, touching both live and neutral terminals can still result in a shock. GFCI (Ground Fault Circuit Interrupter) protection is recommended for bathroom receptacles to further enhance safety by cutting off power if a ground fault is detected. Historically, 'razor only' sockets were the standard in bathrooms, but modern recommendations favor GFCI outlets for better protection. Understanding these safety features is crucial for safe usage in wet environments.
Adz
Messages
9
Reaction score
0
I was told that a shaver socket has an inbuilt isolating transformer to prevent electric shock. But surely if someone touched Live and Neutral at the same time, at the socket outlet, they would get a shock? Can someone explain... thanks..
 
Engineering news on Phys.org
Receptacles located in bathrooms, such as a shaver might be plugged into, should have GFCI capability. You might see a push to test and reset button on the receptacle. Or the breaker supplying the receptacle might be GFCI. GFCI means ground fault circuit interrupting. If the GFCI device detects current leaking to ground it opens the circuit stopping the current flow.
You could still kill yourself getting between the two legs of the supply. But if current were flowing through you to ground the GFCI would trip.
 
I believe that Adz is referring to the original 'razor only' sockets which were the only ones allowed in bathrooms up until a couple of decades ago. A quick Google brought up this explanation.
jkogel
Active Poster


Location: Sooke, BC
Posts: 177
Re: Razor only outlets
Please Note: This user is a non-member guest and is in no way affiliated with InterNACHI.
Quote:
Originally Posted by Mark Nicholet
Thanks, I think it would be good idea to recommend replacement with GFI. But, how does this 'razor only' low volt transformer outlet prevent a shock hazard by being isolated from ground? I would think it would increase shock hazard if there is no ground.

Mark, the isolation transformer consists of 2 coils insulated from each other. 120 volts from the household circuit running thru 1 coil produces 120 volts in the secondary coil. You could still shock yourself by touching both of the output terminals. But there is no electrical potential between one of the output terminals and ground, as there is with conventional wiring because it is a little isolated mini-circuit. Drop it in the tub, theoretically no shock!

As for the lack of ground, most razors and hair dryers are 2-prong devices anyways, no ground wire to the chassis, but the plastic body provides insulation.

I'm not sure if it's legitimate to quote someone from another forum without permission, so this might get deleted.
 
Last edited:
Cool, thanks. I have never seen one.
 
cheers thats, that's exactly what i was thinking.
 
Adz said:
I was told that a shaver socket has an inbuilt isolating transformer to prevent electric shock. But surely if someone touched Live and Neutral at the same time, at the socket outlet, they would get a shock? Can someone explain... thanks..

The isolation transformer electrically decouples the circuit. Essentially, the ground that the utility company provides (at the pole or pad transformer) does not get passed across the transformer (hence the name). Thus one cannot receive an electrical shock from touching only the hot wire will grounded to the earth. However, if one completes the circuit by touching the hot and the return wire then one will indeed receive an electrical shock.

CS
 
Hi all I have some confusion about piezoelectrical sensors combination. If i have three acoustic piezoelectrical sensors (with same receive sensitivity in dB ref V/1uPa) placed at specific distance, these sensors receive acoustic signal from a sound source placed at far field distance (Plane Wave) and from broadside. I receive output of these sensors through individual preamplifiers, add them through hardware like summer circuit adder or in software after digitization and in this way got an...
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker. I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test. I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth...
I am not an electrical engineering student, but a lowly apprentice electrician. I learn both on the job and also take classes for my apprenticeship. I recently wired my first transformer and I understand that the neutral and ground are bonded together in the transformer or in the service. What I don't understand is, if the neutral is a current carrying conductor, which is then bonded to the ground conductor, why does current only flow back to its source and not on the ground path...