US 2-phase conversion to EU one phase

  • Thread starter dabnug
  • Start date
  • Tags Tags
    Phase
41 replies · 21K views · last reply
@Guineafowl I get that everyone has told me how to hook up a machine that is manufactured for the US power grid. Except my manufacture is telling me this is wrong. So my line of questions is to educate myself so that I am confident that they are one in the same.

@Asymptotic Attached is the schematic they provided.
 
Attachments
  • Wiring schematic of a Schneider LXM23DU10M3X servo drive connected to motor M1 with terminals L1, L2, R, S, U, V, W, B1, B2, plus relay KA1 and KA2 contacts driving PLCY2 and PLCY3 with DC24V, servo direction and servo pulse outputs.
    4.jpg
    42.1 KB · Views: 572
  • Wiring schematic of a Mitsubishi FX3SA-14MT-CM PLC with terminal blocks for inputs X0 to X13 and outputs Y0 to Y5, plus a numbered list of connected sensors, switches and outputs labelled in Chinese and English.
    3.jpg
    30.4 KB · Views: 565
  • Front panel wiring diagram of an MCGS TOC7062KD touch panel with a power indicator lamp (terminals 11 and N), Manual/Auto selector SB5 (terminals COM, Y3, 24, 26), Start button SB1 (COM, X06), Power switch SB2 (03, 04), Emergency stop SB4 (COM, X07), Stop button SB3 (COM, X03), and +24V, COM and PE supply terminals.
    1.jpg
    33 KB · Views: 499
  • Wiring schematic of a machine's power circuit with a single-phase L1/N supply feeding a breaker QF1, contactor MC1, a servo driver driving motor M1, a transducer driving cutter motor M2, a PLC power switch, and a full cut electric valve.
    2.jpg
    35.9 KB · Views: 594
dabnug said:
@Guineafowl I get that everyone has told me how to hook up a machine that is manufactured for the US power grid. Except my manufacture is telling me this is wrong. So my line of questions is to educate myself so that I am confident that they are one in the same.

@Asymptotic Attached is the schematic they provided.
The servo drive for motor M1 is a Schneider Electric model LXM23DU10M3X.

https://www.schneider-electric.com/...s&filter=product_parent_category_id-166406748

The input voltage specification for it when wired for single phase is 220 V nominal with a range from 200V to 255V. It can't be wired for 120V operation.

On the print, the drive is connected to "L1" and "N". In this case, "N" isn't neutral - the center tap on a 230V transformer in a US split single phase system - but is rather the other hot lead "L2".
 
  • Like
Likes   Reactions: CalcNerd and Guineafowl
https://www.schneider-electric.com/...s&filter=product_parent_category_id-166406748

The input voltage specification for it when wired for single phase is 220 V nominal with a range from 200V to 255V. It can't be wired for 120V operation.

On the print, the drive is connected to "L1" and "N". In this case, "N" isn't neutral - the center tap on a 230V transformer in a US split single phase system - but is rather the other hot lead "L2".
[/QUOTE]

ok, but this device is designed to operate with the US grid 220v per the spec. So for the input to actually be 220v, you would need to have both L1 and L2 connected, AND a neutral? because just L1 and Neutral would only be 120v?
 
dabnug said:
@Guineafowl I get that everyone has told me how to hook up a machine that is manufactured for the US power grid. Except my manufacture is telling me this is wrong. So my line of questions is to educate myself so that I am confident that they are one in the same
You’re absolutely right to check and double-check.

References to the machine “needing a dedicated neutral” aren’t quite accurate and may be something to do with translation. Perhaps they want to be sure you don’t involve the US centre-tap neutral in anything.
 
  • Like
Likes   Reactions: Asymptotic
dabnug said:
ok, but this device is designed to operate with the US grid 220v per the spec. So for the input to actually be 220v, you would need to have both L1 and L2 connected, AND a neutral? because just L1 and Neutral would only be 120v?
No, just L1 and L2. Leave the neutral out.
 
  • Like
Likes   Reactions: Asymptotic
dabnug said:
https://www.schneider-electric.com/...s&filter=product_parent_category_id-166406748

The input voltage specification for it when wired for single phase is 220 V nominal with a range from 200V to 255V. It can't be wired for 120V operation.

On the print, the drive is connected to "L1" and "N". In this case, "N" isn't neutral - the center tap on a 230V transformer in a US split single phase system - but is rather the other hot lead "L2".
ok, but this device is designed to operate with the US grid 220v per the spec. So for the input to actually be 220v, you would need to have both L1 and L2 connected, AND a neutral? because just L1 and Neutral would only be 120v?
What the manufacturer's print shows as "N" isn't neutral. It is "L2".
Nothing on these prints use 120V so far as I can see.
 
Last edited:
Guineafowl said:
References to the machine “needing a dedicated neutral” aren’t quite accurate and may be something to do with translation. Perhaps they want to be sure you don’t involve the US centre-tap neutral in anything.
This is my suspicion as well.
 
Guineafowl said:
There is no sensible way of obtaining a neutral like a Chinese/EU system in your country
Having thought about this, I realized you could use a suitably rated step-up autotransformer to achieve this. Still not necessary, though, and potentially hard to find.

How are you getting on?
 
I got some electricians that specialize in equipment wiring to come and take a look. After inspecting the wiring and various transformers/power converters they said plug it in. The factory is wrong. Plugged it in and it worked. Sorry for dragging this thing out for so long.

I appreciate all the knowledge and detailed explanations along the way.
 
Attachments
  • Photo of a white machine label rotated sideways, reading WARNING in white on red with Chinese characters, and BE CAREFUL THE MACHINERY TO OFFEND SOMEBODY in black, with a pictogram of a figure beside a machine.
    IMG_20190522_083403.jpg
    38 KB · Views: 436
  • Like
Likes   Reactions: Asymptotic, Guineafowl and berkeman
It is not uncommon for a factory to be 'wrong' simply because they don't want to open a can or worms so-to-speak. It is their right to do so. The company doesn't want the liability of someone from their organization advising a customer wrongly by accident so the policy is: "Wire it only this way!"
 
Welcome to PF.
What is the maximum power or current demand of the printer-drier ?

If it is hard-wired to the building, you will need to call your electrician who will do it safely, according to the code. There should be no voltage problem.

If a power cable and a 3 pin plug, to suit a general purpose power outlet is fitted, then it must have sufficient capacity. The protective Earth PE must be connected, and the integrity checked. That again is a job for a qualified electrician.
 
This problem NEEDS a qualified electrician to figure it out. We cannot properly solve it via the internet, so the thread is closed.