Line Current in a 2 phase transformer

  • Thread starter anoor
  • Start date
  • #1
2
0

Main Question or Discussion Point

I am a graduate engineer and have been set a small task to work out the current (primary side) in a 2 phase 30kVA 415:650 transformer. The 2 phases have been utilized from a 3 phase source and are hence 120 degrees out of phase.

I understand had it been a 3 phase 30kVA transformer I could calculate my current by 30kVA / 415 / route*3 = 42A.

If it was a single phase then simply 30kVA / 415 = 73A.

However if I am only using 2 phases from a 3 phase source yet still need to produce 30kVA of power, how do I calculate the line current?

Thanks in advance.
 

Answers and Replies

  • #2
1,354
336
Hello Anoor and Welcom :

I think we will need a little more info -- you are describing a 30KVA trans but the Voltage is 415:650? And by 2 phase - is the secondary like an Open delta - or some other arrangement? Best bet is to post a diagram of the nameplate info.

Lastly -It is not clear if you are actually working on this physically? In the USA you would not be a " qualified person" - working on this is extremely dangerous, does your University have a qualified electrician that you can work with?.
 
  • #3
2
0
I am not working on it physically its just in theory.

Maybe its my poor explanation ill try again!

If I have a standard 230/400V switchboard and want to connect a transformer it would normally be a 3 phase (400V) or single phase-neutral (230V). However if I wanted to connect a transformer to phases L1 & L2, instead of the neutral (giving me 400V). What would my line current be on the primary and how would I calculate it? I apologise if my ignorance doesnt allow me to adequately suscribe the situation! I have attached a pdf showing an extract of the schematic, I hope this helps!

Thanks again.
 

Attachments

  • #4
1,354
336
OK the diagram help a little. If you think of the "phase" as between the lines, as in L2-L3 - this is really a single phase question - IN the USA we refer to this as Line to Line. In this case there is no phase angle - so the Line current is KVA/V - also the transformer input or out put is only a 2 wire device - right?

The lines L2 and L3 are only out of phase 120Deg relative to the neutral
 

Related Threads on Line Current in a 2 phase transformer

Replies
21
Views
5K
Replies
1
Views
12K
  • Last Post
Replies
1
Views
6K
Replies
1
Views
952
Replies
1
Views
5K
Replies
5
Views
6K
Replies
5
Views
1K
  • Last Post
Replies
2
Views
1K
Replies
3
Views
1K
Top